<p>Dear all,</p>
<p><br>      I have the questions about Active Layer:<br>1. The floor heating area is 27.2 m^2 in our test room, but the floor area is 40 m^2. Like this situation, Can I set two floors in TRNBuild? One is the floor  with 40 m^2, another is floor with 27.2 m^2 active layer? Or others?</p>

<p><br>2. I only know the power of this floor heating 1400 W. How can I define it? Or by what method to stand for this power?</p>
<p><br>     Many thanks in advance!</p>
<p><br>     Br.</p>
<p><br>     wang<br><br></p>
<div class="gmail_quote">2011/9/23 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br>       <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br>       <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>or, via email, send a message with subject or body 'help' to<br>
       <a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br>       <a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br><br>Today's Topics:<br><br>  1. Re: TRnsys3D skecthup plugin (Thibaut VITTE)<br>  2. Re: Type73 - Flat-Plate Collector (Igor Grujic)<br>
  3. Re: Type 2b controller dead band problem. (Michael Bissett)<br><br><br>---------- 已转发邮件 ----------<br>From: Thibaut VITTE <<a href="mailto:thibaut.vitte@h3c-energies.fr">thibaut.vitte@h3c-energies.fr</a>><br>To: <a href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>, <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Thu, 22 Sep 2011 19:49:03 +0200<br>Subject: Re: [TRNSYS-users] TRnsys3D skecthup plugin<br>Dear Matt,<br><br>First, I may have sound a little bit agressive ;-) , and I'm sorry but I was SO frustated to have lost 3 days of work before returning to the old method...<br>
<br>Yes I know quite all the tricks you've said, and I did read the manual, and did a small building, and I perfectly know I would have been able to do so in a training course within 2 hours.<br><br>But the problem is for a bigger building !! (even with the manual next to the keyboard...)<br>
I think my problem is that I (still?) don't know how to draw perfectly from the first click in sketchup, and that I have to erase, cancel, etc. And then, it is a big mess.<br>Anyway, thanks for taking into account our concerns, I have my answer that some people manage to be efficient with Trnsys3D!<br>
<br>Best<br>Thibaut<br><br><br><br><br>---------- 已转发邮件 ----------<br>From: "Igor Grujic" <<a href="mailto:igor.g@gmx.at">igor.g@gmx.at</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Thu, 22 Sep 2011 19:50:44 +0200<br>Subject: Re: [TRNSYS-users] Type73 - Flat-Plate Collector<br>Dear Matt,<br><br>Thanks al lot for your quick reply, but I have one more question.<br><br>If I change the timestep to 0.125 (or smaller) what’s about the weather-values? (Those are generated for 1 year (8760 hours) in 1-hour-steps).<br>
Need to simulate a one-year-consumption of a house for which a have the hourly usage-values. Changing the time step will falsify the results, right?<br>(But I just gonna try it out)<br><br>Thanks again for the help<br><br>
Best regards,<br>Igor<br><br>-------- Original-Nachricht --------<br>> Datum: Wed, 21 Sep 2011 10:15:24 -0500 (CDT)<br>> Von: "Matt Duffy" <<a href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>><br>
> An: "Igor Grujic" <<a href="mailto:igor.g@gmx.at">igor.g@gmx.at</a>>, <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>> Betreff: Re: [TRNSYS-users] Type73 - Flat-Plate Collector<br>
<br>> Dear Igor,First of all, please make sure that your timestep is small -<br>> probably under 0.125 hour. Type Type2b collector is recommended for a<br>> simulation like this. Honestly, there are few simulations where one should use<br>
> Powell's method such as a PV connected to a pump. If you continue to have<br>> problems, please feel free to send to your local TRNSYS distributor or me.Best<br>> regards,Matt Duffy   ----- Original Message -----From: &quot;Igor<br>
> Grujic&quot; >;<a href="mailto:igor.g@gmx.at">igor.g@gmx.at</a><br><br>--<br>NEU: FreePhone - 0ct/min Handyspartarif mit Geld-zurück-Garantie!<br>Jetzt informieren: <a href="http://www.gmx.net/de/go/freephone" target="_blank">http://www.gmx.net/de/go/freephone</a><br>
<br><br><br>---------- 已转发邮件 ----------<br>From: Michael Bissett <<a href="mailto:mikebiscuit@gmail.com">mikebiscuit@gmail.com</a>><br>To: <a href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a><br>Date: Thu, 22 Sep 2011 22:50:09 +0200<br>
Subject: Re: [TRNSYS-users] Type 2b controller dead band problem.<br>I have taken your advice and made the timestep, 0.125hr 
<div><br></div>
<div>Still I cannot get it to work. it is still switching on the time step instead of the dead-band temp.</div>
<div><br></div>
<div>Mike<br><br>
<div class="gmail_quote">On Wed, Sep 21, 2011 at 3:33 PM, Matt Duffy <span dir="ltr"><<a href="mailto:duffy@tess-inc.com" target="_blank">duffy@tess-inc.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote"><br>Dear Michael,<br><br>Please make sure that you are using a reasonable timestep such as 0.125 hr (type in terms of hours to avoid problems with the Studio's minute conversion trucation). Also, make sure that you have the latest TRNSYS and TESS Libraries versions as well.<br>
<br>Best regards,<br><font color="#888888"><br>Matt Duffy<br><br></font>
<div style="BACKGROUND-REPEAT: repeat-x">
<div>
<div></div>
<div><strong>----- Original Message -----</strong><br><strong>From:</strong> "Michael Bissett" <<a href="mailto:mikebiscuit@gmail.com" target="_blank">mikebiscuit@gmail.com</a>> <br><strong>Sent:</strong> Tue, September 20, 2011 12:44<br>
<strong>Subject:</strong> Re: [TRNSYS-users] Type 2b controller dead band problem.<br><br></div></div>
<table cellspacing="5" width="100%">
<tbody>
<tr>
<td>
<div>
<div>
<div></div>
<div>Hi  
<div> </div>
<div>I have read the information, I have tried to increase parameter 1, I have also looped the controller to its self. Still it does not work</div>
<div>I have also tried changing many other parameters and have spent a lot of time on this problem. still with no luck.</div>
<div> </div>
<div>Any other suggestions?</div>
<div> </div>
<div>Mike</div>
<div> </div>
<div> </div>
<div> </div>
<div><br>
<div class="gmail_quote">On Tue, Sep 20, 2011 at 1:59 PM, Angel Carrera <span dir="ltr"><<a href="mailto:angel.carrera@aiguasol.coop" target="_blank">angel.carrera@aiguasol.coop</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0pt 0pt 0pt 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote"><br>Mike,<br><br>you should connect the output control function of the controller to its own input control function (Input number 4). Also, you should increase the value of parameter 1, to the default value at least (the influence of this parameter is explained at the type 2 documentation, I recommend you to read it, together with the generic section for controllers at the trnsys help)<br>
<br>Regards<br><br>Angel<br><br><br>
<div class="gmail_quote">
<div>
<div> </div>
<div>2011/9/19 Michael Bissett <span dir="ltr"><<a href="mailto:mikebiscuit@gmail.com" target="_blank">mikebiscuit@gmail.com</a>></span></div></div>
<blockquote style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0pt 0pt 0pt 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>
<div> </div>
<div>Dear Trnsys 
<div> </div>
<div>I am experiencing problems with a simple<b> type 2b controller</b>.</div>
<div> </div>
<div>I am using a solar collector type 564b</div>
<div> </div>
<div>I am trying to compare the temperature of the output of the collector with output of the tank, getting a temperature difference. I have set the dead band from 4-10 degrees C.</div>
<div> </div>
<div>In the simulation as the temperature rises to 10degrees difference, the control signal is 1 switching the pump on correctly. but after this the controller only switches every time step. I have tried shortening the time step... and changing other parameters.. still with no success.</div>

