    <font face="Verdana" size="2">Guangzhao<br>
        </font>My apologies for the delay, I am still working on trying
    to get the parameters for your PV module generated. While Type194 is
    the preferred model, you could use Type94 for the time being. <br>
    <br>
      As for the mode parameter in Type194, you don't need to worry
    about it. For a time, we were adding an extra "mode" parameter to
    all new Types that we wrote just in case we needed it in the future
    so that we wouldn't run into backwards compatibility problems.
    Type194 only has one mode.<br>
    <br>
      Lastly, the voltage of your PV array and the voltage of your
    battery bank typically need to match each other. A battery charge
    controller can handle some differences but the idea is usually that
    you want your DC PV array to run at a voltage that is a bit higher
    than the battery bank voltage so that it can be used to charge the
    batteries without a step-down voltage converter. The number of cells
    within a PV module obviously can't be changed. However, the number
    of modules that you connect in series and parallel can be. Your PV
    array will run at multiples of about 17.5V, which is about normal
    for charging a 12V battery system I would think. If you have PVs in
    series, you would need to also have batteries in series as well.<br>
    Kind regards,<br>
     David<br>
    <br>
    On 3/14/2011 08:21, lvguangzhao wrote:
    <blockquote cite="mid:201103142121060207523@126.com" type="cite">
      <title></title>
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta content="MSHTML 6.00.6002.18357" name="GENERATOR">
      <style>@font-face {
        font-family: 宋体;
}
@font-face {
        font-family: Verdana;
}
@font-face {
        font-family: @宋体;
}
@page Section1 {size: 595.3pt 841.9pt; margin: 72.0pt 90.0pt 72.0pt 90.0pt; layout-grid: 15.6pt; }
P.MsoNormal {
        TEXT-JUSTIFY: inter-ideograph; FONT-SIZE: 10.5pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman"; TEXT-ALIGN: justify
}
LI.MsoNormal {
        TEXT-JUSTIFY: inter-ideograph; FONT-SIZE: 10.5pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman"; TEXT-ALIGN: justify
}
DIV.MsoNormal {
        TEXT-JUSTIFY: inter-ideograph; FONT-SIZE: 10.5pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman"; TEXT-ALIGN: justify
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline
}
SPAN.EmailStyle17 {
        FONT-WEIGHT: normal; COLOR: windowtext; FONT-STYLE: normal; FONT-FAMILY: Verdana; TEXT-DECORATION: none; mso-style-type: personal-compose
}
DIV.Section1 {
        page: Section1
}
UNKNOWN {
        FONT-SIZE: 10pt
}
</style>
      <div><font color="#000080" face="Verdana" size="2">
          <div><font color="#000080" face="Verdana" size="2">
              <div><font color="#000080" face="Verdana" size="2">Hello,David,I
                  urgently want to get your help.</font></div>
              <div><font color="#000080">Following are the parameters I
                  missed. </font></div>
              <div><font color="#000080">Temperature coefficient of
                  short circuit current = 0.0010 [1/k]</font></div>
              <div><font color="#000080">Temperature coefficient of open
                  circuit voltage = -0.0038 [v/k]</font></div>
              <div><font color="#000080">It's a mono-silicon based
                  panel. All of the parameters I sent to you are from
                  the product manual. The test result of open circuit
                  voltage also matches that value. </font></div>
              <div><font color="#000080">I also want to know which type
                  I should use, type194 or type194b? The parameters of
                  Type194b's seem can be changed. But a message "
                  Only mode 1 has been implemented, mode 2 was
                  created for future updates" is showed in mode card.
                  I'm not sure whether it has been implemented now.</font></div>
              <div>I have another question about the capacity of a
                battery bank. The capacity of a battery bank will not
                vary with the number of cells in series. So if it means
                that the cell capacity should vary with the number
                of cells in series?</div>
              <div><font color="#000080">Best regards!</font></div>
            </font></div>
        </font></div>
      <div> </div>
      <div> </div>
      <div><font color="#c0c0c0" face="Verdana" size="2">2011-03-13 </font></div>
      <font color="#000080" face="Verdana" size="2">
        <hr style="width: 100px;" align="left" color="#b5c4df" size="1">
      </font>
      <div><font color="#c0c0c0" face="Verdana" size="2"><span>
            <div>
              <div>Guangzhao Lv</div>
            </div>
          </span></font></div>
      <hr color="#b5c4df" size="1">
      <div><font face="Verdana" size="2"><strong>发件人:</strong> David
          BRADLEY </font></div>
      <div><font face="Verdana" size="2"><strong>发送时间:</strong>
          2011-03-09  03:24:00 </font></div>
      <div><font face="Verdana" size="2"><strong>收件人:</strong>
          lvguangzhao </font></div>
      <div><font face="Verdana" size="2"><strong>抄送:</strong>
          trnsys-users </font></div>
      <div><font face="Verdana" size="2"><strong>主题:</strong> Re:
          [TRNSYS-users] Questions about Type 194 and Type 665 </font></div>
      <div> </div>
      <div><font face="Verdana" size="2">Guangzhao,<br>
            I also need to know the temperature coefficient of short
          circuit current and the temperature coefficient of open
          circuit voltage. Both of these should be listed on the
          manufacturer's data sheet. Also, is this a silicon-based panel
          or some other material? The reason I ask is that silicon cells
          typically run at about 0.5V per cell so 36 in series would
          have an open cell voltage more like 18V than 21.5V. Its not
          impossible of course.<br>
          Kind regards,<br>
           David<br>
          <br>
          <br>
          On 3/8/2011 05:21, lvguangzhao wrote:
          <blockquote cite="mid:201103081921393855650@126.com"
            type="cite">
            <meta content="MSHTML 6.00.6002.18357" name="GENERATOR">
            <style>@font-face {
        font-family: &#23435;
}
@font-face {
        font-family: Verdana;
}
@font-face {
        font-family: @&#23435;
