    Karol,<br>
      Unless you are concerned about the radiation exchange within the
    zone (and have selected the detailed zone geometry model) you don't
    really need to worry about having only concave zones. Having said
    that, there are a few options for estimating the air exchange
    between air nodes. The simplest method is simply to define some
    arbitrary (usually high) mixing rate between the two parts of the
    zone. This will keep the two zones at approximately the same
    temperature. The other alternative is to use either TRNFlow, COMIS,
    or CONTAM/Type97 to predict the air exchange rate based on the
    temperature and pressure differences between the two air nodes.
    These second alternatives are a significant amount of work so I
    would first look at your building's energy consumption assuming that
    there is no air exchange between the two zones, then look at the
    energy consumption assuming significant air exchange. If there isn't
    a big difference you know that the building isn't very sensitive to
    the air exchange rate and you can save yourself the time of modeling
    it by setting an arbitrary air exchange rate to achieve a realistic
    level of comfort difference between the two zones.<br>
    kind regards,<br>
     David<br>
     <br>
    <br>
    On 9/29/2011 04:08, Karol Bandurski wrote:
    <blockquote cite="mid:000e01cc7e87$57f8f540$07eadfc0$@put.poznan.pl"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 14 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";
        mso-fareast-language:EN-US;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.Stylwiadomocie-mail17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri","sans-serif";
        mso-fareast-language:EN-US;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span lang="EN-US">Hi,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">The problem is from Type
            56.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I have house with few
            rooms which are not rectangular, they are concave. So, I
            can’t make one room=one zone.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I divided room on
            rectangles to make zones, and walls between zones of one
            room are VirtualSurface. Radiation is seemed OK, but air
            between two zones of one room isn’t mixed…<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">What can I do? Is it
            possible to solve this problem in TRNBuild or I have to go
            outside Type 56 and operate in Simulation Studio?<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Regard,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Karol<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>