<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Mayank,<br>
      If there is no sensible or latent load showing in the Type12
    output, that is probably an indication that the building never
    reached its cooling set point temperature. Understanding why you are
    not getting a cooling load is the first place to start. Once you
    have a cooling load then you need to use a component such as Type682
    in the TESS Loads and Structures Library or an equation in your
    input file to impose the cooling load on a water flow. This
    component (or equation) will calculate the water return temperature
    as a function of the load, the flow rate, and the supply
    temperature. You'll then need to implement appropriate pipes, pumps,
    buffer storage tanks, and the absorption chiller model in order to
    meet the load (remove energy from the liquid stream to get the
    return temperature back to the intended supply temperature).<br>
    Regards,<br>
     David<br>
    <br>
    On 9/20/2011 00:05, Mayank Bhatnagar wrote:
    <blockquote cite="mid:4e781edf.6539440a.2ed3.ffff863f@mx.google.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
      <div class="Section1">
        <p class="MsoNormal">Good morning everyone,<o:p></o:p></p>
        <p class="MsoNormal">I am in the starting stage of TRNSYS 16. I
          have made simple
          project using Type 45a, type 107, type 12b as single zone
          building with weather
          data type 109 and simulated it. I can’t attach cooling load of
          building
          with absorption chiller and results shows no sensible and
          latent load in the
          result.<o:p></o:p></p>
        <p class="MsoNormal">Please guide me in this situation.<o:p></o:p></p>
        <p class="MsoNormal">Thank you. <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">Mayank
              Bhatnagar<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">M.Tech.
              (Energy Engineering)<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">Malaviya
              National Institute of Technology,<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">Jaipur
              (INDIA)<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif"">contact
              no.- +91-9983816468<o:p></o:p></span></b></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>