    Erwan,<br>
      Type655 does consider the effect of ambient temperature; it is one
    of the two variables in the performance data file (the other
    variable is the desired chilled water outlet temperature). What you
    might be seeing, however, is that the routine that reads the
    performance data is able to interpolate performance within the range
    of data given but it cannot extrapolate beyond the range. If the
    highest ambient temperature in the data file is 30C and all of the
    ambient temperatures during the simulation are above 30C then you
    will always get the capacity and COP that correspond to to the
    performance at 30C. <br>
    <br>
      If that does not correct the problem, please send me the *.tpf
    file and the chiller data files that you are using and I will see if
    I can determine the cause of the problem.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 8/24/2011 06:45, LIBIOT, Erwan wrote:
    <blockquote
cite="mid:E550451A0F047D4B83593FA050FE6D940389B9D4@BCNVMSB007.bouygues-construction.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"Préformaté HTML Car";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";}
span.ecxhps
        {mso-style-name:ecxhps;}
span.PrformatHTMLCar
        {mso-style-name:"Préformaté HTML Car";
        mso-style-priority:99;
        mso-style-link:"Préformaté HTML";
        font-family:Consolas;}
span.EmailStyle21
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);" lang="EN-US">Dears all,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);" lang="EN-US">I'm using the type 655 "chilled
            water flow rate" from TESS library. First, I noticed an
            inversion between CAPACITY ratio and COP ratio in the
            external file (containing the chiller performance data). <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);" lang="EN-US">Secondly, here my problem; this type
            do not consider the ambient temperature in the chiller
            capacity and COP calculations. In fact, this model always
            choose CAP and COP ratio values corresponding to the highest
            ambient temperature for a chilled water temperature. So,
            have you got an idea about how can I figure out this issue?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);">Thanks you<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);"><br>
            Erwan Libiot<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size: 11pt; font-family:
            "Calibri","sans-serif"; color: rgb(31,
            73, 125);"><o:p> </o:p></span></p>
        <div style="border-right: medium none; border-width: 1pt medium
          medium; border-style: solid none none; border-color: rgb(181,
          196, 223) -moz-use-text-color -moz-use-text-color; padding:
          3pt 0cm 0cm;">
          <p class="MsoNormal"><b><span style="font-size: 10pt;
                font-family: "Tahoma","sans-serif";">De :</span></b><span
              style="font-size: 10pt; font-family:
              "Tahoma","sans-serif";"> Matt Duffy
              [<a class="moz-txt-link-freetext" href="mailto:duffy@tess-inc.com">mailto:duffy@tess-inc.com</a>] <br>
              <b>Envoyé :</b> mardi 2 août 2011 14:49<br>
              <b>À :</b> luis Carlos vela garcia;
              <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
              <b>Objet :</b> Re: [TRNSYS-users] problem type 655
              (chilled water flow rate)<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal" style="margin-bottom: 12pt;">Dear Luis
          Carlos Vela,<br>
          <br>
          That is fixed for TESS Libraries version 17.01 (you may see
          the version of the TESS Libraries that you have by viewing the
          names of their external DLL's in the ".\UserLib\ReleaseDLLs"
          directory or by looking at the 'Readme.html' file in the
          ".\Tess Models" directory). Thus, please make sure that you
          are using that version.<br>
          <br>
          Best regards,<br>
          <br>
          Matt Duffy<br>
          <br>
          <o:p></o:p></p>
        <div>
          <p class="MsoNormal" style="margin-bottom: 12pt;"><strong>-----
              Original Message -----</strong><br>
            <strong>From:</strong> "luis Carlos vela garcia"
            <a class="moz-txt-link-rfc2396E" href="mailto:lcarlosvg@hotmail.es"><lcarlosvg@hotmail.es></a> <br>
            <strong>Sent:</strong> Fri, July 29, 2011 16:24<br>
            <strong>Subject:</strong> [TRNSYS-users] problem type 655
            (chilled water flow rate)<o:p></o:p></p>
          <table class="MsoNormalTable" style="width: 100%;"
            width="100%" border="0" cellpadding="0" cellspacing="5">
            <tbody>
              <tr>
                <td style="padding: 0.75pt;">
                  <div>
                    <div>
                      <div>
                        <div>
                          <p class="MsoNormal"><br>
                            <span class="ecxhps"><span lang="EN">good
                                day.</span></span><o:p></o:p></p>
                        </div>
                        <div>
                          <p class="MsoNormal"><span class="ecxhps"><span
                                lang="EN">My name is Luis Carlos Vela
                                colmbiano am a college student and
                                Francisco José de Caldas District, has
                                the license lacual TRNSYS V17. I am
                                currently developing my graduation
                                project and I have questions,</span></span><span
                              lang="EN"><br>
                              <span class="ecxhps"> </span><br>
                              <span class="ecxhps"> </span><br>
                              <span class="ecxhps"> </span><br>
                              <span class="ecxhps"> TranSys attached
                                image</span></span><o:p></o:p></p>
                        </div>
                        <div>
                          <p class="MsoNormal"> <o:p></o:p></p>
                        </div>
                        <div>
                          <p class="MsoNormal"> <o:p></o:p></p>
                        </div>
                        <div>
                          <p class="MsoNormal"><span class="ecxhps"><span
                                lang="EN">when I choose the type chiller
                                655 and I will enter the input data see
                                the following problem.</span></span><span
                              lang="EN"><br>
                              <span class="ecxhps">Water chiller units
                                are degrees Celsius flexible rate, so my
                                question is what units should I enter in
                                this box as Celsius tablets are not
                                units! of flow.</span></span><o:p></o:p></p>
                        </div>
                      </div>
                    </div>
                    <div class="MsoNormal" style="text-align: center;"
                      align="center">
                      <hr style="color: rgb(160, 160, 160);"
                        width="100%" align="center" noshade="noshade"
                        size="1"></div>
                    <pre><o:p> </o:p></pre>
                    <pre>_______________________________________________<o:p></o:p></pre>
                    <pre>TRNSYS-users mailing list<o:p></o:p></pre>
                    <pre><a moz-do-not-send="true" href="javascript:bodyCreateMail('TRNSYS-users%40cae.wisc.edu')">TRNSYS-users@cae.wisc.edu</a><o:p></o:p></pre>
                    <pre><a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><o:p></o:p></pre>
                  </div>
                </td>
              </tr>
            </tbody>
          </table>
          <p class="MsoNormal"><o:p> </o:p></p>
        </div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>