In the Type 56 manual, it models the thermal network from the supply water to the pipe plane node as resistances placed in series.  For example, if I wanted to find the rate of heat transfer from one node to the next, by using...<br>
<br>Q=[ A*(T1-T2) ] / R<br><br>What area would I use, since all the resistance values are in units of [m^2-K/W].  Here's what I was thinking...<br><br><b>Rz</b>: thermal resistance in z-direction along the pipe length--> A=area of the floor surface, since I see the mean temperature as being similar to node k (pipe plane temperature ) and the heat transfer goes up through the floor into the space.<br>
<br><b>Rw: </b>thermal resistance by forced convection (from fluid to pipe shell) for cylindrical areas--> A=2*pi*Ri*L, the inside surface area of the pipe<br><br><b>Rr:</b> thermal resistance by conduction through the pipe shell--> A=[pi*Ro^2] - [pi*Ri^2], where Ro and Ri are the outside and inside pipe radii<br>
<br><b>Rx:</b> thermal resistance from outer pipe shell to pipe plane by conduction--> A= floor thickness (since the heat transfer is horizontal)<br><br>Please let me know if this is incorrect.  Thank you<br clear="all">
<br>-- <br>Devin M. Rohan<br><a href="mailto:drohan@purdue.edu" target="_blank">drohan@purdue.edu</a><br>