Dear all,<br>I have a queation about TRNFLOW'S large openig and Ventilation in TRNBUILD:<br><br> If I defined TRNFLOW'S large openig and Ventilation in TRNBUILD, <br>
How can both of them work? Can they both have influences on each other?
What does the QVENT include? Only Ventilation in TRNBUILD or both of
them? What does the FLVSZ include? Only TRNFLOW'S large openig's
Ventilation?<br>
<br>Many thanks!<br><br>br.<br><br>wang<br><div><br></div><br><br><div class="gmail_quote">2011/2/9 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">Send TRNSYS-users mailing list submissions to<br>
<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br>
<br>
1. (no subject) (davide disco)<br>
2. Re: TYPECK () (Farah Gammoh)<br>
3. Type 15-2_Simulation start time (Felix Martin Beutefuehr, BLV-TGE)<br>
4. INTERNATIONAL TRNSYS DAY, COURSES & NETWORKING (Info Aiguasol)<br>
<br><br>---------- 已转发邮件 ----------<br>From: davide disco <<a href="mailto:chester_83@hotmail.it">chester_83@hotmail.it</a>><br>To: <<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Wed, 9 Feb 2011 01:23:50 +0100<br>Subject: [TRNSYS-users] (no subject)<br>
<div>
Hello,<br>when I add a wall I <span lang="en"><span title="Fai clic per visualizzare le traduzioni alternative">have</span> <span title="Fai clic per visualizzare le traduzioni alternative">to specify</span> <span title="Fai clic per visualizzare le traduzioni alternative">the</span> <span title="Fai clic per visualizzare le traduzioni alternative">layers</span> <span title="Fai clic per visualizzare le traduzioni alternative">that</span> <span title="Fai clic per visualizzare le traduzioni alternative">make up</span> <span title="Fai clic per visualizzare le traduzioni alternative">the</span> <span title="Fai clic per visualizzare le traduzioni alternative">wall, and for each new layer Trnsys requires three quantities: conductivity, capacity and density.<br>
Now, the capacity is expressed in KJ/(Kg K), but for the layers of wall I have the </span></span>thermal conductivity (expressed in W/m²·K) instead of the capacity <span lang="en"><span title="Fai clic per visualizzare le traduzioni alternative">as</span> <span title="Fai clic per visualizzare le traduzioni alternative">required</span> <span title="Fai clic per visualizzare le traduzioni alternative">by</span> <span title="Fai clic per visualizzare le traduzioni alternative">the program.<br>
There is a way to correlate this two quantities so that I can enter the thermal conductivity instead of the capacity?</span></span><span lang="en"><span title="Fai clic per visualizzare le traduzioni alternative"></span></span><span lang="en"><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"></span><span title="Fai clic per visualizzare le traduzioni alternative"><br>
<br>Thanks in advance<br></span></span> </div>
<br><br>---------- 已转发邮件 ----------<br>From: Farah Gammoh <<a href="mailto:farah.gammoh@mirroxx.com">farah.gammoh@mirroxx.com</a>><br>To: "<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>" <<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>><br>
Date: Wed, 09 Feb 2011 11:58:36 +0100<br>Subject: Re: [TRNSYS-users] TYPECK ()<br>Hello,<br>
could someone please explain to me the last three parameters of the typeck subroutine? what are the correct INPUT, PARAMETER and DERIVATIVE parameters to pass on? do they refer to the total number in the entire type?<br>
thanks in advance<br>
Farah<br>
davide disco schrieb:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
Hello,<br>
when I add a wall I have to specify the layers that make up the wall, and for each new layer Trnsys requires three quantities: conductivity, capacity and density.<br>
Now, the capacity is expressed in KJ/(Kg K), but for the layers of wall I have the thermal conductivity (expressed in W/m²·K) instead of the capacity as required by the program.<br>
There is a way to correlate this two quantities so that I can enter the thermal conductivity instead of the capacity?<br>
<br>
Thanks in advance<br>
------------------------------------------------------------------------<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br>
</blockquote>
<br>
<br>
-- <br>
<br>
Mirroxx Logo <image002.gif><br>
<br>
<br>
<br>
<br>
<br>
* *<br>
<br>
<br>
<br>
<br>
<br>
Farah Gammoh<br>
MSc. Energy Conversion and Management<br>
