Dear all,<br> <br>   Please tell me what's meaning of Wall's Convective heat transfer coefficient and Solar absorptance: Front and Back?<br> <br>   Front means: to the indoor? Back means: to the outdoor?<br> <br>  If I calculate the total heating energy of one room, whether QHEAT include  Wall's Convective heat transfer and Solar absorptance's Front and Back or not?  <br>
 <br>  Many thanks!<br> <br> Br.<br> <br>wang<br><br>
<div class="gmail_quote">在 2011年1月14日 下午9:40,王洋 <span dir="ltr"><<a href="mailto:wanghongyang1767@gmail.com">wanghongyang1767@gmail.com</a>></span>写道:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>Dear all,</div>
<div> </div>
<div>   Please tell me what's meaning of Wall's Convective heat transfer coefficient and Solar absorptance:<font color="#000066"> </font><font color="#000099">Front and Back?</font></div>
<div><font color="#000099"></font> </div>
<div><font color="#000099">   Front means: to the indoor? Back means: to the outdoor?</font></div>
<div><font color="#000099"></font> </div>
<div><font color="#000099">  <font color="#000000">If I calculate the total heating energy of one room, whether QHEAT include  Wall's Convective heat transfer and Solar absorptance's Front and Back or not?  </font></font></div>
<div><font color="#000099"><font color="#000000"></font></font> </div>
<div><font color="#000099"><font color="#000000">  Many thanks!</font></font></div>
<div><font color="#000099"><font color="#000000"></font></font> </div>
<div><font color="#000099"><font color="#000000"> Br.</font></font></div>
<div><font color="#000099"><font color="#000000"></font></font> </div>
<div><font color="#000099"><font color="#000000">wang</font></font></div>
<div><br><br></div>
<div class="gmail_quote">2011/1/14 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br>       <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br>       <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>or, via email, send a message with subject or body 'help' to<br>
       <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br>       <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br><br>Today's Topics:<br><br>  1. Equation tool (Rambod Rayegan)<br>  2. TRNSYS Manual (Rambod Rayegan)<br>
  3. Re: Equation tool (Mehdi Shahrestani)<br>  4. Re: TRNSYS Manual (Matt Duffy)<br>  5. Re: TRNSYS Manual (Mehdi Shahrestani)<br><br><br>---------- 已转发邮件 ----------<br>From: Rambod Rayegan <<a href="mailto:rraye001@fiu.edu" target="_blank">rraye001@fiu.edu</a>><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>Date: Fri, 14 Jan 2011 14:19:11 -0500<br>Subject: [TRNSYS-users] Equation tool<br>
<div>Dear TRNSYS users,</div>
<div> </div>
<div>I don't know  how can I find the function of each botton (like GT, LT, LE, AE, NE, STEP,  ...) in the equation tool of the TRNSYS. </div>
<div>Is there any file or section in the TRNSYS documentation files that explain equation tool functions?</div>
<div> </div>
<div>Thank you,</div>
<div> </div>
<div>Rambod<br clear="all"><br></div><br><br>---------- 已转发邮件 ----------<br>From: Rambod Rayegan <<a href="mailto:rraye001@fiu.edu" target="_blank">rraye001@fiu.edu</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Date: Fri, 14 Jan 2011 14:24:18 -0500<br>Subject: [TRNSYS-users] TRNSYS Manual<br>
<div><br clear="all">Dear TRNSYS users,</div>
<div> </div>
<div>Is ther any file named" TRNSYS Manual " in your documents after installing the software.?</div>
<div>It seems sometime in some documents the author refers to TRNSYS Manual. I have not such a document in my documenation folder.</div>
<div> </div>
<div>Thank you,</div>
<div> </div>
<div>Rambod<br></div><br><br>---------- 已转发邮件 ----------<br>From: "Mehdi Shahrestani" <<a href="mailto:mahdishahrestani@yahoo.com" target="_blank">mahdishahrestani@yahoo.com</a>><br>To: "'Rambod Rayegan'" <<a href="mailto:rraye001@fiu.edu" target="_blank">rraye001@fiu.edu</a>><br>
Date: Fri, 14 Jan 2011 19:30:58 -0000<br>Subject: Re: [TRNSYS-users] Equation tool<br>
<div lang="EN-GB" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Dear Rambod</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Just go to Trnsys manual volume 6 page 25.</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">You can find all of them in that page. Moreover, you can find them as a FORTRAN functions in each FORTRAN book.</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Anyway, if you do not have that page let me know I am online tonight.</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Nice to hearing you</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Mehdi</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt"> </span></font></p>
<div>
<div style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt" lang="EN-US">
<hr align="center" size="2" width="100%">
</span></font></div>
<p class="MsoNormal"><b><font size="2" face="Tahoma"><span style="FONT-FAMILY: Tahoma; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">From:</span></font></b><font size="2" face="Tahoma"><span style="FONT-FAMILY: Tahoma; FONT-SIZE: 10pt" lang="EN-US"> <a href="mailto:trnsys-users-bounces@cae.wisc.edu" target="_blank">trnsys-users-bounces@cae.wisc.edu</a> [mailto:<a href="mailto:trnsys-users-bounces@cae.wisc.edu" target="_blank">trnsys-users-bounces@cae.wisc.edu</a>] <b><span style="FONT-WEIGHT: bold">On Behalf Of </span></b>Rambod Rayegan<br>
