<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META content="text/html; charset=iso-8859-1" http-equiv=Content-Type>
<META name=GENERATOR content="MSHTML 8.00.7600.16766"></HEAD>
<BODY>
<DIV dir=ltr lang=de class=OutlookMessageHeader align=left><FONT color=#0000ff 
size=2 face=Arial><SPAN class=673524507-18052011>Dear Jiang,</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011>the main reason for your troubles is the groundfloor in 
zone 1ST_L. There is a small surface overlapping with the big one. I removed 
this and it works. But you have a lot of wrong adjacent walls and also the 
window in the ceiling of zone 5TH_L is wrong. So I did some more changes to your 
model. I do not know if everything is correct.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011>My advise working with sketchup and TRNBUILD: Do not 
draw the whole model and try to import it at last. Always work step by step. 
Draw the first zone, try to import it check it and if everything is ok do the 
next zone. Save often import often and keep all steps in seperat 
files.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><SPAN class=673524507-18052011><FONT face=Arial><FONT 
color=#0000ff><FONT size=2><SPAN 
class=933343112-19052011>Additionally, </SPAN>Be aware that all zones xxx_L 
are not convex. Thus you will be not able to use the detailed radiaiton model 
for these zones.</FONT></FONT></FONT></SPAN></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011>Hope it works.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011>Best regards,</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=673524507-18052011>Hermann Schranzhofer.</SPAN></FONT></DIV>
<DIV> </DIV><!-- Converted from text/plain format -->
<P><FONT 
size=2>_______________________________________________________________<BR><BR>DI 
Dr. mont. Hermann Schranzhofer<BR>Institut fuer Waermetechnik / Institute of 
Thermal Engineering<BR>TU Graz / Graz University of Technology<BR>Inffeldgasse 
25 / B, A-8010 Graz<BR><BR>Tel.: +43 316 873 7314<BR>mobil: +43 664 60 873 
7314<BR>Fax : +43 316 873 7305<BR><A 
href="http://www.iwt.tugraz.at/">http://www.iwt.tugraz.at/</A><BR>_______________________________________________________________<BR><BR></FONT></P>
<DIV> </DIV><BR>
<DIV dir=ltr lang=de class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>Von:</B> trnsys-users-bounces@cae.wisc.edu 
[mailto:trnsys-users-bounces@cae.wisc.edu] <B>Im Auftrag von </B>Jay 
Zhu<BR><B>Gesendet:</B> Dienstag, 17. Mai 2011 21:49<BR><B>An:</B> 
trnsys-users@cae.wisc.edu<BR><B>Betreff:</B> Re: [TRNSYS-users] TRNSYS-users 
Digest, Vol 77, Issue 60<BR></FONT><BR></DIV>
<DIV></DIV>Dear ALL:<BR>I spent one whole day to draw the building in the google 
sketchup in order to create the IDF file. but i can not input to the simulation 
studio when i use the trnsys muti-zone option. If any one can tell the reason, i 
really appreciate it.I really don't wanna waste another whole day to redo it 
!  Thank you so much much!! <BR>And the IDF file is attached.<BR>waiting 
for your reply!<BR><BR>And by the way, i found a err for the newest version of 
simulation studio. when i input the trnsys 3d using the IDF, i found the 
capacitance is set 0 automatically while the old version 17.000007 works well. 
<BR> <BR>Best Regards!<BR><BR>Jiang<BR><BR>
<DIV class=gmail_quote>On Tue, May 17, 2011 at 11:20 AM, <SPAN dir=ltr><<A 
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</A>></SPAN> 
wrote:<BR>
<BLOCKQUOTE 
style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" 
class=gmail_quote>Send TRNSYS-users mailing list submissions to<BR>  
       <A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A><BR><BR>To 
  subscribe or unsubscribe via the World Wide Web, visit<BR>      
   <A href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" 
  target=_blank>https://mailman.cae.wisc.edu/listinfo/trnsys-users</A><BR>or, 
  via email, send a message with subject or body 'help' to<BR>    
     <A 
  href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</A><BR><BR>You 
  can reach the person managing the list at<BR>       <A 
  href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</A><BR><BR>When 
  replying, please edit your Subject line so it is more specific<BR>than "Re: 
  Contents of TRNSYS-users digest..."<BR><BR>Today's Topics:<BR><BR>  1. 
