Dear all, <br><br><br>I want to compare the test room infiltration rate of actual measurement with by 
TRNSYS simulation. Maybe as you know, in the TRNFlow manual: there it is
 explained that "As soon as TRNFLOW is
 turned on, (...) in the simulation the defined infiltrations, 
ventilations and couplings will be replaced with the calculated air 
flows."<br>
I defined CO2% as 1000 ppm in TRNFlow, then I want to observe CO2%'s 
reducing curve when infiltration rate is 0.5276 1/h (I measured the 
value in the test room), so I defined the infiltration rate as 0.5276 
1/h in TRNBUILD. But when I used TRNFLOW, the defined  infiltration rate
 as 0.5276 1/h in TRNBUILD was replaced. And 1000 ppm keeps constant.<br>
<br>
Please  tell me  how to get   the infiltration rate curve using TRNSYS/TRNFLOW or how to explain this ?<br>
<br>
Many thanks!<br><br>br<br><br>wang<br><br><div class="gmail_quote">在 2011年2月21日 下午12:57, <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span>写道:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
Send TRNSYS-users mailing list submissions to<br>
        <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br>
<br>
   1. infiltration rate (??)<br>
   2. hi friends (sivareddy vundela)<br>
   3. Re: wall definition (Laia Cases - iMat)<br>
<br><br>---------- 已转发邮件 ----------<br>From: 王洋 <<a href="mailto:wanghongyang1767@gmail.com">wanghongyang1767@gmail.com</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>Date: Mon, 21 Feb 2011 12:07:29 +0100<br>
Subject: [TRNSYS-users] infiltration rate<br>Dear all, <br><br><br>I want to compare the test room infiltration rate of actual measurement with by 
TRNSYS simulation. Maybe as you know, in the TRNFlow manual: there it is
 explained that "As soon as TRNFLOW is
 turned on, (...) in the simulation the defined infiltrations, 
ventilations and couplings will be replaced with the calculated air 
flows."<br>
I defined CO2% as 1000 ppm in TRNFlow, then I want to observe CO2%'s 
reducing curve when infiltration rate is 0.5276 1/h (I measured the 
value in the test room), so I defined the infiltration rate as 0.5276 
1/h in TRNBUILD. But when I used TRNFLOW, the defined  infiltration rate
 as 0.5276 1/h in TRNBUILD was replaced. And 1000 ppm keeps constant.<br>
<br>
Please  tell me  how to get   the infiltration rate curve using TRNSYS/TRNFLOW or how to explain this ?<br>
<br>
Many thanks!<br><br>br<br><br>wang<br><br><div class="gmail_quote">2011/2/21  <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">

Send TRNSYS-users mailing list submissions to<br>
        <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br>
<br>
   1. Problems with calling EES (Type66a) (Doms Joris)<br>
   2. wall definition (davide disco)<br>
<br><br>---------- 已转发邮件 ----------<br>From: Doms Joris <<a href="mailto:joris.doms@vito.be" target="_blank">joris.doms@vito.be</a>><br>To: "<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>" <<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>

Date: Sun, 20 Feb 2011 22:43:08 +0100<br>Subject: [TRNSYS-users] Problems with calling EES (Type66a)<br>




<div>
<div>Dear TRNSYS users,</div>
<div><font face="times new roman"></font> </div>
<div><font face="times new roman">When simulating an applied thermal system, I'm using EES for the hydronic part. I programmed the hydronic circuit in EES and coupled it with TRNSYS via Type 66a. This coupling works fine, but;</font></div>


<div><font face="times new roman"></font> </div>
<div><font face="times new roman">The problem is that the simulation runs very slow. Every timestep that TRNSYS calls EES, the EES project is opened and closed. Is there a way to set some settings so EES isen't closed and reopened each time, this
 would minimize the solution time alot.</font></div>
<div><font face="times new roman"></font> </div>
<div><font face="times new roman">Thanks on advance</font></div>
<div><font face="times new roman"></font> </div>
<div><font face="times new roman">Joris Doms</font></div>
<br>
<p align="left"><font face="Tahoma" size="2"><font color="#0000ff">
<hr>
This e-mail, any attachments and the information it contains are confidential and meant only for the use of the addressee(s) only.  Access to this e-mail by anyone other than the addressee(s) is unauthorized.  If you are not the intended addressee (or responsible for delivery of the message to such person), you may not use, copy, distribute or deliver to anyone this message (or any part of its contents) or take any action in reliance on it.  In such case, you should destroy this message and notify the sender immediately.  If you have received this e-mail in error, please notify us immediately by e-mail or telephone and delete the e-mail from any computer.<br>

All reasonable precautions have been taken to ensure no viruses are present in this e-mail and its attachments.  As our company cannot accept responsibility for any loss or damage arising from the use of this e-mail or attachments we recommend that you subject these to your virus checking procedures prior to use.<br>


