<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Béatrice,<br>
      The error message is indicating that the energy balance across one
    of the walls in your Type56 (I am guessing) building is not
    converging. Specifically, the outside surface temperature of the
    wall is not coming to a stable solution. If you are using an
    algorithm to set the convection coefficient on the outside surface
    of your wall, make sure that the algorithm cannot produce a result
    of 0; this would indicate that there is NO convective heat transfer
    on the outside surface of the wall and that only the radiation
    matters, which is unrealistic. The second thing to try is that if
    you have variable convective coefficients on either the inside or
    the outside surface of that wall, turn them off and use constant
    values.<br>
    Kind regards,<br>
     David<br>
    <br>
    On 11/4/2011 04:21, beatrice bernin wrote:
    <blockquote
cite="mid:CAPt99vHZC4=5BrdgiZYX331xmdYzSrBwNc-CL0GH4Gh_Y+k4cw@mail.gmail.com"
      type="cite">Hello,
      <div><br>
      </div>
      <div>I have a mistake during a simulation, an eror occured
        :outside temperature of 11 wall in zone 3 at time 8718 not
        converged.</div>
      <div>I don't uderstand the mistake because I've two models:</div>
      <div>One with a building and convectors and it works, another with
        the same buildind, convector and a wood poele ans it doesn't
        work</div>
      <div>Can you help me?</div>
      <div><br>
      </div>
      <div>Best regards</div>
      <div><br>
      </div>
      <div>Béatrice Bernin</div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>