  Re: thermosyphon sdwh (keilholz, werner)<BR>  2. email (Adwit 
  Kashyap)<BR>  3. query regarding runtime error (Adwit Kashyap)<BR>  
  4. Re: Error: generating shading/insolation matrix (Marion Hiller)<BR>  
  5. Type553 collector performance question (Nicholas LaHam)<BR>  6. 
  Validated (unglazed, or any other...) collector type (Philip 
  Horn)<BR><BR><BR>---------- Forwarded message 
  ----------<BR>From: "keilholz, werner" <<A 
  href="mailto:werner.keilholz@cstb.fr">werner.keilholz@cstb.fr</A>><BR>To: "<A 
  href="mailto:Enmisagh@aol.com">Enmisagh@aol.com</A>" <<A 
  href="mailto:Enmisagh@aol.com">Enmisagh@aol.com</A>>, "<A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A>" <<A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A>><BR>Date: Tue, 
  17 May 2011 08:59:37 +0000<BR>Subject: Re: [TRNSYS-users] thermosyphon 
  sdwh<BR>
  <DIV lang=FR link="blue" vlink="purple">
  <DIV>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt" 
  lang=EN-US>Grüss Gott to the people in Munich ! Do you know there's 
  TRNSYS facebook group, as well as a LinkedIn group? </SPAN></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt" 
  lang=EN-US>You could meet there an set up a local event.</SPAN></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d; FONT-SIZE: 11pt" 
  lang=EN-US></SPAN> </P>
  <DIV>
  <DIV 
  style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 0cm; PADDING-RIGHT: 0cm; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
  <P class=MsoNormal><B><SPAN style="FONT-SIZE: 10pt">De :</SPAN></B><SPAN 
  style="FONT-SIZE: 10pt"> <A href="mailto:trnsys-users-bounces@cae.wisc.edu" 
  target=_blank>trnsys-users-bounces@cae.wisc.edu</A> [mailto:<A 
  href="mailto:trnsys-users-bounces@cae.wisc.edu" 
  target=_blank>trnsys-users-bounces@cae.wisc.edu</A>] <B>De la part de</B> <A 
  href="mailto:Enmisagh@aol.com" 
  target=_blank>Enmisagh@aol.com</A><BR><B>Envoyé :</B> dimanche 15 mai 
  2011 15:56<BR><B>À :</B> <A href="mailto:trnsys-users@cae.wisc.edu" 
  target=_blank>trnsys-users@cae.wisc.edu</A><BR><B>Objet :</B> 
  [TRNSYS-users] thermosyphon sdwh</SPAN></P></DIV></DIV>
  <P class=MsoNormal> </P>
  <DIV>
  <P class=MsoNormal><SPAN style="COLOR: black; FONT-SIZE: 10pt">hi 
  all</SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN style="COLOR: black; FONT-SIZE: 10pt">i want to model 
  a thermosiphon sdwh . in this model the outlet temperature is 55 c . if I want 
  to use auxiliary heater , how can I set outlet 
  temperature?  </SPAN></P></DIV></DIV></DIV><BR><BR>---------- 
  Forwarded message ----------<BR>From: Adwit Kashyap <<A 
  href="mailto:kashyap.adwit235@gmail.com">kashyap.adwit235@gmail.com</A>><BR>To: <A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A><BR>Date: Tue, 
  17 May 2011 14:56:22 +0530<BR>Subject: [TRNSYS-users] email<BR><A 
  href="mailto:kashyap.adwit235@gmail.com" 
  target=_blank>kashyap.adwit235@gmail.com</A> <BR><BR>---------- Forwarded 
  message ----------<BR>From: Adwit Kashyap <<A 
  href="mailto:kashyap.adwit235@gmail.com">kashyap.adwit235@gmail.com</A>><BR>To: <A 
  href="mailto:trnsys-users@engr.wisc.edu">trnsys-users@engr.wisc.edu</A><BR>Date: Tue, 
  17 May 2011 15:24:02 +0530<BR>Subject: [TRNSYS-users] query regarding 
  runtime error<BR>hi. i am a fairly new user. i made a simple solar pv project 
  using types 109-user for weather data, 94-a pv array, 65-d online plotter 
  without file, an equation and a system printer. the time period was from 0 to 
  8670 hours. 
