Dear Jochen,<br><br>Danke für Deine Antwort. <br><br>I have tried to do what you told me, and i got the right pictures . But i found something very strange.<br>1. The simulation of the whole July is not the same like just the 23. July , and there is a very big difference. Still i don't know why. <br>
2. I have tried to caculate the cold load with vdi 2078 in excel, there is also a very big difference . I think maybe it's because of the gains in TRNBUILD. i want 2 persons, 2 computers and a light with 100W. So i made the gains just like what the picture shows. <br>
<br>Can anyone help me?<br>
<br>
Thanks and best regards,<br>
<br>
Leona<br><br><br><br><div class="gmail_quote">2011/8/8 Jochen Doell <span dir="ltr"><<a href="mailto:jochen.doell@ise.fraunhofer.de">jochen.doell@ise.fraunhofer.de</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
Dear Leona,<br>
<br>
you can do just one thing at a time: Simulate the free floating room temperatures when no heat/cold is supplied OR simulate the cold/heat demand when the room is kept at certain temperature.<br>
<br>
What you did is a simulation without a heating/cooling system, so you got the temperature profile.<br>
<br>
You need to turn on the aux cooling system in TRNBUILD (assuming you use type 56) and give the building a desired maximum temperature (constant value, input or schedule). When the room temperature reaches the maximum temperature, you cooling system will start to operate, keeping the room below the temperature. Q_sens is the (negative) cooling demand.<br>
<br>
Best regards,<br>
Jochen<br>
<br>
Am 20:59, schrieb ͫͫ:<div><div></div><div class="h5"><br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Dear all,<br>
<br>
i want to make a building model for the simulation of cold load.It is just<br>
one room with one external wall and 2 unair-conditioned next rooms(one is<br>
the lobby the other is the upper room).<br>
<br>
Questions are<br>
1. I tried to run the simulation, but the cold load is always 0, like the<br>
picture in the mail.<br>
2. i think the temp. is also not correct ,but i don't know why. ps. i just<br>
want to simulate the temp.and the cold load in 23. July in the zone.<br>
<br>
Can anyone help me?<br>
<br>
Thanks and best regards,<br>
<br>
Leona<br>
<br>
</blockquote>
<br></div></div>
-- <br>
______________________________<u></u>___________________<br>
<br>
Dipl.-Ing. (FH) Jochen Döll<br>
Division Thermal Systems and Buildings<br>
<br>
Fraunhofer-Institut für Solare Energiesysteme ISE<br>
Heidenhofstrasse 2, 79110 Freiburg, Germany<br>
<br>
Phone: <a href="tel:%2B49%20%28761%29%204588-5468" value="+4976145885468" target="_blank">+49 (761) 4588-5468</a> Fax: <a href="tel:%2B49%20%28761%29%204588-9000" value="+4976145889000" target="_blank">+49 (761) 4588-9000</a><br>
<font color="#888888">
<a href="mailto:jochen.doell@ise.fraunhofer.de" target="_blank">jochen.doell@ise.fraunhofer.de</a><br>
<a href="http://www.ise.fraunhofer.de" target="_blank">www.ise.fraunhofer.de</a><br>
______________________________<u></u>___________________<br>
<br>
</font></blockquote></div><br>