<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Wang,<br>
      I will preface this by mentioning that I am not an expert in the
    TRNFlow part of Type56. <br>
    <br>
      It is a little hard to know what is going on without knowing
    anything about the building. However, if you have multiple zones in
    the building, I imagine that there would be some air mixing going on
    between zones due to internal temperature and height differences and
    the CO2 concentration would decrease in one zone while increasing in
    another. <br>
    <br>
      I would also recommend looking at the COMIS documentation (COMIS
    is the engine that underlies TRNFlow) to see whether its algorithms
    are trying to predict CO2 concentration at a particular point in the
    space (like we do in Type56 for comfort calculations at a particular
    point in a zone) or whether it is assuming a fully mixed zone as far
    as the CO2 level is concerned. If COMIS is calculating concentration
    at a point and the air continues to mix after your opening factor
    has gone to zero then that might explain the decrease.<br>
    <br>
     Lastly, your mechanical ventilation system might have something to
    do with the decrease; If you are actively supplying air to the space
    after the opening factor is zero and if the mechanical ventilation
    system has some outdoor air associated with it then that also would
    explain the decrease in CO2 level.<br>
    <br>
    Regards,<br>
     David<br>
     <br>
    <br>
    On 9/30/2011 08:47, 王洋 wrote:
    <blockquote
cite="mid:CABF0dEvLYZ_xd4mM59+XsWswZ7kMerrV7Kd7NSc0jvmoBQugwQ@mail.gmail.com"
      type="cite">
      <div>Dear all,</div>
      <div> </div>
      <div>     I simulated CO2 concentration changes using TRNFlow. But
        there is a STRANGE phenomenon. There are 2 occupants from 8am to
        6 pm, CO2% is controlled by PID controller which controls
        Opening Factor (OF) of window at the set-point 1000 ppm. From 6
        pm, there are no occupants, OF is 0, there is no infiltration in
        TRNBuild (Certainly, infiltration in TRNBuild indeed will
        inactivate when couping TRNFlow based on TRNFlow Manual).
        However, from 6 pm, CO2% begins to decrease. It's extremely
        strange!</div>
      <div> </div>
      <div>   Which relative expert can expain that? Or give me some
        advices for that? I am puzzled for a long time.</div>
      <div> </div>
      <div>   Many thanks in advance!</div>
      <div> </div>
      <div>  br</div>
      <div> </div>
      <div> wang<br>
        <br>
      </div>
      <div class="gmail_quote">2011/9/30 <span dir="ltr"><<a
            moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
        <blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px
          0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send
          TRNSYS-users mailing list submissions to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          <br>
          To subscribe or unsubscribe via the World Wide Web, visit<br>
                 <a moz-do-not-send="true"
            href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
            target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
          or, via email, send a message with subject or body 'help' to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
          <br>
          You can reach the person managing the list at<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
          <br>
          When replying, please edit your Subject line so it is more
          specific<br>
          than "Re: Contents of TRNSYS-users digest..."<br>
          <br>
          Today's Topics:<br>
          <br>
            1. Using Excel as Load Profile (Pei Ru Chao)<br>
            2. TRNSYS error 300 (<a moz-do-not-send="true"
            href="mailto:torres.carlos-moises@lte.ireq.ca">torres.carlos-moises@lte.ireq.ca</a>)<br>
            3. Direct expansion solar collector (Mohamad Azly Abd Aziz
          (Ir))<br>
            4. simulation studio crash when updating project (Antoine
          Gautier)<br>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: Pei Ru Chao <<a moz-do-not-send="true"
            href="mailto:simplica1@hotmail.com">simplica1@hotmail.com</a>><br>
          To: TRNSYS <<a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
          Date: Fri, 30 Sep 2011 16:31:53 +1000<br>
          Subject: [TRNSYS-users] Using Excel as Load Profile<br>
          <div>
            <div dir="ltr">Hi all,
              <div><br>
              </div>
              <div>As a newbie I am wondering how to use Excel for load
                profile input. Can anyone point me in the right
                direction as to how to use a Data Reader to do this? For
                example, can the Data Reader read 10920 rows of data? In
                9a for example, Parameter 2 asks how many values of
                input to read and the maximum is only 98?</div>
              <div><br>
              </div>
              <div>Thanks</div>
              <div><br>
              </div>
              <div>Pei</div>
              <div><br>
              </div>
              <div><br>
              </div>
            </div>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: <<a moz-do-not-send="true"
            href="mailto:torres.carlos-moises@lte.ireq.ca">torres.carlos-moises@lte.ireq.ca</a>><br>
          To: <<a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
          Date: Thu, 29 Sep 2011 15:50:36 -0400<br>
          Subject: [TRNSYS-users] TRNSYS error 300<br>
          <div>
            <div><font face="Arial" size="2"><span>Dear all,</span></font></div>
            <div><font face="Arial" size="2"><span></span></font> </div>
            <div><font face="Arial" size="2"><span>Whenever I ry to run
                  a type 56 simulation in TRNSED I am given the
                  following error even though the same program runned
