    Muhammad,<br>
      The excel file has most of the data that you need in it in rows
    9-17. The independent variables required by Type938's data file (the
    lines across the top of the file) are the temperatures in column B
    and the dependent variable values are in column C or D. The map
    given in the data file is not complete (ie not all combinations are
    given). What I would recommend you do is to normalize the data in
    your excel spreadsheet (divide all of the power values by the power
    at rated conditions) then overlay that normalized data on a plot of
    the example Type938 data.  You should find that your data, once
    normalized, fits pretty well with the example normalized data, in
    which case you can use the default data file.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 3/4/2011 04:50, muhammad waseem wrote:
    <blockquote
      cite="mid:AANLkTimexXSTumJg2X=-NspKxBA+5VrWQuS_w-7ahSE6@mail.gmail.com"
      type="cite">
      <div>Hi David,</div>
      <div>Thanks for your kind reply. I fixed my errors. Now the
        problem is I can not understand how to make external file for my
        heat pump. I am using type 938. The data which I get from
        manufacture is in attached file, Which is not as it was written
        as default in type 938. I am attaching manufacture data and Type
        938 data file. </div>
      <div> </div>
      <div>I hope to hearing from you soon.</div>
      <div> </div>
      <div>Kindest Regards<br>
        <br>
      </div>
      <div class="gmail_quote">On Wed, Mar 2, 2011 at 4:15 PM, David
        BRADLEY <span dir="ltr"><<a moz-do-not-send="true"
            href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>></span>
        wrote:<br>
        <blockquote class="gmail_quote" style="padding-left: 1ex;
          margin: 0px 0px 0px 0.8ex; border-left: 1px solid rgb(204,
          204, 204);">
          <div bgcolor="#ffffff" text="#000000">Muhammad,<br>
              In order to run your simulation, I would need the data
            files for the Type534 tank and for the Type938 heat pump.
            The *.lst and *.log files contain information as to the
            cause of the error. As for a radiator and a fancoil model,
            both are available in the TESS HVAC Library for Trnsys17.<br>
            Kind regards,<br>
             David
            <div>
              <div class="h5"><br>
                <br>
                <br>
                On 3/1/2011 04:29, muhammad waseem wrote: </div>
            </div>
            <blockquote type="cite">
              <div>
                <div class="h5">
                  <div>Hi,</div>
                  <div>I have simulated a Solar assisted heat pump
                    system. I am getting some errors, could not
                    understand what these for? Could any one please help
                    me out. </div>
                  <div>Also does any one know any models for radiator
                    and fan coil unit. If there is no standard model
                    then how I can get non standard models? Attached
                    with this email is my project's .tpf file.</div>
                  <div> </div>
                  <div> </div>
                  <div>Thanks</div>
                  <div> </div>
                  <div>Looking forward to hearing from you.</div>
                  <div><br clear="all">
                     </div>
                  <div> </div>
                  <div>Kindest Regards</div>
                  <div><br>
                    -- <br>
                    MUHAMMAD WASEEM AHMAD<br>
                    Loughborough University.</div>
                </div>
              </div>
              <pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
            </blockquote>
            <br>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
          </div>
        </blockquote>
      </div>
      <br>
      <br clear="all">
      <br>
      -- <br>
      MUHAMMAD WASEEM AHMAD<br>
      PHD RESEARCHER<br>
      BUILDING ENERGY RESEARCH GROUP,<br>
      DEPARTMENT OF CIVIL AND BUILDING ENGINEERING,<br>
      LOUGHBOROUGH UNIVERSITY,<br>
      LOUGHBOROUGH, UK<br>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>