    Wang,<br>
      TRNBuild offers an output (NTYPE96) which is the air change rate
    of infiltration. TRNBuild also offers an output for the energy gain
    (or loss) from infiltration (NTYPE4)<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    On 2/21/2011 15:16, 王洋 wrote:
    <blockquote
      cite="mid:AANLkTik6YB2peX_Y_Xt5itV-24de-eiW5hqE7zzp3SXc@mail.gmail.com"
      type="cite">Dear all, <br>
      <br>
      <br>
      I want to compare the test room infiltration rate of actual
      measurement with by TRNSYS simulation. Maybe as you know, in the
      TRNFlow manual: there it is explained that "As soon as TRNFLOW is
      turned on, (...) in the simulation the defined infiltrations,
      ventilations and couplings will be replaced with the calculated
      air flows."<br>
      I defined CO2% as 1000 ppm in TRNFlow, then I want to observe
      CO2%'s reducing curve when infiltration rate is 0.5276 1/h (I
      measured the value in the test room), so I defined the
      infiltration rate as 0.5276 1/h in TRNBUILD. But when I used
      TRNFLOW, the defined infiltration rate as 0.5276 1/h in TRNBUILD
      was replaced. And 1000 ppm keeps constant.<br>
      <br>
      Please tell me  how to get  the infiltration rate curve using
      TRNSYS/TRNFLOW or how to explain this ?<br>
      <br>
      Many thanks!<br>
      <br>
      br<br>
      <br>
      wang<br>
      <br>
      <br>
      <br>
      <div class="gmail_quote">在 2011年2月21日 下午12:07,王洋 <span dir="ltr"><<a
            moz-do-not-send="true"
            href="mailto:wanghongyang1767@gmail.com">wanghongyang1767@gmail.com</a>></span>写
        道:<br>
        <blockquote style="border-left: 1px solid rgb(204, 204, 204);
          margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
          class="gmail_quote">Dear all, <br>
          <br>
          <br>
          I want to compare the test room infiltration rate of actual
          measurement with by TRNSYS simulation. Maybe as you know, in
          the TRNFlow manual: there it is explained that "As soon as
          TRNFLOW is turned on, (...) in the simulation the defined
          infiltrations, ventilations and couplings will be replaced
          with the calculated air flows."<br>
          I defined CO2% as 1000 ppm in TRNFlow, then I want to observe
          CO2%'s reducing curve when infiltration rate is 0.5276 1/h (I
          measured the value in the test room), so I defined the
          infiltration rate as 0.5276 1/h in TRNBUILD. But when I used
          TRNFLOW, the defined infiltration rate as 0.5276 1/h in
          TRNBUILD was replaced. And 1000 ppm keeps constant.<br>
          <br>
          Please tell me  how to get  the infiltration rate curve using
          TRNSYS/TRNFLOW or how to explain this ?<br>
          <br>
          Many thanks!<br>
          <br>
          br<br>
          <br>
          wang<br>
          <br>
          <div class="gmail_quote">2011/2/21 <span dir="ltr"><<a
                moz-do-not-send="true"
                href="mailto:trnsys-users-request@cae.wisc.edu"
                target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
            <blockquote style="border-left: 1px solid rgb(204, 204,
              204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;"
              class="gmail_quote">Send TRNSYS-users mailing list
              submissions to<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
              <br>
              To subscribe or unsubscribe via the World Wide Web, visit<br>
                     <a moz-do-not-send="true"
                href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
              or, via email, send a message with subject or body 'help'
              to<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users-request@cae.wisc.edu"
                target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
              <br>
              You can reach the person managing the list at<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users-owner@cae.wisc.edu"
                target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
              <br>
              When replying, please edit your Subject line so it is more
              specific<br>
              than "Re: Contents of TRNSYS-users digest..."<br>
              <br>
              Today's Topics:<br>
              <br>
                1. Problems with calling EES (Type66a) (Doms Joris)<br>
                2. wall definition (davide disco)<br>
              <br>
              <br>
              ---------- 已转发邮件 ----------<br>
              From: Doms Joris <<a moz-do-not-send="true"
                href="mailto:joris.doms@vito.be" target="_blank">joris.doms@vito.be</a>><br>
              To: "<a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>"
              <<a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>
              Date: Sun, 20 Feb 2011 22:43:08 +0100<br>
              Subject: [TRNSYS-users] Problems with calling EES
              (Type66a)<br>
              <div>
                <div>Dear TRNSYS users,</div>
                <div> </div>