                  perfectly in TRNEdit</span></font></div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA"></span></span></font> </div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA"> *****
                    ERROR *****        TRNSYS ERROR # 300<br>
                     UNABLE TO START PROGRAM IN CALLPROGRAM UTILITY<br>
                     PLEASE CHECK PATH AND PROGRAM NAME, THIS MAY BE A
                    PROBLEM IN TYPE 66<br>
                     <br>
                    *** Fatal Error at time   :         0.000000<br>
                        Generated by Unit     : Not applicable or not
                    available<br>
                        Generated by Type     : Not applicable or not
                    available<br>
                        TRNSYS Message    300 : The TRNSYS Program
                    attempted to evaluate an EQUATION that raised a
                    negative number to a non-integer value. Please check
                    the EQUATION formulation and re-run the simulation<br>
                        Reported information  : Not available</span></span></font></div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA"></span></span></font> </div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA">the
                    message is not very helpfull and I don't even use
                    Type 66 in my simulation and I checked all my
                    equations and nothing obvious comes to view.</span></span></font></div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA"></span></span></font> </div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA">Is
                    there any known solution to this problem? If need be
                    I can send you the files im using.</span></span></font></div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA"></span></span></font> </div>
            <div><font face="Arial" size="2"><span><span lang="FR-CA">Thank
                    you</span></span></font></div>
            <div> </div>
            <div align="left">
              <div><font face="Arial" size="2"><span>Carlos Torres</span></font></div>
              <div><font face="Arial" size="2"><span>Stagiaire
                    universitaire</span></font></div>
              <div><font face="Arial" size="2"><span>Laboratoire des
                    technologies de l'énergie (LTE)</span></font><font
                  face="Arial" size="2"><span></span></font></div>
            </div>
            <div> </div>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: "Mohamad Azly Abd Aziz (Ir)" <<a
            moz-do-not-send="true" href="mailto:AZLY@jkr.gov.my">AZLY@jkr.gov.my</a>><br>
          To: "<a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>"
          <<a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
          Date: Fri, 30 Sep 2011 04:36:25 -0700<br>
          Subject: [TRNSYS-users] Direct expansion solar collector<br>
          <div vlink="purple" link="blue" lang="EN-MY">
            <div>
              <p class="MsoNormal">Hi</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">I wonder whether someone has come-out
                with heat pump type with direct expansion solar
                collector/evaporator?.</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">Regards</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">Azly </p>
            </div>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: "Antoine Gautier" <<a moz-do-not-send="true"
            href="mailto:antoine.gautier@solamen.fr">antoine.gautier@solamen.fr</a>><br>
          To: <<a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
          Date: Fri, 30 Sep 2011 13:48:10 +0200<br>
          Subject: [TRNSYS-users] simulation studio crash when updating
          project<br>
          <div vlink="purple" link="blue" lang="FR">
            <div>
              <p class="MsoNormal"><span lang="EN-US">Dear all</span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">I cannot update my
                  project any more without crashing simulation studio
                  (*.tpf and *.b17 in attachment).</span></p>
              <p class="MsoNormal"><span lang="EN-US">Is there another
                  way to update the input list for Type56 so that I can
                  keep on working?</span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">Thanks a lot for
                  your help.</span></p>
              <p class="MsoNormal"><span lang="EN-US">Best regards</span></p>
              <p class="MsoNormal"><span style="COLOR: #404040"
                  lang="EN-US">--</span></p>
              <p class="MsoNormal"><span style="COLOR: #404040"
                  lang="EN-US">Antoine Gautier<br>
                  Solam</span><span style="COLOR: #70b221" lang="EN-US">en</span><span
                  style="COLOR: black" lang="EN-US"><br>
                </span><span style="COLOR: #404040" lang="EN-US"><a
                    moz-do-not-send="true"
                    href="tel:%2B33%206%2098%2078%2056%2046"
                    target="_blank" value="+33698785646">+33 6 98 78 56
                    46</a></span></p>
              <p class="MsoNormal"><span style="COLOR: #404040"
                  lang="EN-US">antoine.gautier@so</span><span
                  style="COLOR: #404040"><a moz-do-not-send="true"
                    href="http://lamen.fr/" target="_blank">lamen.fr</a></span><span
                  style="COLOR: black"></span></p>
              <p class="MsoNormal"> </p>
            </div>
          </div>
          <br>
          _______________________________________________<br>
          TRNSYS-users mailing list<br>
          <a moz-do-not-send="true"
            href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
          <a moz-do-not-send="true"
            href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
            target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>