  <DIV>on running the simulation, it shows zero simulation time and the output 
  file shows only one row of values, all zeroes.</DIV>
  <DIV><BR></DIV>
  <DIV>also, when i save it in C:>Program Files 
  (x86)>Trnsys>MyProjects, it is not visible in the folder, but is visible 
  when u use the File>Open option in Trnsys Studio and go to the 
  location.</DIV>
  <DIV>i tried saving the project in a different drive and then it got 
  saved. </DIV><BR><BR>---------- Forwarded message 
  ----------<BR>From: "Marion Hiller" <<A 
  href="mailto:hiller@transsolar.com">hiller@transsolar.com</A>><BR>To: "joke.d" 
  <<A 
  href="mailto:joke.d@vkgroup.be">joke.d@vkgroup.be</A>><BR>Date: Tue, 
  17 May 2011 13:26:54 +0200<BR>Subject: Re: [TRNSYS-users] Error: 
  generating shading/insolation matrix<BR>Joke,<BR><BR>the error message is due 
  to too surface numbers > 999. The surface<BR>number can't be written in the 
  log file (artsmetiers7_shd.log) and ***<BR>are written instead.<BR><BR>*** 
  Notice at time        :         
  0.000000<BR> Orientation of wall   SURF=***: azimuth angle= 180.00°, 
  slope=  90.00°<BR> Orientation of wall   SURF=***: azimuth 
  angle=   0.00°, slope=   0.00°<BR><BR>In order to see why the 
  surface numbers are so high (starting with<BR>3993 instead of 1) I need to 
  need the original *.idf and check the<BR>import function.<BR><BR>With what 
  version of TRNSYS17 are you working? I have in mind that we<BR>fixed such a 
  bug created by the import.<BR><BR>Kind 
  regards,<BR><BR>Marion<BR><BR><BR><BR>-----Ursprüngliche 
  Nachricht-----<BR>Von: Joke De Beuckelaer [mailto:<A 
  href="mailto:joke.d@vkgroup.be">joke.d@vkgroup.be</A>]<BR>Gesendet: 
  Donnerstag, 12. Mai 2011 08:58<BR>An: <A 
  href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</A>; <A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A><BR>Betreff: 
  Re: [TRNSYS-users] Error: generating shading/insolation 
  matrix<BR><BR>_______________________________________________<BR>TRNSYS-users 
  mailing list<BR><A 
  href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</A><BR><A 
  href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" 
  target=_blank>https://mailman.cae.wisc.edu/listinfo/trnsys-users</A><BR><BR><BR><BR><BR><BR>---------- 
  Forwarded message ----------<BR>From: Nicholas LaHam <<A 
  href="mailto:ndlaham@gmail.com">ndlaham@gmail.com</A>><BR>To: <A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A><BR>Date: Tue, 
  17 May 2011 12:01:56 -0400<BR>Subject: [TRNSYS-users] Type553 collector 
  performance question<BR><SPAN 
  style="BORDER-COLLAPSE: collapse; FONT-FAMILY: arial, sans-serif; FONT-SIZE: 13px">Hey 
  all, 
  <DIV><BR></DIV>
  <DIV>I have a question about the Type553 Unglazed collector and how it's 
  performance interacts when changing flowrates in two different scenarios. I 
  was wondering if someone could help explain the trend in a practical way for 
  me so I can explain it to my colleague.</DIV>
  <DIV><BR></DIV>
  <DIV>First off, when just running a constant flowrate and 
  constant incoming temperature as the inputs to the collector, I can 
  see that increasing that flowrate increases the useful energy out of the 
  collector. This makes sense and is intuitive.</DIV>
  <DIV><BR>Now when I use a loop instead for the same collector, (say with a 
  pump operating at 1 GPM just as a starting point), and a perfect heat 
  exchanger with the same incoming water temp now on the load side of the HX, I 
  see a different trend I'm having trouble explaining to my colleague.</DIV>
  <DIV><BR></DIV>
  <DIV>What is happening is that the useful energy increases like the first 
  scenario, but only up to the flowrate that is on the load side of the 
  HX. <I>ex. So if I have 5 GPM on my load side, I see an increase in 
  performance up to 5 gpm on my collector side, and then the performance begins 
  to drop after increasing it any further.</I></DIV>
  <DIV><BR></DIV>
  <DIV>Another way to say it is that whenever my flowrate of the collector array 
