Mayank,<br>
If there is no sensible or latent load showing in the Type12
output, that is probably an indication that the building never
reached its cooling set point temperature. Understanding why you are
not getting a cooling load is the first place to start. Once you
have a cooling load then you need to use a component such as Type682
in the TESS Loads and Structures Library or an equation in your
input file to impose the cooling load on a water flow. This
component (or equation) will calculate the water return temperature
as a function of the load, the flow rate, and the supply
temperature. You'll then need to implement appropriate pipes, pumps,
buffer storage tanks, and the absorption chiller model in order to
meet the load (remove energy from the liquid stream to get the
return temperature back to the intended supply temperature).<br>
Regards,<br>
David<br>
<br>
On 9/20/2011 00:05, Mayank Bhatnagar wrote:
<blockquote cite="mid:4e781edf.6539440a.2ed3.ffff863f@mx.google.com"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 12 (filtered
medium)">
<style>
<!--
/* Font Definitions */
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
span.EmailStyle17
{mso-style-type:personal-compose;
font-family:"Calibri","sans-serif";
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
{page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="Section1">
<p class="MsoNormal">Good morning everyone,<o:p></o:p></p>
<p class="MsoNormal">I am in the starting stage of TRNSYS 16. I
have made simple
project using Type 45a, type 107, type 12b as single zone
building with weather
data type 109 and simulated it. I can’t attach cooling load of
building
with absorption chiller and results shows no sensible and
latent load in the
result.<o:p></o:p></p>
<p class="MsoNormal">Please guide me in this situation.<o:p></o:p></p>
<p class="MsoNormal">Thank you. <o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><b><span
style="font-size:12.0pt;font-family:"Times New
Roman","serif"">Mayank
Bhatnagar<o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:12.0pt;font-family:"Times New
Roman","serif"">M.Tech.
(Energy Engineering)<o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:12.0pt;font-family:"Times New
Roman","serif"">Malaviya
National Institute of Technology,<o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:12.0pt;font-family:"Times New
Roman","serif"">Jaipur
(INDIA)<o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:12.0pt;font-family:"Times New
Roman","serif"">contact
no.- +91-9983816468<o:p></o:p></span></b></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>