    <font size="-1"><font face="Arial">Dear Marcus,<br>
        <br>
      </font></font><font size="-1"><font face="Arial"></font></font><font
      size="-1"><font face="Arial">The error you get with automatic heat
        transfer calculation is not linked with your orientation
        definition and connection with type56, which seems to be fine. <br>
        <br>
        This is due to an external wall or window in Type56, which have
        its convective heat transfer coefficient calculated automaticaly
        on its back side.<br>
        <br>
        To deal with that issue, check all of your wall defintion in
        Wall type manager and be sure that </font></font><font
      size="-1"><font face="Arial"> convective heat transfer coefficient
        of back</font></font><font size="-1"><font face="Arial"> sides
        of your exernal wall are not defined as automatic.<br>
      </font></font><font size="-1"><font face="Arial"><br>
        Best regards<br>
      </font></font>
    <div class="moz-signature">
      <hr align="LEFT" color="#3300FF" size="2" width="450">
      <font color="#DC143C" face="CALIBRI" size="2"> Je serai absent du
        1er au 28 Août 2011
        <table border="0">
          <tbody>
            <tr>
              <td rowspan="3" width="120">
                <center><a href="http://www.itf.biz"><img
                      src="cid:part1.07010107.04070505@itf.biz"
                      alt="www.itf.biz" border="0" height="103"
                      width="66"></a><br>
                  <font color=" #0000FF" face="CALIBRI" size="1"><a
                      href="http://www.itf.biz">www.itf.biz</a></font></center>
              </td>
              <td colspan="2"><font color="#000000" face="CALIBRI"
                  size="2">Adrien JEZEQUEL<br>
                  Simulations Thermiques Dynamiques</font></td>
            </tr>
            <tr>
              <td align="LEFT"> <font color="#0000FF" face="CALIBRI"
                  size="4"><b>ITF</b></font><br>
              </td>
              <td><font color="#0000FF" face="CALIBRI" size="2">62, Rue
                  du Bolliet<br>
                  73230 St Alban Leysse<br>
                  FRANCE<br>
                </font></td>
            </tr>
            <tr>
              <td align="LEFT" width="40"><font color="#0000FF"
                  face="CALIBRI" size="2"> Phone :<br>
                  Fax :<br>
                  Mail:<br>
                </font>
              </td>
              <td><font color="#0000FF" face="CALIBRI" size="2"> +33(0)
                  479 750 029<br>
                  +33(0) 479 852 122<br>
                  <a class="moz-txt-link-freetext"
                    href="mailto:a.jezequel@itf.biz">a.jezequel@itf.biz</a>
                  ou <a class="moz-txt-link-freetext"
                    href="mailto:aj@itf.biz">aj@itf.biz</a></font></td>
            </tr>
          </tbody>
        </table>
        <i><font color="#008000" face="CALIBRI" size="1">Afin de
            contribuer au respect de l'environnement, merci de
            n'imprimer cet e-mail que si nécessaire<br>
            <font color="#008000" face="CALIBRI" size="1">Please,
              consider our environmental responsability before printing
              this email<br>
            </font></font></i>
      </font></div>
    <br>
    Le 21/07/2011 15:01, Marcus.Joppich a écrit :
    <blockquote
cite="mid:B029A4705B5E4144A549AC8C0C3AB204498B3853@WHZ-EXC-04.zw.fh-zwickau.de"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Vorformatiert Zchn";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
span.E-MailFormatvorlage17
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
span.HTMLVorformatiertZchn
        {mso-style-name:"HTML Vorformatiert Zchn";
        mso-style-priority:99;
        mso-style-link:"HTML Vorformatiert";
        font-family:Consolas;
        color:black;}
span.E-MailFormatvorlage20
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page Section1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 2.0cm 70.85pt;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
      <div class="Section1">
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Hello
            David,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">thank
            you for your answer. I´ve tried it. The following steps were
            performed:<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">I
            defined 6 orientations of walls to external: Northwest (Wall
            to external)/ Southeast (Wall to external)/ Northeast (Wall
            to external)/ Northwest with a slope of 37 degrees (sloping
            roof)/ Southeast with a slope of 37 degrees (sloping roof)/
            Northeast with a slope of 37 degrees (sloping roof).<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">At
            Type109 I defined 6 surfaces with the following parameters:<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Surface1/Slope
            of surface 0/Azimuth of surface 225<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Surface2/Slope
            of surface 0/Azimuth of surface 135<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Surface3/Slope
            of surface 0/Azimuth of surface 315<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Surface4/Slope
            of surface 37/Azimuth of surface 225<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Surface5/Slope
            of surface 37/Azimuth of surface 135<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Surface6/Slope
            of surface 37/Azimuth of surface 315<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Then
            I connected the outputs with the inputs by Type56.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Is
            it the right way?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal" style="line-height:200%"><span
            style="color:#1F497D" lang="EN-US">I get a fatal error:
            “Error in automatic heat transfer calculation  for surface  
            1 or its adjacent surface!: Automatic heat transfer
            calculation is only allowed on surfaces within a zone. 
