<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#ffffff">
    Rakesh,<br>
      It looks as though you are passing some incorrect variables back
    to the building model and that the variables you are passing
    (T_HEATING, T_COOLING, and RH_COOLING) are defined in the building
    but aren't actually implemented in your zone. The inputs that you
    need to pass from the furnace model to the building model are the
    furnace's outlet air temperature, RH, and flow rate. You will need
    to open TRNBuild and define a VENTILATION type in your zone. A
    couple hints:<br>
    <br>
    1. Specify that you are going to provide air flow rate as a mass
    flow and change the flow rate from a constant value (the default) to
    an input.  Give the input a name like MVNT_55FC41<br>
    2. Specify that you are going to provide the temperature of the
    ventilation air as an input. Give the input a name like TVNT_55FC41.<br>
    3. Specify that you are going to provide the humidity of the
    ventilation air as an input and as an RH (which is the default).
    Give the input a name like RHVNT_55FC41.<br>
    <br>
    When Type56 talks about ventilation, it means a stream of air, not
    necessarily the zone's fresh or outdoor air as is sometimes
    traditional in the US.<br>
    best,<br>
     David<br>
    <br>
    <br>
    On 7/26/2011 15:08, Rakesh Kaushik wrote:
    <blockquote
cite="mid:CAL+Gj7GSHgtrj-mzMLZy-dvJECRfeByBqZ7YywmU19mJ85Wp9Q@mail.gmail.com"
      type="cite">Dear trnsys user,<br>
      <br>
      I created a type-56 3D model for a zone, and I introduced the type
      108 thermostat to monitor the temperature in the zone with the
      help of fan, furnace and auxiliary cooling unit, and I need little
      help to figure what I am doing wrong I attached my model with this
      email.<br>
      <br>
      Thank you very much in advance   <br>
      <br>
      Regards,<br>
      <div><b>Rakesh Kaushik</b></div>
      <div>Graduate Student</div>
      <div>Department of Mechanical Engineering</div>
      <div>University of Dayton</div>
      <div><a moz-do-not-send="true"
          href="mailto:rakeshkaushik25@gmail.com" target="_blank">rakeshkaushik25@gmail.com</a></div>
      <div>Cell: 937-239-5924</div>
      <br>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>