    The Type56 model by itself does not calculate any interzonal air
    flow (ie the buoyancy of warmer air is not accounted for). Type56
    allows you to specify coupling airflow between zones. Calculation of
    the coupling airflow must be done by integrating Type56's thermal
    solution with TRNFlow, COMIS, or Type97 (Contam). The effect you are
    seeing is only due to a change between the star-network (simple)
    radiation model and the gebhardt factor (detailed) radiation model
    now available in Type56.<br>
    Kind regards,<br>
     David<br>
    <br>
    On 4/14/2011 09:46, <a class="moz-txt-link-abbreviated" href="mailto:pseudomino@gmx.com">pseudomino@gmx.com</a> wrote:
    <blockquote cite="mid:20110414144642.35590@gmx.com" type="cite"><span
        style="font-family: Verdana;"><span style="font-size: 12px;"><span
            style="font-family: verdana;"><span style="font-size: 12px;">Hi,<br>
              <br>
              In Trnsys 17, I made a very simple test : two little
              air-nodes superposed, forming part of a thermal zone.<br>
              There is only one windows facing south, at the first
              floor. I ditn't made anything else.<br>
              <br>
              <strong>Case 1 : Simple radiation model</strong><br>
              Quite realistically, the second floor is warmer.<br>
              <br>
              <strong>Case 2 : Detailed radiation model</strong><br>
              The 2 air-nodes have their temperatures centered around
              the same value and very near, except that the first floor
              has more extreme temperature variations.<br>
              <br>
              I want to illustrate the hot air elevation by a simple
              example, but I'm not sure of the phenomenon that are taken
              into account.<br>
              <br>
              Thank you !</span></span></span></span>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>