    Mayank,<br>
      Type107 in the standard TRNSYS library is a generic absorption
    chiller model. It takes a few external data files that contain
    "typical" manufacturer's performance such as how the chiller's
    capacity and input energy change with varying inlet conditions. In
    actual practice, I think getting ahold of realistic data is very
    hard. Manufacturers either don't have it or don't want to give it
    out. The data files that are provided with Type107 are for a much
    larger machine than would be appropriate for a residential scale. I
    would highly recommend finding a manufacturer who has a piece of
    equipment in the size range that you are looking at so that you can
    work with them using their data. <br>
    <br>
      I am not sure how you are planning to model the refrigerator
    itself. You might have some luck using one of the lumped thermal
    capacitance models such as Type59. Alternatively, there is an actual
    refrigerator model in the TESS Loads and Structures Library (v17).<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 11/7/2011 10:16, Mayank Bhatnagar wrote:
    <blockquote cite="mid:4eb80446.8879440a.5338.38bb@mx.google.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
      <div class="Section1">
        <p class="MsoNormal">Dear all,<o:p></o:p></p>
        <p class="MsoNormal">I want to simulate a absorption
          refrigerator using heat of
          solar energy. Is it possible to make a absorption refrigerator
          in TRNSYS
          because I need it to compare domestic refrigeration system
          with domestic air
          conditioning  system of absorption type.<o:p></o:p></p>
        <p class="MsoNormal">Thank you all for your support in advance.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Regards,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">Mayank
              Bhatnagar<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">M.Tech.
              (Energy Engineering)<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">Malaviya
              National Institute of Technology,<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">Jaipur
              (INDIA)<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">contact
              no.- +91-9983816468<o:p></o:p></span></b></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>