<!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html;charset=ISO-8859-1" http-equiv="Content-Type">
</head>
<body bgcolor="#ffffff" text="#000000">
Hello Johannes,<br>
<br>
I do not fully understand your goal: Do you want to receive 8760
optimized control variables?<br>
This will not work. If you want to optimize your shading control, you
should play with the value that "triggers" your shading system (like
total irradiation on a surface). Maybe you can use monthly values. Then
you have 12 variables to optimize, which is a managable goal with
GenOpt. And also could be adapted in a real system...<br>
<br>
But you have to define your cost function very carefully, especially
when you want to optimize two (to some extent) opposed values like room
temperature & irradiation.<br>
<br>
Best regards,<br>
Jochen<br>
<br>
<a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a> schrieb:
<blockquote
 cite="mid:mailman.9590.1305192449.32758.trnsys-users@cae.wisc.edu"
 type="cite">
  <pre wrap="">Send TRNSYS-users mailing list submissions to
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>

To subscribe or unsubscribe via the World Wide Web, visit
        <a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
or, via email, send a message with subject or body 'help' to
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>

You can reach the person managing the list at
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."</pre>
  <pre wrap="">
<hr size="4" width="90%">
Today's Topics:

   1. optimazation with TrnOpt/GenOpt (Gantner)
   2. Re: Error: generating shading/insolation matrix (hotline)
   3. Re: Error: generating shading/insolation matrix (mail 2/3)
      (Joke De Beuckelaer)</pre>
  <br>
  <hr size="4" width="90%"><br>
  <table class="header-part1" border="0" cellpadding="0" cellspacing="0"
 width="100%">
    <tbody>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Betreff:
        </div>
[TRNSYS-users] optimazation with TrnOpt/GenOpt</td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Von: </div>
"Gantner" <a class="moz-txt-link-rfc2396E" href="mailto:Gantner@transsolar.com"><Gantner@transsolar.com></a></td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Datum: </div>
Thu, 12 May 2011 10:40:04 +0200</td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">An: </div>
trnsys-users <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@cae.wisc.edu"><trnsys-users@cae.wisc.edu></a></td>
      </tr>
    </tbody>
  </table>
  <table class="header-part2" border="0" cellpadding="0" cellspacing="0"
 width="100%">
    <tbody>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">An: </div>
trnsys-users <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@cae.wisc.edu"><trnsys-users@cae.wisc.edu></a></td>
      </tr>
    </tbody>
  </table>
  <br>
  <pre wrap="">Dear trnsys users,

 

I`m currently trying to optimize some control signals in my trnsys
model.

Is there any possibility to optimize the control signals for every
single hour

of the year? For example I would like to get a certain hourly signal for
the shading

control (0, 0.1, 0.2,…, 1). 

The error function is the indoor temperature/ irradiation.

Is that possible with TrnOpt?

 

Thanks a lot.

 

Best,

Johannes


  </pre>
  <br>
  <hr size="4" width="90%"><br>
  <table class="header-part1" border="0" cellpadding="0" cellspacing="0"
 width="100%">
    <tbody>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Betreff:
        </div>
Re: [TRNSYS-users] Error: generating shading/insolation matrix</td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Von: </div>
"hotline" <a class="moz-txt-link-rfc2396E" href="mailto:hotline@transsolar.com"><hotline@transsolar.com></a></td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Datum: </div>
Thu, 12 May 2011 11:09:43 +0200</td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">An: </div>
duffy <a class="moz-txt-link-rfc2396E" href="mailto:duffy@tess-inc.com"><duffy@tess-inc.com></a>, "joke.d" <a class="moz-txt-link-rfc2396E" href="mailto:joke.d@vkgroup.be"><joke.d@vkgroup.be></a>,
trnsys-users <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@cae.wisc.edu"><trnsys-users@cae.wisc.edu></a></td>
      </tr>
    </tbody>
  </table>
  <table class="header-part2" border="0" cellpadding="0" cellspacing="0"
 width="100%">
    <tbody>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">An: </div>
duffy <a class="moz-txt-link-rfc2396E" href="mailto:duffy@tess-inc.com"><duffy@tess-inc.com></a>, "joke.d" <a class="moz-txt-link-rfc2396E" href="mailto:joke.d@vkgroup.be"><joke.d@vkgroup.be></a>,
trnsys-users <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@cae.wisc.edu"><trnsys-users@cae.wisc.edu></a></td>
      </tr>
    </tbody>
  </table>
  <br>
  <pre wrap="">Dear Joke,

for giving more detailed help we need to have a look at your IDF.