}
@page Section1 {size: 595.3pt 841.9pt; margin: 72.0pt 90.0pt 72.0pt 90.0pt; layout-grid: 15.6pt; }
P.MsoNormal {
        TEXT-JUSTIFY: inter-ideograph; FONT-SIZE: 10.5pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman"; TEXT-ALIGN: justify
}
LI.MsoNormal {
        TEXT-JUSTIFY: inter-ideograph; FONT-SIZE: 10.5pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman"; TEXT-ALIGN: justify
}
DIV.MsoNormal {
        TEXT-JUSTIFY: inter-ideograph; FONT-SIZE: 10.5pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman"; TEXT-ALIGN: justify
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline
}
SPAN.EmailStyle17 {
        FONT-WEIGHT: normal; COLOR: windowtext; FONT-STYLE: normal; FONT-FAMILY: Verdana; TEXT-DECORATION: none; mso-style-type: personal-compose
}
DIV.Section1 {
        page: Section1
}
UNKNOWN {
        FONT-SIZE: 10pt
}
</style>
            <div><font color="#000080" face="Verdana" size="2">
                <div><font color="#000080" face="Verdana" size="2">Hello,
                    David, thank you very much for your
                    reply.Attached are my project.Following are the
                    parameters that I am trying to enter into the EES.</font></div>
                <div>Number of cells in series within a module = 36</div>
                <div>Open circuit voltage at reference conditions = 21.5
                  V</div>
                <div>Short ciecuit current at reference conditions
                  = 7.55 amp</div>
                <div>Max. power voltage at reference conditions = 17.5 V</div>
                <div>Max. power current at reference conditions = 6.86
                  amp</div>
                <div>Module area = 0.92m2</div>
                <div>I also have tryed to change some parameters in
                  EXAMPLE.VAR in the folder of Type194 ,but I didn't
                  know what to correct.</div>
                <div>Thank you in advance !</div>
              </font></div>
            <div> </div>
            <div> </div>
            <div><font color="#c0c0c0" face="Verdana" size="2">2011-03-08
              </font></div>
            <font color="#000080" face="Verdana" size="2">
              <hr style="width: 100px;" align="left" color="#b5c4df"
                size="1"> </font>
            <div><font color="#c0c0c0" face="Verdana" size="2"><span>
                  <div>
                    <div>Guangzhao Lv<br>
                    </div>
                  </div>
                </span></font></div>
            <hr color="#b5c4df" size="1">
            <div><font face="Verdana" size="2"><strong>发件人:</strong>
                David BRADLEY </font></div>
            <div><font face="Verdana" size="2"><strong>发送时间:</strong>
                2011-03-02  23:04:11 </font></div>
            <div><font face="Verdana" size="2"><strong>收件人:</strong>
                lvguangzhao </font></div>
            <div><font face="Verdana" size="2"><strong>抄送:</strong>
                trnsys-users </font></div>
            <div><font face="Verdana" size="2"><strong>主题:</strong> Re:
                [TRNSYS-users] Questions about Type 194 and Type 665 </font></div>
            <div><font face="Verdana" size="2">Guangzhao,<br>
                  Could you please send me an email containing the
                parameters that you are entering into the EES plugin for
                Type194? I have run into some similar problems in the
                past and may be able to help solve this one. It sounds
                from what you describe as though the problem is in
                launching the plugin, not actually in having the plugin
                solve so perhaps you only need to send me the Trnsys
                Studio project that causes the error.<br>
                Kind regards,<br>
                 David<br>
                <br>
                <br>
                On 3/1/2011 00:47, lvguangzhao wrote:
                <blockquote cite="mid:201103011447088651496@126.com"
                  type="cite">
                  <meta content="MSHTML 6.00.6002.18357"
                    name="GENERATOR">
                  <link
href="BLOCKQUOTE%7Bmargin-Top:%200px;%20margin-Bottom:%200px;%20margin-Left:%202em%7D"
                    rel="stylesheet">
                  <div><font face="Verdana" size="2">Hello, I have two
                      questions to ask.</font></div>
                  <div><font face="Verdana" size="2">1. I encountered a
                      problem when I was trying to change the parameters
                      of Type 194 using EES. A error "Missing user
                      function or improper format for Call statement"
                      was showed after I clicked on the icon on the
                      parameter card. What's wrong with it? </font></div>
                  <div>2. A convertible frequency air source heat
                    pump is needed in my model but I can't find one in
                    TRNSYS. <font style="background-color: rgb(183,
                      232, 189);">Is Type 665 Ok? </font></div>
                  <div align="left"><font color="#c0c0c0" face="Verdana"
                      size="2">2011-03-01 </font></div>
                  <font face="Verdana" size="2">
                    <hr style="width: 122px; height: 2px;" align="left"
                      size="2">
                    <div><font color="#c0c0c0" face="Verdana" size="2"><span>
                          <div>
                            <div>Guangzhao Lv<br>
                            </div>
                          </div>
                        </span></font></div>
                  </font>
                  <pre wrap=""><fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu" moz-do-not-send="true">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" moz-do-not-send="true">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
                </blockquote>
                <br>
                <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" moz-do-not-send="true">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com" moz-do-not-send="true">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com" moz-do-not-send="true">http://www.trnsys.com</a></pre>
              </font></div>
          </blockquote>
          <br>
          <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
        </font></div>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>