<div> </div>
<div>I have attached the file.</div>
<div> </div>
<div>Yours Sincerely</div>
<div> </div>
<div>Mike Bissett</div>
<div> </div>
<div>Department of Electrical Engineering</div>
<div>University of Cape Town </div>
<div>South Africa</div></div></div>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br><font style="COLOR: rgb(0,102,0)" size="4"><b>Àngel Carrera</b></font><br style="COLOR: rgb(0,102,0)"><br style="COLOR: rgb(0,102,0)"><b style="COLOR: rgb(0,102,0)">Responsable I+D<br>
Àrea tècnica</b><br style="COLOR: rgb(0,102,0)"><img alt=""><br><span style="COLOR: rgb(0,153,0)">Sistemes Avançats d'Energia Solar Tèrmica SCCL</span><br style="COLOR: rgb(0,153,0)"><span style="COLOR: rgb(0,153,0)">C/ Roger de Llúria, 29 3r 2a 08009 Barcelona</span><br style="COLOR: rgb(0,153,0)">
<span style="COLOR: rgb(0,153,0)">Tel: <a href="tel:%28%2B34%29%2093%20342%2047%2055" target="_blank" value="+34933424755">(+34) 93 342 47 55</a> Fax: <a href="tel:%28%2B34%29%2093%20342%2047%2056" target="_blank" value="+34933424756">(+34) 93 342 47 56</a></span><br>
<font color="#888888"><br><a href="mailto:angel.carrera@aiguasol.coop" target="_blank">angel.carrera@aiguasol.coop</a><br><a href="http://www.aiguasol.coop/" target="_blank">http://www.aiguasol.coop</a></font><br></blockquote>
</div></div></div></div>
<hr size="1" noshade>

<div><pre>_______________________________________________
TRNSYS-users mailing list
<a>TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre></div></div></td></tr></tbody></table></div></blockquote></div><br></div><br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br><br></blockquote></div><br>