Wang, <br>
If you have variable convection coefficients on either the inside
or outside surface of that particular window, turn them off in favor
of constant values (11 kJ/h.m2.K for the inside, 64 for the
outside). If the problem still occurs, unfortunately, you are going
to have to adjust the thermal properties of your window. If you
created the window using LBNL's Window 5 software, you can change it
yourself. If you are using a standard window, then you will need to
send your project to your distributor for assistance.<br>
Regards,<br>
David<br>
<br>
<br>
On 11/7/2011 06:55, 王洋 wrote:
<blockquote
cite="mid:CABF0dEsxdB1PovGMvpP9XzzzPJ_OoJ+c+NzrNu5N0E_hUR9txQ@mail.gmail.com"
type="cite">
<div> </div>
<div>Dear all,</div>
<div> </div>
<div>I met an Fatal Error as follows, which experts could deal
with it? Please tell me in detail.</div>
<div> </div>
<div>*** Fatal Error at time : 0.010000<br>
Generated by Unit : 2<br>
Generated by Type : 56<br>
Message : Zone 3 surface 18 pane
temperature calculation is diverging at time 0.01000TDIF:
NaN ITPANE: 31 ITCALC: 51</div>
<div> </div>
<div>Many thanks in advance!</div>
<div> </div>
<div>br</div>
<div> </div>
<div>wang<br>
<br>
</div>
<div class="gmail_quote">2011/11/6 <span dir="ltr"><<a
moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px
0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send
TRNSYS-users mailing list submissions to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
<a moz-do-not-send="true"
href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more
specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>
Today's Topics:<br>
<br>
1. Re: about the chilled ceiling below the roof room (Matt
Duffy)<br>
2. Re: command line to generate dck from tpf (Matt Duffy)<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "Matt Duffy" <<a moz-do-not-send="true"
href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>><br>
To: <a moz-do-not-send="true" href="mailto:ilyt2000@gmail.com">ilyt2000@gmail.com</a>,
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Sun, 6 Nov 2011 16:20:10 -0600 (CST)<br>
Subject: Re: [TRNSYS-users] about the chilled ceiling below
the roof room<br>
<br>
<p class="MsoNormal">Dear Leona,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I am not exactly sure what you mean by,
“there is a roof room above”. If there is indeed a thermal
zone above your room, that would require an adjacent wall
and not a boundary wall.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Best regards,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Matt Duffy</p>
<p class="MsoNormal"> </p>
<br>
<br>
<div style="BACKGROUND-REPEAT: repeat-x"><strong>-----
Original Message -----</strong><br>
<strong>From:</strong> "ͫͫ" <<a moz-do-not-send="true"
href="mailto:ilyt2000@gmail.com" target="_blank">ilyt2000@gmail.com</a>>
<br>
<strong>Sent:</strong> Fri, November 4, 2011 9:45<br>
<strong>Subject:</strong> [TRNSYS-users] about the chilled
ceiling below the roof room<br>
<br>
<table cellspacing="5" width="100%">
<tbody>
<tr>
<td>! </td>
</tr>
<tr>
<td>
<div>
<div>Dear all,</div>
<div> </div>
<div>i want to add a chilled ceiling ,but there is
a roof room above, and i have made the boundary
temperatur of the wall type " ceiling" as 35 °C.
Wenn i use the chilled ceiling ,it seems like
something is wrong,</div>
<div> </div>
<div>Does someone know, what i should change?</div>
<div> </div>
<div>best regards from Leona</div>
<hr noshade="noshade" size="1">
<pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</div>
</td>
</tr>
</tbody>
</table>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "Matt Duffy" <<a moz-do-not-send="true"
href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>><br>
To: "Keech, Richard" <<a moz-do-not-send="true"
href="mailto:richard.keech@gmail.com">richard.keech@gmail.com</a>>,
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Sun, 6 Nov 2011 16:23:47 -0600 (CST)<br>
Subject: Re: [TRNSYS-users] command line to generate dck from
tpf<br>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Dear Richard,</p>
<p class="MsoNormal">To the best of my knowledge, you cannot
do this from the command line. However, you could perhaps
implement an Auto HotKey application that would create all
of the input *.dck files from many *.tpf Studio projects.</p>
<p class="MsoNormal">Best regards,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Matt Duffy</p>
<br>
<br>
<br>
<div style="BACKGROUND-REPEAT: repeat-x"><strong>-----
Original Message -----</strong><br>
<strong>From:</strong> "Keech, Richard" <<a
moz-do-not-send="true"
href="mailto:richard.keech@gmail.com" target="_blank">richard.keech@gmail.com</a>>
<br>
<strong>Sent:</strong> Fri, November 4, 2011 20:23<br>
<strong>Subject:</strong> [TRNSYS-users] command line to
generate dck from tpf<br>
<br>
<table cellspacing="5" width="100%">
<tbody>
<tr>
<td>
<div>Is it possible to generate a TRNSYS input "dck"
file from a TRNSYS Studio "tpf" file straight from
the command line? <br clear="all">
<br>
-- <br>
Richard Keech <a moz-do-not-send="true"
href="tel:%2B61%20419%20036%20463"
target="_blank" value="+61419036463">+61 419 036
463</a><br>
<hr noshade="noshade" size="1">
<pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</div>
</td>
</tr>
</tbody>
</table>
</div>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br>
</blockquote>
</div>
<br>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>