<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    In general, Type56 doesn't really care what happens to the air that
    leaves the zone. (note: this is NOT the case when Type56 is coupled
    with COMIS or CONTAM). If you have an exhaust fan, you can simply
    use an external model and use the zone air temperature and RH as the
    inputs. What you do have to concern yourself with is where the
    replacement air is going to come from. In otherwords, when the
    exhaust fan turns on, it will depressurize the zone and some
    replacement air will come into the zone. Type56 assumes that the
    zone remains pressure neutral and does not do a mass balance. So it
    is up to you to make sure that you add an equal amount of air into
    the zone (using a VENTILATION type (as was correctly recommended by
    Baboo Gowreesunker) or a coupling airflow to an adjacent zone).<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 10/24/2011 23:03, hankiat lee wrote:
    <blockquote cite="mid:SNT141-W487DAFB4FE65C6B58C3C0BD3EC0@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Tahoma
}
--></style>
      <div dir="ltr">
        <br>
        hi,<br>
        <br>
        Does anybody know how to blow out the hot air in type 56? i link
        a fan trying to simulate flowing out of hot air, but there is no
        mass flow rate in the output of type 56. <br>
        <br>
        Thank You<br>
        <br>
        Lee Han Kiat<br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>