<br>
Engineering<br>
<br>
<br>
<br>
*Mirroxx GmbH*<br>
<br>
*Emmy-Noether-Str. 2*<br>
<br>
*79110 Freiburg*<br>
<br>
*Germany*<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
T (++49) 761 - 767 111-0<br>
<br>
F (++49) 761 - 767 111-99<br>
<br>
<a href="mailto:farah.gammoh@mirroxx.com" target="_blank">farah.gammoh@mirroxx.com</a> <mailto:<a href="mailto:farah.gammoh@mirroxx.com" target="_blank">farah.gammoh@mirroxx.com</a>><br>
<br>
<a href="http://www.mirroxx.com" target="_blank">www.mirroxx.com</a> <<a href="http://www.mirroxx.com/" target="_blank">http://www.mirroxx.com/</a>><br>
<br>
<br>
<br>
*Register*<br>
<br>
Amtsgericht Freiburg<br>
<br>
HRB 703185<br>
<br>
<br>
<br>
<br>
<br><br>---------- 已转发邮件 ----------<br>From: "Felix Martin Beutefuehr, BLV-TGE" <<a href="mailto:beutefuf@fh-trier.de">beutefuf@fh-trier.de</a>><br>To: <a href="mailto:trnsys-users@engr.wisc.edu">trnsys-users@engr.wisc.edu</a><br>
Date: Wed, 9 Feb 2011 12:00:50 +0100<br>Subject: [TRNSYS-users] Type 15-2_Simulation start time<br><br>
Dear Trnsys users,<br>
<br>
I am using Type 15-2 and i am using a simulation timestep of 3 min. If the<br>
simulation start time is 0 hr, everything works out fine. But once i change<br>
the simulation starttime to 2000 hours i get the following error<br>
massage_"unable to correctly read from the supplied data file-please check<br>
the file and re-run the simulation". This massage refers to Type 15-2.<br>
If I then change the simulation time step to 1 hour and re run the<br>
simulation, no error occurs.<br>
<br>
So what can I do to if I want a simulation time step within the range of 1-5<br>
min?<br>
<br>
Many thanks in advance<br>
<br>
Felix<br>
<br>
--<br>
<a href="http://webmail.fh-trier.de" target="_blank">http://webmail.fh-trier.de</a><br>
<br>
<br>
<br><br>---------- 已转发邮件 ----------<br>From: Info Aiguasol <<a href="mailto:infoaiguasol@aiguasol.coop">infoaiguasol@aiguasol.coop</a>><br>To: Info Aiguasol <<a href="mailto:infoaiguasol@aiguasol.coop">infoaiguasol@aiguasol.coop</a>><br>
Date: Wed, 9 Feb 2011 12:29:15 +0100<br>Subject: [TRNSYS-users] INTERNATIONAL TRNSYS DAY, COURSES & NETWORKING<br>
<div link="blue" vlink="purple" lang="ES">
<div>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"> <span lang="CA"></span></p>
<div>
<div>
<div>
<table style="width: 623.3pt; border-collapse: collapse;" border="0" cellpadding="0" cellspacing="0" width="831">
<tbody><tr>
<td colspan="7" style="width: 623.3pt; border-width: 1pt 1pt medium; border-style: solid solid none; border-color: windowtext windowtext -moz-use-text-color; background: none repeat scroll 0% 0% rgb(242, 242, 242); padding: 0cm 7.1pt;" valign="top" width="831">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt; color: rgb(31, 73, 125);"><img src="cid:image003.png@01CBC84E.1BDE0310" alt="tud02.png" width="794" height="163"></span></p>
</td>
</tr>
<tr style="min-height: 545.75pt;">
<td style="width: 207.75pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(242, 242, 242); padding: 0cm 7.1pt; min-height: 545.75pt;" valign="top" width="277">
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-US">Dear
all,</span></p>
<p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-US"> We
are glad to invite you to the,</span><span> </span></p>
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/3/" target="_blank"><span style="color: rgb(255, 153, 0);">1st FOCUSED International TRNSYS Users’ Day</span></a></span></b></p>
<p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-US">that
will take place in Barcelona the next <b>April 5<sup>th</sup></b>, under
the frame of the</span><span> </span></p>
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/" target="_blank"><span style="color: rgb(255, 153, 0);">Energy Thinking days 2011</span></a></span></b></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(51, 51, 51);" lang="EN-US">As usual, TRNSYS users’ day wants to be a space for sharing
experiences in the use of our tool where to explain, ask and exchange ideas,
works, what to do and what not to. This time two different things will be
introduced. First of all, the <b>presentation of new version of TRNSYS,
17<sup><span style="border: 1pt none windowtext; padding: 0cm;">th</span></sup></b>,
with its main new features, especially it’s Sketch up plug-in, with a demo.