<hr>

<p></p></font></font></p></div>

<br><br>---------- 已转发邮件 ----------<br>From: davide disco <<a href="mailto:chester_83@hotmail.it" target="_blank">chester_83@hotmail.it</a>><br>To: <<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>

Date: Mon, 21 Feb 2011 11:57:59 +0100<br>Subject: [TRNSYS-users] wall definition<br>



<div>
Dear all,<br>when entering data in Trnbuild I have to describe the walls of the zone: if, looking at the plant of the building, the building has more than a wall south oriented for example (wall to the left in the plant) <span lang="en"><span title="Fai clic per visualizzare le traduzioni alternative">I</span> <span title="Fai clic per visualizzare le traduzioni alternative">should</span> <span title="Fai clic per visualizzare le traduzioni alternative">enter in T</span><span title="Fai clic per visualizzare le traduzioni alternative">rnbuild</span> <span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative">each section</span> <span title="Fai clic per visualizzare le traduzioni alternative">of</span> <span title="Fai clic per visualizzare le traduzioni alternative">wall</span> <span title="Fai clic per visualizzare le traduzioni alternative">facing south or I should enter a unique wall that is the sum of all sections of wall facing south?<br>

Thanks in advace.<br>Best regards<br></span></span>                                       </div>
<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br>
<br><br>---------- 已转发邮件 ----------<br>From: sivareddy vundela <<a href="mailto:vundelaap@gmail.com">vundelaap@gmail.com</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>Date: Mon, 21 Feb 2011 17:17:37 +0530<br>
Subject: [TRNSYS-users] hi friends<br><br clear="all">I have small problem in transys 16 software installation.<br><br>i got  STEC model library  file for TRNSYS 16 .<br>but i don't no how to attach to TRNSYS 16 library.<br>
you have any idea about how to instale extended library files in  TRNSYS 16.<br>
please do favor to me.<br><br>Your early action in this matter is highly solicited.<br>-- <br><br>With Regards<br><br><br>V.Siva Reddy<br>Research Scholar ,<br>Center for Energy Studies,<br>IIT-Delhi.<br>PhNo:9891742963.<br>


<br><br>---------- 已转发邮件 ----------<br>From: Laia Cases - iMat <<a href="mailto:lcases@imat.cat">lcases@imat.cat</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>Date: Mon, 21 Feb 2011 12:56:57 +0100<br>
Subject: Re: [TRNSYS-users] wall definition<br>

  
    
  
  <div bgcolor="#ffffff" text="#000000">
    Hi Davide,<br>
    <br>
    if the wall is the same in all the sections, and there is a unic
    space... so you can enter the wall as a unique wall.<br>
    <br>
    Laia Cases<br>
    <br>
    El 21/02/2011 11:57, davide disco escribió:
    <blockquote type="cite">
      
      Dear all,<br>
      when entering data in Trnbuild I have to describe the walls of the
      zone: if, looking at the plant of the building, the building has
      more than a wall south oriented for example (wall to the left in
      the plant) <span lang="en"><span title="Fai clic
          per visualizzare le traduzioni alternative">I</span>
        <span title="Fai clic per visualizzare le traduzioni
          alternative">should</span> <span title="Fai clic
          per visualizzare le traduzioni alternative">enter
          in T</span><span title="Fai clic per visualizzare le
          traduzioni alternative">rnbuild</span> <span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le
          traduzioni alternative">each section</span> <span title="Fai clic per visualizzare le traduzioni alternative">of</span> <span title="Fai clic per visualizzare
          le traduzioni alternative">wall</span> <span title="Fai clic per visualizzare le traduzioni alternative">facing south or I should enter a unique wall that
          is the sum of all sections of wall facing south?<br>
          Thanks in advace.<br>
          Best regards<br>
        </span></span>
      <pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <div>-- <br>
      
      <div>
        <table width="410" border="0" cellpadding="1" cellspacing="1" height="128">
          <tbody>
            <tr>
              <td valign="top"><img src="cid:part1.00030300.05060003@imat.cat" width="100" height="43"></td>
              <td valign="top">
                <span style="font-size: 8pt; font-family: Arial; color: green;">
                  <b>Laia Cases</b><br>
                  Unitat de Condicionament Tèrmic<br>
                  <b>iMat - Centre Tecnològic de la Construcció<br>
                    <a href="mailto:lcases@imat.cat" target="_blank">lcases@imat.cat</a><br>
                    <a href="http://www.imat.cat/" target="_blank">www.imat.cat</a></b><br>
                </span></td>
            </tr>
            <tr>
              <td valign="bottom"><img src="cid:part2.03020408.09010404@imat.cat" width="99" height="42"></td>
              <td valign="top"><span style="font-size: 8pt; font-family: Arial; color: green;">
                  Wellington 23  ·   E-08018 Barcelona<br>
                  T +34 93 553 97 95<br>
                  F +34 93 553 97 96<br>
                  Imprimiu aquest document només si és necessari</span>
              </td>
            </tr>
          </tbody>
        </table>
      </div>
    </div>
  </div>

<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br>