<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#ffffff">
    Igor,<br>
      Matt's suggestion to use type9 is good. I would only add that the
    100 point limitation is just imposed by the Studio and by the way
    that the Type14 proforma is configured. Type14 itself can use as
    many points as you like. If you need to change the limitation,
    you'll have to edit the Type14 proforma (change the "max value" of
    the question that determines the size of the cycle) and then do an
    Edit: Replace on all instances of Type14 that need more than 100
    points.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    On 8/2/2011 09:08, Matt Duffy wrote:
    <blockquote
      cite="mid:1312294088.v2.mailanyonewebmail-331886@fuseweb2d"
      type="cite"><br>
      Dear Igor,<br>
      <br>
      I would strongly advise you not to use Type14 to do that! Type14
      is great for a few points but not 8760! That is why there is the
      Type9 data reader. Simply create the 8760 schedule as a text file
      and reference that file in the 'External Files' tab of Type9.
      Please see the examples for reference.<br>
      <br>
      Best regards,<br>
      <br>
      Matt Duffy<br>
      <br>
      <!--replyfwdwrap-->
      <div style="background-image:
        url("http://webmail.fusemail.com/de/r_bg_img.gif");
        background-position: center top; background-repeat: repeat-x;"><strong>-----
          Original Message -----</strong><br>
        <strong>From:</strong> "Igor Grujic" <a class="moz-txt-link-rfc2396E" href="mailto:igor.g@gmx.at"><igor.g@gmx.at></a> <br>
        <strong>Sent:</strong> Tue, August 2, 2011 8:50<br>
        <strong>Subject:</strong> [TRNSYS-users] Type14h - max. number
        of points<br>
        <br>
        <table width="100%" cellspacing="5">
          <tbody>
            <tr>
              <td>
                <div class="PrivateMsgDiv">
                  <pre>Dear users,

Is it possible to change the maximal number of points to more than 100?

I have a flow rate which changes hourly during the entire year, so that I thought I
may use the Type14h to consider that changes with a function, but for that I need
8760 points (one for each hour). 

Thanks in advance

Kind regards,
Igor

-- 
NEU: FreePhone - 0ct/min Handyspartarif mit Geld-zurück-Garantie!                
Jetzt informieren: <a moz-do-not-send="true" target="_blank" href="http://www.gmx.net/de/go/freephone">http://www.gmx.net/de/go/freephone</a>
_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="javascript:bodyCreateMail('TRNSYS-users%40cae.wisc.edu')">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" target="_blank" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
                </div>
              </td>
            </tr>
          </tbody>
        </table>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>