And, also new, the idea of having a <b>technologically focused workshop</b>:
we ask you to present your <b>works on</b></span></p>
<p class="MsoNormal"><b><span style="font-size: 2pt; color: rgb(31, 73, 125);" lang="EN-US"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 10pt; color: rgb(51, 51, 51);" lang="EN-US">solar thermal coupled with DHC, heat pumps and/or seasonal
storage,</span></b></p>
<p class="MsoNormal"><b><span style="font-size: 10pt; color: rgb(51, 51, 51);" lang="EN-US">and also DHC and seasonal storage by itself</span></b><span style="font-size: 10pt; color: rgb(51, 51, 51);" lang="EN-US">.</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(51, 51, 51);" lang="EN-US">The aim is to have a technical meeting focused on systems
simulation useful for the 44<sup><span style="border: 1pt none windowtext; padding: 0cm;">th</span> </sup>and 45<sup><span style="border: 1pt none windowtext; padding: 0cm;">th</span></sup> IEA Tasks work that will have their meeting
in Barcelona the same weeks. We hope this effort will be useful for all.</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
</td>
<td colspan="4" style="width: 207.85pt; background: none repeat scroll 0% 0% rgb(234, 234, 234); padding: 0cm 7.1pt; min-height: 545.75pt;" valign="top" width="277">
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 10pt; color: rgb(31, 73, 125);" lang="EN-US"> </span></b></p>
<p class="MsoNormal"><span style="font-size: 10pt;"> <i>Benvolguts,</i></span></p>
<p class="MsoNormal"><i><span style="font-size: 10pt;"> Ens plau
convidar-vos al,</span></i><span> </span></p>
<p class="MsoNormal" style="text-align: center;" align="center"><b><i><span style="font-size: 14pt; color: rgb(255, 153, 0);"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/3/" target="_blank"><span style="color: rgb(255, 153, 0);">1st FOCUSED International
TRNSYS Users’ Day</span></a></span></i></b></p>
<p class="MsoNormal"><b><i><span style="font-size: 10pt;"> </span></i></b><i><span style="font-size: 10pt;">que tindrà lloc a
Barcelona el proper <b>5 d’abril</b> sota el paraigües dels</span></i><span> </span></p>
<p class="MsoNormal" style="text-align: center;" align="center"><b><i><span style="font-size: 14pt; color: rgb(255, 153, 0);"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/" target="_blank"><span style="color: rgb(255, 153, 0);">Energy Thinking days 2011</span></a></span></i></b></p>
<p class="MsoNormal"><i><span style="font-size: 10pt;"> <span style="color: rgb(51, 51, 51);">Com de costum, el dia els usuaris de TRNSYS vol ser un
espai per compartir experiències en l'ús de la nostra eina, per explicar,
preguntar i intercanviar idees, treballs, què fer i què no. Aquesta vegada
dues coses noves. En primer lloc, la <b>presentació de la nova versió de
TRNSYS, la 17</b>, amb les seves principals novetats, sobretot el
plug-in d’Sketch-Up, amb una demostració. I, també nou, la voluntat de
ser <b>un taller de tecnologia enfocada</b>: us demanem que presenteu
els vostres treballs sobre</span></span></i></p>
<p class="MsoNormal"><span> </span><span style="font-size: 7pt; color: rgb(51, 51, 51);"> </span><b><i><span style="font-size: 10pt; color: rgb(51, 51, 51);">solar
tèrmica acoblada amb DHC, bombes de calor i/o acumulació estacional</span></i></b></p>
<p class="MsoNormal"><b><i><span style="font-size: 10pt; color: rgb(51, 51, 51);">i
també, DHC i acumulació estacional en sí mateixos.</span></i></b></p>
<p class="MsoNormal"><i><span style="font-size: 10pt;">L’objectiu és
aconseguir una trobada tècnica focalitzada en simulació de sistemes que sigui
d’utilitat per a les Tasks 44 i 45 de la IEA, que es trobaran a Barcelona la
mateixa setmana. Esperem que aquest esforç sigui útil per a tothom.</span></i></p>
<p class="MsoNormal" style="text-align: center;" align="center"><span> </span></p>
</td>
<td colspan="2" style="width: 207.7pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt; min-height: 545.75pt;" valign="top" width="277">
