    Wang,<br>
      You should already have the source code for the PID controller in
    ..\TrnsysXX\SourceCode\Types\. I would also recommend reading the
    Type23 section of the 04-MathematicalDescription manual.<br>
    <br>
      PID controllers can operate in one of two ways: they can generate
    a greater signal value if the sampled input value is below the set
    point or they can generate a greater signal value if the sampled
    input is above the current set point. Imagine a heating application
    with a PID controller. As the zone temperature falls, you want the
    PID to give you a bigger and bigger signal. Now imagine a cooling
    application. As the zone temperature rises, you want the PID to give
    you a bigger and bigger signal. You may have to add an equation
    after the PID to invert its control signal if it is acting the
    opposite of the way that you want.<br>
    <br>
    David<br>
    <br>
    On 11/14/2011 04:28, wangyang wrote:
    <blockquote
cite="mid:CABF0dEviioFncZaxiY+P_jTpfTY4wvw-pZKKC7CGANvvqV7WZg@mail.gmail.com"
      type="cite">
      <div>Dear all,</div>
      <div> </div>
      <div>    I have a question about PID controller in TRNSYS for its
        developer.</div>
      <div> </div>
      <div>    Which expert knows PID controller in TRNSYS developer? Or
        Which expert could pass me the source code of PID controller or
        its internal algorithm etc.? I guess PID controller in TRNSYS is
        based on empirical equation or iterative algorithm. Since there
        is <strong><font color="#3333ff">very weird</font></strong>
        simulation results i.e. I set the set point CO2 concentration
        1000 ppm as PID controller's set point; its control signal links
        to Opening Factor (OF) of windows; indoor CO2 concentration
        links to PID's controlled variable. However, when indoor CO2
        concentration is less than set point 1000 ppm, PID begins to
        activate OF i.e. windows are open. But based on PID principle,
        as we know, if CO2 concentration is not getting to set point
        1000 ppm, at this time windows are open will result in <font
          color="#3333ff"><strong>the ERROR</strong></font> (between the
        set point and actual indoor CO2 concentration)<font
          color="#3333ff"><strong> increasing. </strong><font
            color="#000000">So I'm puzzled! Please PID controller in
            TRNSYS developer or other experts explain this weird
            phenomenon!</font></font></div>
      <div><font color="#3333ff">  </font><font color="#000000"> Many
          thanks in advance!</font></div>
      <div> </div>
      <div><font color="#000000">   br</font></div>
      <div> </div>
      <div><font color="#3333ff"><font color="#000000">   wang</font></font></div>
      <div><br>
        <br>
      </div>
      <div class="gmail_quote">2011/11/12 <span dir="ltr"><<a
            moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
        <blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px
          0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send
          TRNSYS-users mailing list submissions to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          <br>
          To subscribe or unsubscribe via the World Wide Web, visit<br>
                 <a moz-do-not-send="true"
            href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
            target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
          or, via email, send a message with subject or body 'help' to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
          <br>
          You can reach the person managing the list at<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
          <br>
          When replying, please edit your Subject line so it is more
          specific<br>
          than "Re: Contents of TRNSYS-users digest..."<br>
          <br>
          Today's Topics:<br>
          <br>
            1. Re: (no subject) (David BRADLEY)<br>
            2. Re: TRNSYS3D Shading on Walls? (David BRADLEY)<br>
            3. Re: how to identify a wall that is adjacent two walls<br>
               (David BRADLEY)<br>
            4. Error in reading type 51 external performance File<br>
               (Walif M'kacher)<br>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: David BRADLEY <<a moz-do-not-send="true"
            href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
          To: Erik Boschek <<a moz-do-not-send="true"
            href="mailto:erikboschek@yahoo.com">erikboschek@yahoo.com</a>><br>
          Date: Fri, 11 Nov 2011 12:01:47 -0600<br>
          Subject: Re: [TRNSYS-users] (no subject)<br>
          <div bgcolor="#FFFFFF" text="#000000">Erik,<br>
             You are right on with all three of your points. For
            reference, we discontinued use of Type109 in Trnsys17 in
            favor of option 2 (Type15), which is correct from an energy
            perspective even though it isn't a smooth curve. In gernal