Best regards,
Marion

-----Ursprüngliche Nachricht-----
Von: Joke De Beuckelaer [<a class="moz-txt-link-freetext" href="mailto:joke.d@vkgroup.be">mailto:joke.d@vkgroup.be</a>] 
Gesendet: Donnerstag, 12. Mai 2011 08:58
An: <a class="moz-txt-link-abbreviated" href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>; <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>
Betreff: Re: [TRNSYS-users] Error: generating shading/insolation matrix

_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>


  </pre>
  <br>
  <hr size="4" width="90%"><br>
  <table class="header-part1" border="0" cellpadding="0" cellspacing="0"
 width="100%">
    <tbody>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Betreff:
        </div>
Re: [TRNSYS-users] Error: generating shading/insolation matrix (mail
2/3)</td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Von: </div>
Joke De Beuckelaer <a class="moz-txt-link-rfc2396E" href="mailto:joke.d@vkgroup.be"><joke.d@vkgroup.be></a></td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">Datum: </div>
Thu, 12 May 2011 09:26:16 +0000</td>
      </tr>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">An: </div>
hotline <a class="moz-txt-link-rfc2396E" href="mailto:hotline@transsolar.com"><hotline@transsolar.com></a>, duffy
<a class="moz-txt-link-rfc2396E" href="mailto:duffy@tess-inc.com"><duffy@tess-inc.com></a>, trnsys-users
<a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@cae.wisc.edu"><trnsys-users@cae.wisc.edu></a></td>
      </tr>
    </tbody>
  </table>
  <table class="header-part2" border="0" cellpadding="0" cellspacing="0"
 width="100%">
    <tbody>
      <tr>
        <td>
        <div class="headerdisplayname" style="display: inline;">An: </div>
hotline <a class="moz-txt-link-rfc2396E" href="mailto:hotline@transsolar.com"><hotline@transsolar.com></a>, duffy
<a class="moz-txt-link-rfc2396E" href="mailto:duffy@tess-inc.com"><duffy@tess-inc.com></a>, trnsys-users
<a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@cae.wisc.edu"><trnsys-users@cae.wisc.edu></a></td>
      </tr>
    </tbody>
  </table>
  <br>
  <pre wrap="">Mail (2/3)


KR,

Joke De Beuckelaer
project engineer mep


VK     HEALTHCARE      |      BUILDINGS      |      INDUSTRY      |      INFRA

Value by design

VK ENGINEERING  Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel, Belgium
t   +32 2 414 07 77   f  +32 2 414 04 98   m  +32 473 97 01 50   e   <a class="moz-txt-link-abbreviated" href="mailto:joke.d@vkgroup.be">joke.d@vkgroup.be</a>   w   <a class="moz-txt-link-abbreviated" href="http://www.vkgroup.be">www.vkgroup.be</a>


-----Oorspronkelijk bericht-----
Van: hotline [<a class="moz-txt-link-freetext" href="mailto:hotline@transsolar.com">mailto:hotline@transsolar.com</a>]
Verzonden: donderdag 12 mei 2011 11:10
Aan: duffy; Joke De Beuckelaer; trnsys-users
Onderwerp: AW: Re: [TRNSYS-users] Error: generating shading/insolation matrix

Dear Joke,

for giving more detailed help we need to have a look at your IDF.

Best regards,
Marion

-----Ursprüngliche Nachricht-----
Von: Joke De Beuckelaer [<a class="moz-txt-link-freetext" href="mailto:joke.d@vkgroup.be">mailto:joke.d@vkgroup.be</a>]
Gesendet: Donnerstag, 12. Mai 2011 08:58
An: <a class="moz-txt-link-abbreviated" href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>; <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>
Betreff: Re: [TRNSYS-users] Error: generating shading/insolation matrix

_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>


  SUBSCRIBE TO OUR NEW E-LETTER    VK NOW ALSO OFFERS ACOUSTICAL ENGINEERING

****DISCLAIMER****
This communication is confidential and for the sole useof the addressee. If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and then delete it from your system
without copying, disclosing or forwarding its contents. Thank you.

  </pre>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
_________________________________________________

Dipl.-Ing. (FH) Jochen Döll
Division Thermal Systems and Buildings

Fraunhofer-Institut für Solare Energiesysteme ISE
Heidenhofstrasse 2, 79110 Freiburg, Germany

Phone: +49 (761) 4588-5468 Fax: +49 (761) 4588-9000
<a class="moz-txt-link-abbreviated" href="mailto:jochen.doell@ise.fraunhofer.de">jochen.doell@ise.fraunhofer.de</a>
<a class="moz-txt-link-abbreviated" href="http://www.ise.fraunhofer.de">www.ise.fraunhofer.de</a>
_________________________________________________</pre>
</body>
</html>