    Mike,<br>
      I think your simulation is correct (nice job, incidentally, in
    setting it up). I think the "problem" is that your collector is just
    too small to collect enough energy to add to the tank. As a result,
    whenever there is flow through the collector, the temperature rise
    is so small that the outlet temperature basically equals the inlet
    temperature and the controller decides to turn off. Imagine the
    limit; if you had a collector that had zero area, it couldn't
    collect any energy; it would just a pipe of water sitting in the
    sun. When there is no flow, the pipe heats up, the water gets hot,
    and the controller decides to turn on the pump. However, as soon as
    the flow starts, the water comes back to the tank at the same
    temperature with which it left. I doubled the area of your collector
    and suddenly it all went stable. <br>
    <br>
      I did clean up the connections between the weather processor and
    the collector; there are a few more solar radiation connections that
    need to be made (diffuse solar, incidence angle, etc.). You also
    need to use Type69 to get the sky temperature. Alternatively (and
    much preferably) you should change Type109 for Type15; Type15 also
    reads TMY2/Meteonorm data files but has a number of advantages over
    Type109 (including calculating the effective sky temperature
    internally and outputting the wind speed.<br>
    <br>
    Regards,<br>
     David<br>
    <br>
    On 9/22/2011 15:50, Michael Bissett wrote:
    <blockquote
cite="mid:CAEWo59-f+cF2WEdKARo4-JUu-j4xF7a+Fs4kNautrisYq+n5Zw@mail.gmail.com"
      type="cite">I have taken your advice and made the timestep,
      0.125hr
      <div><br>
      </div>
      <div>Still I cannot get it to work. it is still switching on the
        time step instead of the dead-band temp.</div>
      <div><br>
      </div>
      <div>Mike<br>
        <br>
        <div class="gmail_quote">
          On Wed, Sep 21, 2011 at 3:33 PM, Matt Duffy <span dir="ltr"><<a
              moz-do-not-send="true" href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex;">
            <br>
            Dear Michael,<br>
            <br>
            Please make sure that you are using a reasonable timestep
            such as 0.125 hr (type in terms of hours to avoid problems
            with the Studio's minute conversion trucation). Also, make
            sure that you have the latest TRNSYS and TESS Libraries
            versions as well.<br>
            <br>
            Best regards,<br>
            <font color="#888888"><br>
              Matt Duffy<br>
              <br>
            </font>
            <div style="background-repeat:repeat-x">
              <div>
                <div class="h5"><strong>----- Original Message -----</strong><br>
                  <strong>From:</strong> "Michael Bissett" <<a
                    moz-do-not-send="true"
                    href="mailto:mikebiscuit@gmail.com" target="_blank">mikebiscuit@gmail.com</a>>
                  <br>
                  <strong>Sent:</strong> Tue, September 20, 2011 12:44<br>
                  <strong>Subject:</strong> Re: [TRNSYS-users] Type 2b
                  controller dead band problem.<br>
                  <br>
                </div>
              </div>
              <table cellspacing="5" width="100%">
                <tbody>
                  <tr>
                    <td>
                      <div>
                        <div>
                          <div>
                          </div>
                          <div class="h5"> Hi 
                            <div> </div>
                            <div>I have read the information, I have
                              tried to increase parameter 1, I have also
                              looped the controller to its self. Still
                              it does not work</div>
                            <div>I have also tried changing many other
                              parameters and have spent a lot of time on
                              this problem. still with no luck.</div>
                            <div> </div>
                            <div>Any other suggestions?</div>
                            <div> </div>
                            <div>Mike</div>
                            <div> </div>
                            <div> </div>
                            <div> </div>
                            <div><br>
                              <div class="gmail_quote">On Tue, Sep 20,
                                2011 at 1:59 PM, Angel Carrera <span
                                  dir="ltr"><<a
                                    moz-do-not-send="true"
                                    href="mailto:angel.carrera@aiguasol.coop"
                                    target="_blank">angel.carrera@aiguasol.coop</a>></span>
                                wrote:<br>
                                <blockquote style="margin:0pt 0pt 0pt
                                  0.8ex;border-left:1px solid rgb(204,
                                  204, 204);padding-left:1ex"
                                  class="gmail_quote"><br>
                                  Mike,<br>
                                  <br>
                                  you should connect the output control
                                  function of the controller to its own
                                  input control function (Input number
                                  4). Also, you should increase the
                                  value of parameter 1, to the default
                                  value at least (the influence of this
                                  parameter is explained at the type 2
                                  documentation, I recommend you to read
                                  it, together with the generic section
                                  for controllers at the trnsys help)<br>
                                  <br>
                                  Regards<br>
                                  <br>
                                  Angel<br>
                                  <br>
                                  <br>
                                  <div class="gmail_quote">
                                    <div>
                                      <div> </div>
                                      <div>2011/9/19 Michael Bissett <span
                                          dir="ltr"><<a
                                            moz-do-not-send="true"
                                            href="mailto:mikebiscuit@gmail.com"
                                            target="_blank">mikebiscuit@gmail.com</a>></span></div>
                                    </div>
                                    <blockquote style="margin:0pt 0pt