                <div><font face="times new roman">When simulating an
                    applied thermal system, I'm using EES for the
                    hydronic part. I programmed the hydronic circuit in
                    EES and coupled it with TRNSYS via Type 66a. This
                    coupling works fine, but;</font></div>
                <div> </div>
                <div><font face="times new roman">The problem is that
                    the simulation runs very slow. Every timestep that
                    TRNSYS calls EES, the EES project is opened and
                    closed. Is there a way to set some settings so EES
                    isen't closed and reopened each time, this would
                    minimize the solution time alot.</font></div>
                <div> </div>
                <div><font face="times new roman">Thanks on advance</font></div>
                <div> </div>
                <div><font face="times new roman">Joris Doms</font></div>
                <br>
                <p align="left"><font face="Tahoma" size="2"><font
                      color="#0000ff">
                      <hr>
                      This e-mail, any attachments and the information
                      it contains are confidential and meant only for
                      the use of the addressee(s) only.  Access to this
                      e-mail by anyone other than the addressee(s) is
                      unauthorized.  If you are not the intended
                      addressee (or responsible for delivery of the
                      message to such person), you may not use, copy,
                      distribute or deliver to anyone this message (or
                      any part of its contents) or take any action in
                      reliance on it.  In such case, you should destroy
                      this message and notify the sender immediately. 
                      If you have received this e-mail in error, please
                      notify us immediately by e-mail or telephone and
                      delete the e-mail from any computer.<br>
                      All reasonable precautions have been taken to
                      ensure no viruses are present in this e-mail and
                      its attachments.  As our company cannot accept
                      responsibility for any loss or damage arising from
                      the use of this e-mail or attachments we recommend
                      that you subject these to your virus checking
                      procedures prior to use.<br>
                      <hr>
                    </font></font>
                </p>
              </div>
              <br>
              <br>
              ---------- 已转发邮件 ----------<br>
              From: davide disco <<a moz-do-not-send="true"
                href="mailto:chester_83@hotmail.it" target="_blank">chester_83@hotmail.it</a>><br>
              To: <<a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>
              Date: Mon, 21 Feb 2011 11:57:59 +0100<br>
              Subject: [TRNSYS-users] wall definition<br>
              <div>Dear all,<br>
                when entering data in Trnbuild I have to describe the
                walls of the zone: if, looking at the plant of the
                building, the building has more than a wall south
                oriented for example (wall to the left in the plant) <span
                  lang="en"><span title="Fai clic per visualizzare le
                    traduzioni alternative">I</span> <span title="Fai
                    clic per visualizzare le traduzioni alternative">should</span>
                  <span title="Fai clic per visualizzare le traduzioni
                    alternative">enter in T</span><span title="Fai clic
                    per visualizzare le traduzioni alternative">rnbuild</span>
                  <span title="Fai clic per visualizzare le traduzioni
                    alternative"></span><span title="Fai clic per
                    visualizzare le traduzioni alternative">each section</span>
                  <span title="Fai clic per visualizzare le traduzioni
                    alternative">of</span> <span title="Fai clic per
                    visualizzare le traduzioni alternative">wall</span>
                  <span title="Fai clic per visualizzare le traduzioni
                    alternative">facing south or I should enter a unique
                    wall that is the sum of all sections of wall facing
                    south?<br>
                    Thanks in advace.<br>
                    Best regards<br>
                  </span></span></div>
              <br>
              _______________________________________________<br>
              TRNSYS-users mailing list<br>
              <a moz-do-not-send="true"
                href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
              <a moz-do-not-send="true"
                href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
              <br>
            </blockquote>
          </div>
          <br>
        </blockquote>
      </div>
      <br>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>