    As noted in TRNBuild (where you set the back side convection
    coefficient), a value smaller than 0.001 is used to indicate direct
    contact between a BOUNDARY wall and a temperature. A large value
    (such as 999) is used with other wall categories (ADJACENT,
    EXTERNAL, etc.) to indicate good thermal contact.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    On 4/13/2011 10:30, <a class="moz-txt-link-abbreviated" href="mailto:pseudomino@gmx.com">pseudomino@gmx.com</a> wrote:
    <blockquote cite="mid:20110413153100.35610@gmx.com" type="cite"><span
        style="font-family: Verdana;"><span style="font-size: 12px;">Hello,<br>
          <br>
          Usually, when using the assistant to create a multizone
          building, the convection coefficient between the soil and the
          floor is set to 999 to reproduce the absence of thermal
          resistance.<br>
          <br>
          But when I create a file using the Trnsys3D import from
          Sketchup, this same coefficient is set by default to 0,001.<br>
          Why is that ?<br>
          <br>
          Please help me understand</span></span>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>