<b><span style="FONT-WEIGHT: bold">Sent:</span></b> 14 January 2011 19:19<br><b><span style="FONT-WEIGHT: bold">To:</span></b> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br><b><span style="FONT-WEIGHT: bold">Subject:</span></b> [TRNSYS-users] Equation tool</span></font><span lang="EN-US"></span></p>
</div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Dear TRNSYS users,</span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">I don't know  how can I find the function of each botton (like GT, LT, LE, AE, NE, STEP,  ...) in the equation tool of the TRNSYS. </span></font></p>
</div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Is there any file or section in the TRNSYS documentation files that explain equation tool functions?</span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Thank you,</span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Rambod<br clear="all"></span></font></p></div></div></div><br><br>---------- 已转发邮件 ----------<br>From: "Matt Duffy" <<a href="mailto:duffy@tess-inc.com" target="_blank">duffy@tess-inc.com</a>><br>
To: "Rambod Rayegan" <<a href="mailto:rraye001@fiu.edu" target="_blank">rraye001@fiu.edu</a>>, <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>Date: Fri, 14 Jan 2011 13:38:12 -0600 (CST)<br>
Subject: Re: [TRNSYS-users] TRNSYS Manual<br><br>Rambod,<br><br>Simply hit the "F1" button to open the documentation main menu, or you can click on the "?" icon in the Studio. You can manually go to the documentaiton folder as well, ".\Documentation".<br>
<br>The section about the logical functions is in the TRNEdit manual - Volume 6 - section 6.3.9.1.<br><br>Best regards,<br><br>Mat Duffy<br><br>
<div style="BACKGROUND-REPEAT: repeat-x"><strong>----- Original Message -----</strong><br><strong>From:</strong> "Rambod Rayegan" <<a href="mailto:rraye001@fiu.edu" target="_blank">rraye001@fiu.edu</a>> <br>
<strong>Sent:</strong> Fri, January 14, 2011 13:24<br><strong>Subject:</strong> [TRNSYS-users] TRNSYS Manual<br><br>
<div>
<div><br clear="all">Dear TRNSYS users,</div>
<div> </div>
<div>Is ther any file named" TRNSYS Manual &qu! ot; in your documents after installing the software.?</div>
<div>It seems sometime in some documents the author refers to TRNSYS Manual. I have not such a document in my documenation folder.</div>
<div> </div>
<div>Thank you,</div>
<div> </div>
<div>Rambod<br> </div>
<hr size="1" noshade>
<pre>_______________________________________________
TRNSYS-users mailing list
<a>TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre></div></div><br><br>---------- 已转发邮件 ----------<br>From: "Mehdi Shahrestani" <<a href="mailto:mahdishahrestani@yahoo.com" target="_blank">mahdishahrestani@yahoo.com</a>><br>To: "'Rambod Rayegan'" <<a href="mailto:rraye001@fiu.edu" target="_blank">rraye001@fiu.edu</a>><br>
Date: Fri, 14 Jan 2011 19:40:09 -0000<br>Subject: Re: [TRNSYS-users] TRNSYS Manual<br>
<div lang="EN-GB" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Rambod </span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">At the top of your TRNSYS screen after “windows” there is a icon with this sign “?” .</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">If you go through that, manuals are there.</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Hope it helps</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt">Mehdi</span></font></p>
<p class="MsoNormal"><font color="blue" size="3" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: blue; FONT-SIZE: 12pt"> </span></font></p>
<div>
<div style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt" lang="EN-US">
<hr align="center" size="2" width="100%">
</span></font></div>
<p class="MsoNormal"><b><font size="2" face="Tahoma"><span style="FONT-FAMILY: Tahoma; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">From:</span></font></b><font size="2" face="Tahoma"><span style="FONT-FAMILY: Tahoma; FONT-SIZE: 10pt" lang="EN-US"> <a href="mailto:trnsys-users-bounces@cae.wisc.edu" target="_blank">trnsys-users-bounces@cae.wisc.edu</a> [mailto:<a href="mailto:trnsys-users-bounces@cae.wisc.edu" target="_blank">trnsys-users-bounces@cae.wisc.edu</a>] <b><span style="FONT-WEIGHT: bold">On Behalf Of </span></b>Rambod Rayegan<br>
<b><span style="FONT-WEIGHT: bold">Sent:</span></b> 14 January 2011 19:24<br><b><span style="FONT-WEIGHT: bold">To:</span></b> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br><b><span style="FONT-WEIGHT: bold">Subject:</span></b> [TRNSYS-users] TRNSYS Manual</span></font><span lang="EN-US"></span></p>
</div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"><br clear="all">Dear TRNSYS users,</span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Is ther any file named" TRNSYS Manual " in your documents after installing the software.?</span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">It seems sometime in some documents the author refers to TRNSYS Manual. I have not such a document in my documenation folder.</span></font></p>
</div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Thank you,</span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Rambod</span></font></p></div></div></div><br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br><br></blockquote></div><br></blockquote></div><br>