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 10pt;">Estimados,</span></p>
<p class="MsoNormal"><span style="font-size: 10pt;">Nos complace
invitaros al,</span><span> </span></p>
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/3/" target="_blank"><span style="color: rgb(255, 153, 0);" lang="ES">1st FOCU</span><span style="color: rgb(255, 153, 0);">SED
International TRNSYS Users' Day</span></a></span></b></p>
<p class="MsoNormal"><span> </span><span style="font-size: 10pt;">que tendrá lugar en Barcelona <span style="color: rgb(31, 73, 125);">e</span>l <b>próximo 5 de abril</b> bajo el paraguas de
los</span><span> </span></p>
<p class="MsoNormal" style="text-align: center;" align="center"><b><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/" target="_blank"><span style="color: rgb(255, 153, 0);" lang="ES">Energy Thinking days 2011</span></a></span></b></p>
<p class="MsoNormal"><span> </span><span style="font-size: 10pt; color: rgb(51, 51, 51);">Como de costumbre, el
día los usuarios de TRNSYS quiere ser un espacio para compartir experiencias
en el uso de nuestra herramienta, para explicar, preguntar e intercambiar
ideas, trabajos, qué hacer y qué no. Esta vez dos cosas nuevas. En primer
lugar, <b>la presentación de la nueva versión de TRNSYS, la 17</b>, con sus
principales novedades, sobre todo el plug-in de Sketch-Up, con una
demostración. Y, también nuevo, la voluntad de ser <b>un taller de tecnología
enfocada</b>: os pedimos que presentéis vuestros trabajos sobre </span></p>
<p class="MsoNormal"><b><span style="font-size: 10pt; color: rgb(51, 51, 51);">solar
térmica acoplada con DHC, bombas de calor y / o acumulación estacional </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 10pt; color: rgb(51, 51, 51);">y
también, DHC y acumulación estacional en sí mismos.</span></b></p>
<p class="MsoNormal"><span style="font-size: 10pt;">El objetivo es
conseguir un encuentro técnico focalizada en simulación de sistemas que sea
de utilidad para las Tasks 44 y 45 de la IEA, que se encontrarán en Barcelona
la misma semana. Esperamos que este esfuerzo sea útil para todos.</span></p>
</td>
</tr>
<tr style="min-height: 59pt;">
<td style="width: 207.75pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(242, 242, 242); padding: 0cm 7.1pt; min-height: 59pt;" valign="top" width="277">
<p class="MsoNormal"><b><span style="font-size: 14pt; color: rgb(51, 51, 51);" lang="EN-US">Please send your abstracts before February 25<sup>th</sup>. </span></b><span style="font-size: 10pt; color: rgb(51, 51, 51);" lang="EN-US"> </span><b><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/3/" target="_blank"><span style="color: rgb(255, 153, 0);">info ></span></a></span></b></p>
</td>
<td colspan="4" style="width: 207.85pt; background: none repeat scroll 0% 0% rgb(234, 234, 234); padding: 0cm 7.1pt; min-height: 59pt;" valign="top" width="277">
<p class="MsoNormal"><b><i><span style="font-size: 14pt; color: rgb(51, 51, 51);">Sisplau,
envieu els vostres resums abans del 25 de Febrer. </span></i></b><i><span style="font-size: 10pt;"> </span></i><b><i><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/3/" target="_blank"><span style="color: rgb(255, 153, 0);" lang="ES">info ></span></a></span></i></b></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
</td>
<td colspan="2" style="width: 207.7pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt; min-height: 59pt;" valign="top" width="277">
<p class="MsoNormal"><b><span style="font-size: 13.5pt;">Por favor, envía tus
resúmenes antes del 25 de Febrero. </span></b><b><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US"><a href="http://aiguasol.coop/2011/01/energy-thinking-days/3/" target="_blank"><span style="color: rgb(255, 153, 0);" lang="ES">info ></span></a></span></b></p>
<p class="MsoNormal"><span> </span></p>
</td>
</tr>
<tr>
<td colspan="4" style="width: 327.85pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="437">
