<font size=2 face="sans-serif">Dear TRNSYS users,</font>
<br>
<br><font size=2 face="sans-serif">the building type 56 is used to generate
a load profile regarding to a constant room temperature. I experienced
a different behavior of cooling and heating demand based on the time-step
selected. It seems that the building type is extrapolating its performance
within one hour, when such a smaller time-step is selected - and correction
its state, based on one hour calculations. </font>
<br>
<br><font size=2 face="sans-serif">All input values like irradiation on
all surfaces contribute as a continuous function. Details are shown in
the attached .pdf file. The same issue appears in TRNSYS versions of 16
and 17.</font>
<br>
<br><font size=2 face="sans-serif">The same issue has already been discussed
without detailed answering: </font><a href="https://mailman.cae.wisc.edu/pipermail/trnsys-users/2008/003893.html"><font size=2 face="sans-serif">https://mailman.cae.wisc.edu/pipermail/trnsys-users/2008/003893.html</font></a>
<br>
<br>
<br><font size=2 face="sans-serif">Tanks for help</font>
<br><font size=2 face="sans-serif">best regards,</font>
<br>
<br><font size=2 face="sans-serif">Axel Oliva</font>
<br><font size=2 face="sans-serif">-- <br>
-----------------------------------------------------------------------------<br>
Dipl.-Ing. Axel Oliva<br>
Division Solar Thermal and Optics<br>
Fraunhofer Institute for Solar Energy Systems ISE<br>
Heidenhofstrasse 2, 79110 Freiburg, Germany<br>
Phone:+49(0)761/4588-5698 Fax:+49(0)761/4588-9950<br>
axel.oliva@ise.fraunhofer.de<br>
</font><a href=http://www.ise.fraunhofer.de/><font size=2 face="sans-serif">http://www.ise.fraunhofer.de</font></a><font size=2 face="sans-serif"><br>
-----------------------------------------------------------------------------</font>
<br>
<br>
<br>