    Dapeng,<br>
      While BESTEST (and ASHRAE Standard 140 - which is identical to
    BESTEST) try hard to be very clear about what assumptions you should
    make in each of the test cases, there is still <i>a lot</i> of room
    for interpretation. Some years ago, we ran TRNSYS 16.1 through those
    test cases as well and found that you can make quite legitimate
    interpretations of the standard and come out with quite a variety of
    results. I would recommend you have a look at a couple papers that
    we wrote about the effort:<br>
    <br>
    "Converging on a Recommended Set of Interpretations and Assumptions
    in Applying Standard Tests to Energy Analysis Tools"<br>
    "Experiences with and Interpretations of Standard Test Methods of
    Building Energy Analysis Tools"<br>
    <br>
    both are available at <a class="moz-txt-link-freetext" href="http://www.tess-inc.com/pubs">http://www.tess-inc.com/pubs</a>.<br>
    <br>
    If my recollection is correct, we were within the range on the 600
    cases. If anything, the annual cooling that modern versions of
    TRNSYS predict is on the low end of the range and is sometimes below
    the range. It is worth keeping in mind that the "acceptable range"
    of results does not come from an analytical solution. It comes from
    the results generated by a bunch of software tools and TRNSYS
    (version 13!) is one of them. Other software developers have
    mentioned to me recently that building science and cooling load
    algorithms have advanced since the 1980s and that more recent
    algorithms do predict lower cooling loads than did the older
    algorithms. This is not reflected in the BESTEST or Standard140
    results; those ranges are still set by the older versions of the
    tools. <br>
    <br>
    Best,<br>
     David<br>
    <br>
    <br>
    On 11/14/2011 21:14, Dapeng Li wrote:
    <blockquote
cite="mid:CAE+QzVkE48exSZbThXF_jcQpA4NarHf87QMmAReNWTurZCDL=g@mail.gmail.com"
      type="cite">
      <div class="gmail_quote"><br>
        Dear all users, 
        <div>Hello.</div>
        <div><br>
        </div>
        <div>I try to take a test by using BESTEST algorithm. I use
          TRNSYS version 16.01.003. I think I have taken my best to set
          up each parameters in TRNSYS's deck and TRNBUILD according to
          case 600's condition in the BESTEST documents which is
          downloaded from <u style="color:rgb(0, 0, 128)"><a
              moz-do-not-send="true"
              href="http://www.nrel.gov/docs/legosti/old/6231.pdf"
              target="_blank">http://www.nrel.gov/docs/legosti/old/6231.pdf</a>。</u><span
            style="color:rgb(0, 0, 128)"> </span>But the annual heating
          load (5.997MWh) from TRNSYS is different from the value ranges
          (4.296 to 5.709). The annual cooling load (6.519MWh) fit well.
          I wonder the reasons of this kind of difference. For
          convenience, I attached my project for your deep examine.</div>
        <div><br>
        </div>
        <div>Thank you for your help in advance. </div>
        <div><br>
        </div>
        <div>kindly regards, </div>
        <span class="HOEnZb"><font color="#888888">
            <div>Dapeng Li</div>
            <p style="margin-bottom:0in">
            </p>
          </font></span></div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>