            think that a control strategy that relies only on the
            instantaneous DNI as its input might run into trouble not
            only in simulation but also in the real world; clouds pass
            in front of the sun rapidly sometimes. While I won't pretend
            that the "spiky" profile that Type15 generates is totally
            realistic, I think it is a fairly accurate representation of
            DNI. Bear in mind that Type15 is trying to reconstruct a
            minute by minute radiation profile based only on 1 number
            and to do so correctly for all possible climate types. You
            might consider a control strategy that uses the output of
            Type15 but put through a running-average component so that
            your control decisions are based on a somewhat more stable
            (smoother) profile.<br>
            Best,<br>
             David<br>
            <br>
            <br>
            On 11/11/2011 00:32, Erik Boschek wrote:
            <blockquote type="cite">
              <div style="BACKGROUND-COLOR: #fff; FONT-FAMILY: arial,
                helvetica, sans-serif; COLOR: #000; FONT-SIZE: 12pt">
                <div><br>
                </div>
                <div>Dear TRNSYS users,</div>
                <div><br>
                </div>
                <div>I have a simple question regarding weather reading
                  and interpolating direct normal radiation (DNI) values
                  for time steps less than an hour.</div>
                <div><br>
                </div>
                <div>As long as I have been using TRNSYS (using TRNSYS
                  16.1) I have understood this can be done in a few ways
                  as follows, including the consequence for an example
                  TM2 file (see attached screen shot for clarification):</div>
                <div><br>
                </div>
                <div>1.) Do not interpolate, using Type 15 with output
                  DNR (not interpolated): you end up with a "steppy"
                  profile</div>
                <div>2.) Using Type 15, but with 2-axis tracking and the
                  output "Beam radiation for surface": you get a
                  discontinuous "spikey" profile, but the integration of
                  energy across the hour is respected</div>
                <div>3.) Same as 2, but using Type109-TMY2: You get a
                  smooth profile, but often there appear inexplicable
                  spikes at the beginning or end of the day. The one in
                  the plot obviously is an extreme case.<br>
                </div>
                <div><br>
                </div>
                <div>For reference: I just used the Daggett profile
                  "US-CA-Daggett-23161.tm2" which came with TRNSYS, but
                  the behavior is not specific to this file.</div>
                <div><br>
                </div>
                <div>Generally, I have been using 2, but it can cause
                  problems if there is, for example, some triggering
                  function based on DNI and the DNI hovers around the
                  threshold. Is there another option for getting a
                  smoother profile or is it best just to not
                  interpolate? Any opinions? Feel free to point me to an
                  earlier post on this topic in case I missed it.<br>
                </div>
                <div><br>
                </div>
                <div>Thanks,</div>
                <div><br>
                </div>
                <div>Erik Boschek<br>
                </div>
                <div><br>
                </div>
                <div><br>
                </div>
                <div><br>
                </div>
                <div><br>
                </div>
                <div><br>
                </div>
                <div><br>
                </div>
              </div>
              <br>
              <fieldset></fieldset>
              <br>
              <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
            </blockquote>
            <br>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:<a moz-do-not-send="true" href="tel:%2B1.608.274.2577" target="_blank" value="+16082742577">+1.608.274.2577</a>
F:<a moz-do-not-send="true" href="tel:%2B1.608.278.1475" target="_blank" value="+16082781475">+1.608.278.1475</a>
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: David BRADLEY <<a moz-do-not-send="true"
            href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
          To: Marion Hiller <<a moz-do-not-send="true"
            href="mailto:hiller@transsolar.com">hiller@transsolar.com</a>><br>
          Date: Fri, 11 Nov 2011 12:03:16 -0600<br>
          Subject: Re: [TRNSYS-users] TRNSYS3D Shading on Walls?<br>
          TRNSYS-users,<br>
           My apologies; my reply to Graham was incorrect; as Marion
          says, only the windows are affected.<br>
          Kind regards,<br>
           David<br>
          <br>
          <br>
