<br>Mike,<br><br>you should connect the output control function of the controller to its own input control function (Input number 4). Also, you should increase the value of parameter 1, to the default value at least (the influence of this parameter is explained at the type 2 documentation, I recommend you to read it, together with the generic section for controllers at the trnsys help)<br>
<br>Regards<br><br>Angel<br><br><br><div class="gmail_quote">2011/9/19 Michael Bissett <span dir="ltr"><<a href="mailto:mikebiscuit@gmail.com">mikebiscuit@gmail.com</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
Dear Trnsys<div><br></div><div>I am experiencing problems with a simple<b> type 2b controller</b>.</div><div><br></div><div>I am using a solar collector type 564b</div><div><br></div><div>I am trying to compare the temperature of the output of the collector with output of the tank, getting a temperature difference. I have set the dead band from 4-10 degrees C.</div>

<div><br></div><div>In the simulation as the temperature rises to 10degrees difference, the control signal is 1 switching the pump on correctly. but after this the controller only switches every time step. I have tried shortening the time step... and changing other parameters.. still with no success.</div>

<div><br></div><div>I have attached the file.</div><div><br></div><div>Yours Sincerely</div><div><br></div><div>Mike Bissett</div><div><br></div><div>Department of Electrical Engineering</div><div>University of Cape Town </div>

<div>South Africa</div>
<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br><font style="color:rgb(0, 102, 0)" size="4"><b>Àngel Carrera</b></font><br style="color:rgb(0, 102, 0)"><br style="color:rgb(0, 102, 0)"><b style="color:rgb(0, 102, 0)">Responsable I+D<br>
Àrea
 tècnica</b><br style="color:rgb(0, 102, 0)"><img src="http://www.aiguasol.coop/img/logo.gif"><br><span style="color:rgb(0, 153, 0)">Sistemes Avançats d'Energia Solar 
Tèrmica SCCL</span><br style="color:rgb(0, 153, 0)">
<span style="color:rgb(0, 153, 0)">C/ Roger de Llúria, 29 3r 2a 08009 
Barcelona</span><br style="color:rgb(0, 153, 0)"><span style="color:rgb(0, 153, 0)">Tel: (+34) 93 342 47 55 Fax: (+34) 93 342 47 56</span><br><font color="#888888"><br>
<a href="mailto:angel.carrera@aiguasol.coop" target="_blank">angel.carrera@aiguasol.coop</a><br><a href="http://www.aiguasol.coop/" target="_blank">http://www.aiguasol.coop</a></font><br>