    Fanfan,<br>
      I am not aware of a way in TRNSYS to actually model the CO2
    concentration in the space. Typically, I have assumed that CO2
    concentration varies according to the occupancy of the space and I
    vary the mechanical ventilation rate according to the fraction of
    occupancy. This is, of course, a significant simplification. There
    are some components in the TESS Applications Library that allow you
    to set weekday, saturday, and sunday schedules using a
    slider-plugin. You can also define a few Type14s (one for weekdays,
    one for weekends, etc.) and then combine them using either an
    equation or the forcing function sequencer (Type41). If you have a
    very complex schedule, you can enter it into Excel as hourly values
    then use a Type9 data reader to read the excel file.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 9/25/2011 20:32, fanfan fanfan wrote:
    <blockquote
cite="mid:CAGQOnVD-uMf+mmgr+qrBT0RMHGkP89P+HyzcEawpZuw+Unasrw@mail.gmail.com"
      type="cite">
      <div>Dear trnsys users,</div>
      <div> </div>
      <div>I am try to use a PID Controller to modulate the indoor co2
        concentration. According to input signal there will be easy to
        output the control signal from the PID controller, however, co2
        source concentration must be varied base on working time
        schedule. How to input this proportion figure between the number
        of people and 24 hours by using trnsys tpye? For TRNbuild
        module, seems impossible to output value directly from schedule
        setting, therefore, I try to use type 14 to add the number of
        each hour. Unfortunately, it is difficult to integrate those
        type14 to form a time figure. </div>
      <div>Is there anyone have a experience on co2 base demand control,
        please give me some suggestions. </div>
      <div> </div>
      <div> </div>
      <div>Thank you very much.</div>
      <div> </div>
      <div>Best regards</div>
      <div> </div>
      <div>fanfan</div>
      <div> </div>
      <div><font face="tahoma,sans-serif">IGSES</font><font
          face="tahoma,sans-serif">, <span style="font-family:
            "Times New Roman","serif"; font-size:
            12pt; mso-fareast-font-family: "MS 明朝";
            mso-font-kerning: 1.0pt; mso-ansi-language: EN-US;
            mso-fareast-language: JA; mso-bidi-language: AR-SA;
            mso-bidi-font-weight: bold;">Kyushu
            University Japan</span></font></div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>