          On 11/11/2011 01:33, Marion Hiller wrote:<br>
          <blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px
            0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Graham,<br>
            <br>
            the shading defined in Trnsys3D effects only windows.<br>
            <br>
            Marion<br>
            <br>
            Dipl.-Ing. Marion Hiller<br>
            TRANSSOLAR: KlimaEngineering - Technologien für
            energieeffizientes Bauen<br>
            und Nutzerkomfort in Gebäude<br>
            Munich - New York - Stuttgart <a moz-do-not-send="true"
              href="tel:%2B%2049.711.67976.0" target="_blank"
              value="+49711679760">+ 49.711.67976.0</a><br>
            <br>
            Transsolar Energietechnik GmbH, Curiestrasse 2, 70563
            Stuttgart<br>
            Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911,
            USt-IdNr.:<br>
            DE152272639<br>
            Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing.
            Thomas Auer,<br>
            Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher<br>
            <br>
            <br>
            <br>
            -----Ursprüngliche Nachricht-----<br>
            Von: Graham Linn [mailto:<a moz-do-not-send="true"
              href="mailto:grahamjlinn@gmail.com" target="_blank">grahamjlinn@gmail.com</a>]<br>
            Gesendet: Donnerstag, 10. November 2011 21:49<br>
            An: <a moz-do-not-send="true"
              href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
            Betreff: [TRNSYS-users] TRNSYS3D Shading on Walls?<br>
            <br>
            Hello TRNSYS users,<br>
            <br>
            I have a question about shading in TRNSYS3D. Does a shading
            object<br>
            affect how much insolation hits the entire building or just
            the<br>
            windows on the building?<br>
            <br>
            Thank you!<br>
            Graham<br>
            _______________________________________________<br>
            TRNSYS-users mailing list<br>
            <a moz-do-not-send="true"
              href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
            <a moz-do-not-send="true"
              href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
              target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
            <br>
            <br>
            <br>
            _______________________________________________<br>
            TRNSYS-users mailing list<br>
            <a moz-do-not-send="true"
              href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
            <a moz-do-not-send="true"
              href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
              target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
            <br>
            <br>
          </blockquote>
          <br>
          -- <br>
          ***************************<br>
          David BRADLEY<br>
          Principal<br>
          Thermal Energy Systems Specialists, LLC<br>
          22 North Carroll Street - suite 370<br>
          Madison, WI  53703 USA<br>
          <br>
          P:<a moz-do-not-send="true" href="tel:%2B1.608.274.2577"
            target="_blank" value="+16082742577">+1.608.274.2577</a><br>
          F:<a moz-do-not-send="true" href="tel:%2B1.608.278.1475"
            target="_blank" value="+16082781475">+1.608.278.1475</a><br>
          <a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com"
            target="_blank">d.bradley@tess-inc.com</a><br>
          <br>
          <a moz-do-not-send="true" href="http://www.tess-inc.com/"
            target="_blank">http://www.tess-inc.com</a><br>
          <a moz-do-not-send="true" href="http://www.trnsys.com/"
            target="_blank">http://www.trnsys.com</a><br>
          <br>
          <br>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: David BRADLEY <<a moz-do-not-send="true"
            href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
          To: Nidal Abdalla <<a moz-do-not-send="true"
            href="mailto:nidalabdalla@yahoo.com">nidalabdalla@yahoo.com</a>><br>
          Date: Fri, 11 Nov 2011 12:29:48 -0600<br>
          Subject: Re: [TRNSYS-users] how to identify a wall that is
          adjacent two walls<br>
          <div bgcolor="#FFFFFF" text="#000000">Nidal,<br>
              You have to be a little careful here. If you have a wall
            in zone 1, half of which is adjacent to zone 2 and half of
            which is adjacent to zone 3, you actually need to draw the
            wall as two walls in zone 1. Trnsys3D requires the user to
            be quite vigilant about manually setting adjacencies. You
            need to draw the ADJACENT wall in both zones and you need to
            open the object window for each of them, set the
            construction to ADJ_WALL, set the "outside boundary
            condition" to "Zone" and then manually select the zone to
            which it is adjacent in the "outside boundary object" field.