<p class="MsoNormal"><b><span style="font-size: 14pt; color: rgb(31, 73, 125);"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 14pt; color: rgb(255, 153, 0);" lang="EN-US">Other Energy Thinking days’ events:</span></b></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">> </span><b><span style="color: black;" lang="EN-US"><a href="http://aiguasol.coop/2011/02/energy-thinking-days/2/" target="_blank"><span style="font-size: 10pt; color: black; text-decoration: none;" lang="ES">ecoheat</span><span style="font-size: 10pt; color: black; text-decoration: none;">4eu DHC open
workshop</span></a></span></b></p>
</td>
<td colspan="2" style="width: 90pt; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="120">
<p class="MsoNormal" style="text-align: right;" align="right"><span style="font-size: 10pt; color: black;" lang="EN-US">4 April </span></p>
</td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" width="274">
</td>
</tr>
<tr>
<td colspan="4" style="width: 327.85pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="437">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;" lang="EN-US">> </span><b><span style="color: black;"><a href="http://aiguasol.coop/2011/02/energy-thinking-days/3/" target="_blank"><span style="font-size: 10pt; color: black; text-decoration: none;" lang="EN-US">1st FOCUSED International TRNSYS Users’ Day</span></a></span></b></p>
</td>
<td colspan="2" style="width: 90pt; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="120">
<p class="MsoNormal" style="text-align: right;" align="right"><span style="font-size: 10pt; color: black;" lang="EN-US">5 April</span></p>
</td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" width="274">
</td>
</tr>
<tr>
<td colspan="4" style="width: 327.85pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="437">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">><b>
</b></span><b><span style="color: black;"><a href="http://www.iea-shc.org/task45/" target="_blank"><span style="font-size: 10pt; color: black; text-decoration: none;" lang="EN-US">IEA-SHC Task 45
Meeting</span></a></span></b></p>
</td>
<td colspan="2" style="width: 90pt; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="120">
<p class="MsoNormal" style="text-align: right;" align="right"><span style="font-size: 10pt; color: black;" lang="EN-US">5,6 April</span></p>
</td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" width="274">
</td>
</tr>
<tr>
<td colspan="4" style="width: 327.85pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="437">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">><b>
</b></span><b><span style="color: black;"><a href="http://aiguasol.coop/2011/02/energy-thinking-days/4/" target="_blank"><span style="font-size: 10pt; color: black; text-decoration: none;" lang="EN-US">IEA-SHC
Tasks’ Experts Open Workshop</span></a></span></b></p>
</td>
<td colspan="2" style="width: 90pt; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="120">
<p class="MsoNormal" style="text-align: right;" align="right"><span style="font-size: 10pt; color: black;" lang="EN-US">6 April</span></p>
</td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" width="274">
</td>
</tr>
<tr>
<td colspan="4" style="width: 327.85pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="437">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">> </span><b><span style="color: black;"><a href="http://aiguasol.coop/wp-content/uploads/2011/02/Curso-iniciaci%C3%B3n-a-TRNSYS17+Simulaci%C3%B3n-de-Edificios.pdf" target="_blank"><span style="font-size: 10pt; color: black; text-decoration: none;">Curso iniciación a TRNSYS17 y simulación de edificios</span></a></span></b></p>
</td>
<td colspan="2" style="width: 90pt; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="120">
<p class="MsoNormal" style="text-align: right;" align="right"><span style="font-size: 10pt; color: black;" lang="EN-US">6,7,8 April</span></p>
