    Dr Abdunnabi,<br>
      As Matt mentioned, if all of your collectors are plumbed in a
    pattern (say 30 in parallel or 15 in parallel and 2 sets in series)
    then you can use the "number in series" and "number in parallel"
    parameters to simulate the whole collector array with a single
    instance of the collector component. This method neglects the
    thermal losses from the piping between collectors and can't be used
    if you have a complicated flow pattern. The fewer components in your
    system, the faster TRNSYS will be able to solve them so if you can
    reduce the number of components, you will get some benefits from
    that.<br>
    <br>
      My guess is that when you run the smaller parts of your system
    (the micros) individually, the simulation converges well but that
    when you add the others, some output is not converging. If turning
    on the "debug" switch in the simulation control cards does not help
    then please send your input file to your distributor and they should
    be able to help further.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 10/30/2011 04:30, mohammad abdunnabi wrote:
    <blockquote
      cite="mid:1319967042.4996.YahooMailNeo@web114606.mail.gq1.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:times
        new roman, new york, times, serif;font-size:12pt">
        <div style="RIGHT: auto"><span style="RIGHT: auto">Dear Trnsys
            Users</span></div>
        <div style="RIGHT: auto"><span style="RIGHT: auto"></span> </div>
        <div style="RIGHT: auto"><span style="RIGHT: auto">I've faced
            problem when I used macro. The macro is consists of 30
            evacuated tube collector with flow diverters and mixers.
            I've used three maco in my system to be simulated with the
            other components such as sotrage tanks auxilary heaters etc.
            When I run the program the following error appears:</span></div>
        <div style="RIGHT: auto"><span style="RIGHT: auto">Range check
            error</span></div>
        <div style="RIGHT: auto"><span style="RIGHT: auto"></span> </div>
        <div style="RIGHT: auto"><span style="RIGHT: auto">Bear in mind
            that each micro works fine (when I delete the other macros).
            Can any body help</span></div>
        <div style="RIGHT: auto"><span style="RIGHT: auto"></span> </div>
        <div style="RIGHT: auto"><span style="RIGHT: auto">Many thanks
            in advace</span></div>
        <div style="RIGHT: auto"> </div>
        <div style="RIGHT: auto">Dr. Mohammad Abdunnabi<br>
          Head of Thermal Energy conversion Department<br>
          Center for Solar Energy Research and Studies (CSERS)</div>
        <div><var id="yui-ie-cursor"></var>Tripoli-Libya<br>
          P.O.Box: 12932<br>
          Tel.: +218 21 3699323<br>
          Fax.: +218 21 3699322<br>
          Office Phone: +218 21 7201993<br>
          Mobile Phone: +218 92 2256067</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>