  is greater then my load I have weakened performance. It seems that a 
  1:1 flow ratio on each side of the HX is the optimal method (assuming same 
  specific heats).</DIV>
  <DIV><BR></DIV>
  <DIV>Can anyway explain in a conceptual manner why there is this 
  decrease only when using the HX? I was thinking that because the load side of 
  the HX is the limiting flow (the one that isn't changing) then because the 
  collector flow is higher, that not all the heat from the collector can be 
  transfered, leaving the outlet of the HX on the collector side hotter than if 
  the flows were balanced. Thus in turn lowering the efficiency 
  and available energy to be collected the next time it passes through 
  the collector.</DIV>
  <DIV><BR></DIV>
  <DIV>I can actually see the source side temp coming out of the HX hotter than 
  the incoming water when the collector flow is higher, but my colleague still 
  thinks the energy should not drop. He believes that when increasing the 
  flow up to a very large number over many trials, the useful energy will always 
  rise up until it levels off asymptotically, whereas in my case, it is 
  doing more of a bell curve and dropping off after it becomes higher than the 
  load flowrate.</DIV>
  <DIV><BR></DIV>
  <DIV>Thanks for any help.</DIV>
  <DIV>Nick LaHam</DIV></SPAN><BR><BR>---------- Forwarded message 
  ----------<BR>From: Philip Horn <<A 
  href="mailto:phorn@fraunhofer.org">phorn@fraunhofer.org</A>><BR>To: "<A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A>" <<A 
  href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</A>><BR>Date: Tue, 
  17 May 2011 12:23:20 -0400<BR>Subject: [TRNSYS-users] Validated 
  (unglazed, or any other...) collector type<BR>
  <DIV lang=EN-US link="blue" vlink="purple">
  <DIV>
  <P class=MsoNormal>Dear All,</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>I am searching for a experimentally validated unglazed 
  collector setting in TRNSYS (with values of Inputs, Parameters, assumptions, 
  etc.).</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>I am currently working on an unglazed polymer PVT collector 
  with rectangular flow channels (so NOT a fin-type collector.</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>I would like to compare my attempts with similar systems. 
  As there are probably no "really similar" systems available, any validated 
  solar collector model will be helpful.</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>Ideally with long term measurements validation.</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>Can someone comment on the accuracy of the default values 
  for the collector types, e.g. is it a good enough reference to simply use a 
  TRNSYS type out of the box? </P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>Would  some standard decks from IEA tasks work (I 
  think they exist, right?) for my purpose?</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>I am currently reading about <B>Type 132</B>, but till now 
  I could not find any download link (and it should be openly available if I 
  understood correctly). </P>
  <P class=MsoNormal>Can anyone help on that?</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>I am not sure about the validity of my potential results, 
  as I do not have a prototype yet, so I try to judge how I could somewhat 
  validate by comparison.</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>Your help is highly appreciated!!</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal>Best from freezing Boston,</P>
  <P class=MsoNormal>Philip</P>
  <P class=MsoNormal> </P>
  <P class=MsoNormal> </P>
  <P 
  class=MsoNormal> </P></DIV></DIV><BR>_______________________________________________<BR>TRNSYS-users 
  mailing list<BR><A 
  href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</A><BR><A 
  href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" 
  target=_blank>https://mailman.cae.wisc.edu/listinfo/trnsys-users</A><BR><BR></BLOCKQUOTE></DIV><BR></BODY></HTML>