Muhammad,<br>
The excel file has most of the data that you need in it in rows
9-17. The independent variables required by Type938's data file (the
lines across the top of the file) are the temperatures in column B
and the dependent variable values are in column C or D. The map
given in the data file is not complete (ie not all combinations are
given). What I would recommend you do is to normalize the data in
your excel spreadsheet (divide all of the power values by the power
at rated conditions) then overlay that normalized data on a plot of
the example Type938 data. You should find that your data, once
normalized, fits pretty well with the example normalized data, in
which case you can use the default data file.<br>
Kind regards,<br>
David<br>
<br>
<br>
On 3/4/2011 04:50, muhammad waseem wrote:
<blockquote
cite="mid:AANLkTimexXSTumJg2X=-NspKxBA+5VrWQuS_w-7ahSE6@mail.gmail.com"
type="cite">
<div>Hi David,</div>
<div>Thanks for your kind reply. I fixed my errors. Now the
problem is I can not understand how to make external file for my
heat pump. I am using type 938. The data which I get from
manufacture is in attached file, Which is not as it was written
as default in type 938. I am attaching manufacture data and Type
938 data file. </div>
<div> </div>
<div>I hope to hearing from you soon.</div>
<div> </div>
<div>Kindest Regards<br>
<br>
</div>
<div class="gmail_quote">On Wed, Mar 2, 2011 at 4:15 PM, David
BRADLEY <span dir="ltr"><<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="padding-left: 1ex;
margin: 0px 0px 0px 0.8ex; border-left: 1px solid rgb(204,
204, 204);">
<div bgcolor="#ffffff" text="#000000">Muhammad,<br>
In order to run your simulation, I would need the data
files for the Type534 tank and for the Type938 heat pump.
The *.lst and *.log files contain information as to the
cause of the error. As for a radiator and a fancoil model,
both are available in the TESS HVAC Library for Trnsys17.<br>
Kind regards,<br>
David
<div>
<div class="h5"><br>
<br>
<br>
On 3/1/2011 04:29, muhammad waseem wrote: </div>
</div>
<blockquote type="cite">
<div>
<div class="h5">
<div>Hi,</div>
<div>I have simulated a Solar assisted heat pump
system. I am getting some errors, could not
understand what these for? Could any one please help
me out. </div>
<div>Also does any one know any models for radiator
and fan coil unit. If there is no standard model
then how I can get non standard models? Attached
with this email is my project's .tpf file.</div>
<div> </div>
<div> </div>
<div>Thanks</div>
<div> </div>
<div>Looking forward to hearing from you.</div>
<div><br clear="all">
</div>
<div> </div>
<div>Kindest Regards</div>
<div><br>
-- <br>
MUHAMMAD WASEEM AHMAD<br>
Loughborough University.</div>
</div>
</div>
<pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
</div>
</blockquote>
</div>
<br>
<br clear="all">
<br>
-- <br>
MUHAMMAD WASEEM AHMAD<br>
PHD RESEARCHER<br>
BUILDING ENERGY RESEARCH GROUP,<br>
DEPARTMENT OF CIVIL AND BUILDING ENGINEERING,<br>
LOUGHBOROUGH UNIVERSITY,<br>
LOUGHBOROUGH, UK<br>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>