    Rambod,<br>
      I assume that by umin and umax, you mean inputs 4 and 5. If that
    is the case then this inputs simply define the range of the
    controller's output. If you want to control a pump between fully off
    and fully on at its rated flow rate then you might choose 0 and 1
    for your limits (as in the SDHW-Feedback example). If you wanted the
    controller to set the flow rate directly then you would set umin to
    0 and umax to the maximum allowable flow rate.<br>
    <br>
      As for the issue of the temperature being above 120C when flow
    rate is zero, that seems quite possible since collectors can reach
    very high "stagnation" temperatures when there is no flow through
    them. It may be that under those circumstances, your controller
    cannot meet 120C at any flow rate so hits its limit on the number of
    times that it can change control decisions before it "sticks"
    (oscillation limit parameter).<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 1/16/2011 16:49, Rambod Rayegan wrote:
    <blockquote
      cite="mid:AANLkTi=KcE3AYMhfHUEHuYRcvgE--0Y4O0yMf9A9CMw9@mail.gmail.com"
      type="cite"><br clear="all">
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font size="3"><font
            face="Calibri">Dear TRNSYS users,</font></font></p>
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font
          face="Calibri" size="3"> </font></p>
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font size="3"><font
            face="Calibri">I created a TRNSYS file to simulate the
            performance of a flat plate collector. In this file I used a
            feedback controller to set the collector’s output
            temperature on 120 <span style="">°</span>C.<span style=""> 
            </span>I checked the TRNSYS example “SDHW-Feedback
            controller” and I chose umin and umax equal to 0 and 1
            respectively. </font></font></p>
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font size="3"><font
            face="Calibri">When I check the results I see that in some
            time steps temperature is higher than 120 <span style="">°</span>C
            while flow rate is zero. BY changing umax in feedback
            controller the results are being modified slightly but I
            don’t know how I can find the optimum umax. </font></font></p>
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font size="3"><font
            face="Calibri">Actually I am not sure that changing umax
            will solve the problem.</font></font></p>
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font size="3"><font
            face="Calibri">Attached to this email you can find a copy of
            my file.</font></font></p>
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font size="3"><font
            face="Calibri">Thank you.</font></font></p>
      <p style="margin: 0in 0in 10pt;" class="MsoNormal"><font size="3"><font
            face="Calibri">Rambod</font></font></p>
      <br>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>