            Please check building input file (.bui)”, but I think it has
            a different reason.<o:p></o:p></span></p>
        <p class="MsoNormal" style="line-height:200%"><span
            style="color:#1F497D" lang="EN-US">Thank you for your help.<o:p></o:p></span></p>
        <p class="MsoNormal" style="line-height:200%"><span
            style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal" style="line-height:200%"><span
            style="color:#1F497D" lang="EN-US">Regards, Marcus<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">Von:</span></b><span
                style="font-size:10.0pt;font-family:
"Tahoma","sans-serif";color:windowtext"> David
                BRADLEY [<a class="moz-txt-link-freetext" href="mailto:d.bradley@tess-inc.com">mailto:d.bradley@tess-inc.com</a>]
                <br>
                <b>Gesendet:</b> Mittwoch, 20. Juli 2011 19:12<br>
                <b>An:</b> Marcus.Joppich<br>
                <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
                <b>Betreff:</b> Re: [TRNSYS-users] sloping surfaces<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Marcus,<br>
           It depends somewhat on what component you are using to model
          the attic. However, almost without exception, you need to
          define the slope and azimuth of the attic roof surfaces in
          your weather component (Type15 probably) and then pass the
          appropriate solar radiation outputs from that component to the
          appropriate inputs of your building component.<br>
          Regards,<br>
           David<br>
          <br>
          <br>
          On 7/20/2011 06:57, Marcus.Joppich wrote: <o:p></o:p></p>
        <p class="MsoNormal">Hello TRNSYS-users,<o:p></o:p></p>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal"><span lang="EN-US">I try to simulate few
            rooms in an attic. I don´t understand how I can describe a
            sloping surface (like a sloping roof) with TRNSYS. Maybe you
            can help me.</span><o:p></o:p></p>
        <p class="MsoNormal"><span lang="EN-US"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span lang="EN-US">Thanks for your time.</span><o:p></o:p></p>
        <p class="MsoNormal"><span lang="EN-US"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span lang="EN-US">Marcus</span><o:p></o:p></p>
        <pre><o:p> </o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>_______________________________________________<o:p></o:p></pre>
        <pre>TRNSYS-users mailing list<o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><o:p></o:p></pre>
        <p class="MsoNormal"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman","serif""><br>
            <br>
            <o:p></o:p></span></p>
        <pre>-- <o:p></o:p></pre>
        <pre>***************************<o:p></o:p></pre>
        <pre>David BRADLEY<o:p></o:p></pre>
        <pre>Principal<o:p></o:p></pre>
        <pre>Thermal Energy Systems Specialists, LLC<o:p></o:p></pre>
        <pre>22 North Carroll Street - suite 370<o:p></o:p></pre>
        <pre>Madison, WI  53703 USA<o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>P:+1.608.274.2577<o:p></o:p></pre>
        <pre>F:+1.608.278.1475<o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a><o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre><a moz-do-not-send="true" href="http://www.tess-inc.com">http://www.tess-inc.com</a><o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="http://www.trnsys.com">http://www.trnsys.com</a><o:p></o:p></pre>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
  </body>
</html>