</td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" width="274">
</td>
</tr>
<tr>
<td colspan="4" style="width: 327.85pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="437">
<p class="MsoNormal"><span style="font-size: 10pt; color: black;">> </span><b><span style="color: black;"><a href="http://aiguasol.coop/wp-content/uploads/2011/02/Curso-de-simulaci%C3%B3n-de-CSP-con-TRNSYS17.pdf" target="_blank"><span style="font-size: 10pt; color: black; text-decoration: none;">Curso de simulación de CSP con TRNSYS17. </span></a></span></b></p>
</td>
<td colspan="2" style="width: 90pt; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="120">
<p class="MsoNormal" style="text-align: right;" align="right"><span style="font-size: 10pt; color: black;" lang="EN-US">6,7,8 April</span></p>
</td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" width="274">
</td>
</tr>
<tr>
<td colspan="4" style="width: 327.85pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="top" width="437">
<p class="MsoNormal"><span style="color: black;" lang="EN-US">><b> </b></span><b><span style="color: black;"><a href="http://www.iea-shc.org/task44/" target="_blank"><span style="font-size: 10pt; color: black; text-decoration: none;" lang="EN-US">IEA-SHC Task 44
Meeting</span></a></span></b></p>
</td>
<td colspan="2" style="width: 90pt; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="top" width="120">
<p class="MsoNormal" style="text-align: right;" align="right"><span style="font-size: 10pt; color: black;" lang="EN-US">7,8 April </span></p>
</td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; background: none repeat scroll 0% 0% rgb(221, 221, 221); padding: 0cm 7.1pt;" valign="bottom" width="274">
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
</td>
</tr>
<tr>
<td colspan="3" style="width: 253.5pt; border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color windowtext; padding: 0cm 7.1pt;" width="338">
</td>
<td style="width: 74.35pt; padding: 0cm 7.1pt;" width="99"></td>
<td colspan="2" style="width: 90pt; padding: 0cm 7.1pt;" width="120"></td>
<td style="width: 205.45pt; border-width: medium 1pt medium medium; border-style: none solid none none; border-color: -moz-use-text-color windowtext -moz-use-text-color -moz-use-text-color; padding: 0cm 7.1pt;" width="274">
</td>
</tr>
<tr>
<td colspan="2" style="width: 212.25pt; border-width: medium medium 1pt 1pt; border-style: none none solid solid; border-color: -moz-use-text-color -moz-use-text-color windowtext windowtext; padding: 0cm 7.1pt;" width="283">
</td>
<td style="width: 41.25pt; border-width: medium medium 1pt; border-style: none none solid; border-color: -moz-use-text-color -moz-use-text-color windowtext; padding: 0cm 7.1pt;" width="55"></td>
<td style="width: 74.35pt; border-width: medium medium 1pt; border-style: none none solid; border-color: -moz-use-text-color -moz-use-text-color windowtext; padding: 0cm 7.1pt;" width="99"></td>
<td colspan="2" style="width: 90pt; border-width: medium medium 1pt; border-style: none none solid; border-color: -moz-use-text-color -moz-use-text-color windowtext; padding: 0cm 7.1pt;" width="120"></td>
<td style="width: 205.45pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0cm 7.1pt;" width="274"></td>
</tr>
<tr>
<td style="width: 207.75pt; padding: 0cm;" width="277"></td>
<td style="width: 4.5pt; padding: 0cm;" width="6"></td>
<td style="width: 41.25pt; padding: 0cm;" width="55"></td>
<td style="width: 74.35pt; padding: 0cm;" width="99"></td>
<td style="width: 87.75pt; padding: 0cm;" width="117"></td>
<td style="width: 2.25pt; padding: 0cm;" width="3"></td>
<td style="width: 205.45pt; padding: 0cm;" width="274"></td>
</tr>
</tbody></table>
<p class="MsoNormal"><span lang="CA"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);" lang="CA"> </span><span style="color: black;" lang="EN-US"> </span><span lang="CA"></span></p>
</div>
</div>
</div>
</div>
</div>
<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br>