            <br>
            <br>
              If you have been very careful about drawing your ADJACENT
            walls so that they have exactly the same verticies in both
            zones to which they belong, you can then select the menu
            item:  Plugins: Trnsys3d: Surface Matching and click the
            "match in entire model" button.<br>
            <br>
            Kind regards,<br>
             David<br>
             <br>
            <br>
            On 11/11/2011 08:32, Nidal Abdalla wrote:
            <blockquote type="cite">
              <div style="BACKGROUND-COLOR: #fff; FONT-FAMILY: arial,
                helvetica, sans-serif; COLOR: #000; FONT-SIZE: 18pt">
                <div><font face="Calibri">I drew a house using Trnsys3d
                    that consists of: 3 bed rooms, living room, guest
                    room and bath . The house was divided into 6 zones.
                    Wall_zone5, for example, is adjacent two walls for
                    two different zones. I am wondering how to identify
                    a wall (using Object Info) that is adjacent two or
                    more walls of diff. zones.</font></div>
                <div> </div>
                <div><font face="Calibri">Best Regards</font></div>
                <div> </div>
                <div><font face="Calibri">Nidal Abdalla</font></div>
                <div style="MARGIN: 0in 0in 10pt" class="MsoNormal"><span
                    style="LINE-HEIGHT: 115%; FONT-SIZE: 11pt"></span> </div>
              </div>
              <br>
              <fieldset></fieldset>
              <br>
              <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
            </blockquote>
            <br>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:<a moz-do-not-send="true" href="tel:%2B1.608.274.2577" target="_blank" value="+16082742577">+1.608.274.2577</a>
F:<a moz-do-not-send="true" href="tel:%2B1.608.278.1475" target="_blank" value="+16082781475">+1.608.278.1475</a>
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: "Walif M'kacher" <<a moz-do-not-send="true"
            href="mailto:walif.mkacher@gmail.com">walif.mkacher@gmail.com</a>><br>
          To: <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          Date: Sat, 12 Nov 2011 15:13:05 +0100<br>
          Subject: [TRNSYS-users] Error in reading type 51 external
          performance File<br>
          <div dir="ltr">
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal">Dear TRNSys Users,</p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"> </p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal">I have a problem with external file of
              type 51a (cooling tower with an external performance
              File):</p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"><br>
            </p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal">That the simulation with this type
              causes error and this can't read this external file (.txt)</p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"><br>
            </p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"><br>
            </p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal">Would you please help me how to correct
              the file joined or send me a truth format of this .txt
              file</p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"><br>
            </p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"> </p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"><span style="FONT-SIZE: 10.5pt">Many
                thanks in advance</span></p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"><span style="FONT-SIZE: 10.5pt"> </span></p>
            <p style="BACKGROUND-COLOR: rgb(255,255,255); FONT-FAMILY:
              arial, sans-serif; COLOR: rgb(34,34,34); FONT-SIZE: 13px"
              class="MsoNormal"><span style="FONT-SIZE: 10.5pt"><u>Mkacher
                  Walif</u></span></p>
          </div>
          <br>
          _______________________________________________<br>
          TRNSYS-users mailing list<br>
          <a moz-do-not-send="true"
            href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
          <a moz-do-not-send="true"
            href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
            target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>