Stefano,<br>
<span style="font-family:"Trebuchet
MS","sans-serif""><o:p></o:p></span>
<blockquote
cite="mid:EF650F471C832344BEBD07E6C0E0DB3F178241E0@abz02be.eurac.edu"
type="cite">
<div class="WordSection1">
<p class="MsoNormal"><span style="font-family:"Trebuchet
MS","sans-serif"">Why is not the button
“Divide surface” always present?<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-family: "Trebuchet
MS","sans-serif";">I am simulating a radiant
wall with “standard” features (pipe spacing 15 cm, pipe ext
diameter 2 cm, pipe thickness 2 mm).</span></p>
</div>
</blockquote>
the "divide surface" button is only needed if TRNBuild calculates
that the specific mass flow rate (kg/h.m2) of the floor you are
proposing is below the allowable limit. If the specific flow rate is
below 13 kg/h/m2 then you have to segment the floor into multiple
floors in series (and the "divide surface" button will become
active.<br>
<blockquote
cite="mid:EF650F471C832344BEBD07E6C0E0DB3F178241E0@abz02be.eurac.edu"
type="cite">
<div class="WordSection1">
<p class="MsoNormal"><span style="font-family:"Trebuchet
MS","sans-serif""><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-family:"Trebuchet
MS","sans-serif""><o:p> </o:p>Furthermore, I
have found no information about how the parameter “number of
fluid loops” is taken into account in the mathematical
model. Do you have any idea? <o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-family: "Trebuchet
MS","sans-serif";">Last question: how does
TRNSYS calculate the minimum allowed inlet mass flowrate in
case of a “number of fluid loops” greater than 1?</span></p>
</div>
</blockquote>
I am not sure about these but have forwarded the question on to our
Transsolar colleagues. I will let you know as soon as I hear back
from them.<br>
Best,<br>
David<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>