<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#ffffff">
    Jiang,<br>
    The first method is the correct one. The heating and cooling types
    that are built into Type56 are idealized and are intended to
    calculate the energy required to keep the space at a given
    temperature. The resulting loads give you an idea of the size of
    equipment needed to maintain those set points. By defining a
    thermostat and a delivery device you are able to calculate the
    actual energy required (accounting for the non-idealities of the
    equipment, the controls, and the delivery). Make sure that when you
    define your equipment and use the ventilation type for delivery you
    also reduce your simulation timestep to something reasonable for
    making control decisions (1 minute or 5 minutes probably).<br>
    best,<br>
     David<br>
    <br>
    On 4/13/2011 13:27, Jay Zhu wrote:
    <blockquote
      cite="mid:BANLkTik6D=Sg6TgJAtk2FFKOdPBGcMJP4w@mail.gmail.com"
      type="cite">Dear All:<br>
      <br>
      I have a question about the connection between the external
      heating and cooling source, such as water source heat pump, air
      source heat pump , and the building type 56, i tried two methods
      to simulate .<br>
      1, use the ventilation, supplied air flow ,air T, Humidity<br>
      2, use the heating and cooling type, supplied cooling power and
      heating power. <br>
      From the manual , either way should work, However, the results for
      the two cases have a big difference in my simulation. <br>
      <br>
      Does anyone know the reasons or have some relative experience?  
      Thank you in advance!<br>
      <br>
      Best <br>
      <br>
      Jiang <br>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>