                                      0pt 0.8ex;border-left:1px solid
                                      rgb(204, 204,
                                      204);padding-left:1ex"
                                      class="gmail_quote">
                                      <div>
                                        <div> </div>
                                        <div>Dear Trnsys
                                          <div> </div>
                                          <div>I am experiencing
                                            problems with a simple<b>
                                              type 2b controller</b>.</div>
                                          <div> </div>
                                          <div>I am using a solar
                                            collector type 564b</div>
                                          <div> </div>
                                          <div>I am trying to compare
                                            the temperature of the
                                            output of the collector with
                                            output of the tank, getting
                                            a temperature difference. I
                                            have set the dead band from
                                            4-10 degrees C.</div>
                                          <div> </div>
                                          <div>In the simulation as the
                                            temperature rises to
                                            10degrees difference, the
                                            control signal is 1
                                            switching the pump on
                                            correctly. but after this
                                            the controller only switches
                                            every time step. I have
                                            tried shortening the time
                                            step... and changing other
                                            parameters.. still with no
                                            success.</div>
                                          <div> </div>
                                          <div>I have attached the file.</div>
                                          <div> </div>
                                          <div>Yours Sincerely</div>
                                          <div> </div>
                                          <div>Mike Bissett</div>
                                          <div> </div>
                                          <div>Department of Electrical
                                            Engineering</div>
                                          <div>University of Cape Town </div>
                                          <div>
                                            South Africa</div>
                                        </div>
                                      </div>
_______________________________________________<br>
                                      TRNSYS-users mailing list<br>
                                      <a moz-do-not-send="true"
                                        href="mailto:TRNSYS-users@cae.wisc.edu"
                                        target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
                                      <a moz-do-not-send="true"
                                        href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                                        target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
                                      <br>
                                    </blockquote>
                                  </div>
                                  <br>
                                  <br clear="all">
                                  <br>
                                  -- <br>
                                  <font style="color:rgb(0, 102, 0)"
                                    size="4"><b>Àngel Carrera</b></font><br
                                    style="color:rgb(0, 102, 0)">
                                  <br style="color:rgb(0, 102, 0)">
                                  <b style="color:rgb(0, 102, 0)">Responsable
                                    I+D<br>
                                    Àrea tècnica</b><br
                                    style="color:rgb(0, 102, 0)">
                                  <img moz-do-not-send="true" alt=""><br>
                                  <span style="color:rgb(0, 153, 0)">Sistemes
                                    Avançats d'Energia Solar Tèrmica
                                    SCCL</span><br style="color:rgb(0,
                                    153, 0)">
                                  <span style="color:rgb(0, 153, 0)">C/
                                    Roger de Llúria, 29 3r 2a 08009
                                    Barcelona</span><br
                                    style="color:rgb(0, 153, 0)">
                                  <span style="color:rgb(0, 153, 0)">Tel:
                                    <a moz-do-not-send="true"
                                      value="+34933424755"
                                      href="tel:%28%2B34%29%2093%20342%2047%2055"
                                      target="_blank">(+34) 93 342 47 55</a>
                                    Fax: <a moz-do-not-send="true"
                                      value="+34933424756"
                                      href="tel:%28%2B34%29%2093%20342%2047%2056"
                                      target="_blank">(+34) 93 342 47 56</a></span><br>
                                  <font color="#888888"><br>
                                    <a moz-do-not-send="true"
                                      href="mailto:angel.carrera@aiguasol.coop"
                                      target="_blank">angel.carrera@aiguasol.coop</a><br>
                                    <a moz-do-not-send="true"
                                      href="http://www.aiguasol.coop/"
                                      target="_blank">http://www.aiguasol.coop</a></font><br>
                                </blockquote>
                              </div>
                            </div>
                          </div>
                        </div>
                        <hr noshade="noshade" size="1">
                        <div class="im">
                          <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
                        </div>
                      </div>
                    </td>
                  </tr>
                </tbody>
              </table>
            </div>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>