    I think you might be best off trying to model that type of heat pump
    using a performance map instead of trying to model the whole
    refrigeration cycle. Typically the dynamics of a refrigeration cycle
    have a very very short time constant while the dynamics of a solar
    collector (due to its mass) have a longer time constant. Getting a
    correct first-principals model of the refrigerant evaporation and
    the energy transfer within the fins and tubes of the solar collector
    might be difficult. However, if you can get information about the
    COP of the heat pump under different circumstances, you might be
    able to mimic the way that most other heat pumps are modeled (ie
    with a catalog-data lookup table approach).<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 3/12/2011 03:20, <a class="moz-txt-link-abbreviated" href="mailto:Enmisagh@aol.com">Enmisagh@aol.com</a> wrote:
    <blockquote cite="mid:1c389.62bcd525.3aac94ce@aol.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <meta name="GENERATOR" content="MSHTML 8.00.6001.18702">
      <font id="role_document" color="#000000" face="Arial" size="2">
        <div>dear all,</div>
        <div>I was wondering you to give me an idea to model a direct
          expansion solar assisted heat pump? In this heat pump , a flat
          plate collector has the role of evaporator and refrigerant
          circulates in tubes of collector . other components are
          similar to conventional heat pump  Is there any special type
          for this application or I have to simulate every part of
          refrigeration cycle separately?</div>
        <div>best regad,</div>
        <div> </div>
      </font>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>