David,<br>
the variable names in Type56's inputs are just variable names.
They do not have any orientation information built into them. The
building takes as an input whatever amount of solar radiation you
tell it is incident on those surfaces. The orientation definition is
typically done in the weather data reading/processing component
(Type15) by setting the slope and azimuth of each of your building's
surfaces. The weather component will output total and beam radiation
as well as the angle of incidence (which is quite important as the
thermal properties of the windows in your building have angular
dependence to them)<br>
Best,<br>
David<br>
<br>
<br>
On 1/12/2011 10:12, <a class="moz-txt-link-abbreviated" href="mailto:david.irusta@idom.com">david.irusta@idom.com</a> wrote:
<blockquote
cite="mid:OF468024C9.6F949C12-ONC1257816.00579F84-C1257816.00587D13@idom.com"
type="cite"><font face="sans-serif" size="2">Hi!</font>
<br>
<br>
<font face="sans-serif" size="2">I want to study the relevance of
orientation
on energy efficiency in buildings.</font>
<br>
<br>
<font face="sans-serif" size="2">If I used type 56b with different
buildings
which only differ in their orientation,</font>
<br>
<br>
<font face="sans-serif" size="2">should I know how to get the Type
56b
inputs??:</font>
<br>
<br>
<font face="sans-serif" size="2">ITNORTH, ITSOUTH, ITEAST,ITWEST</font>
<br>
<br>
<font face="sans-serif" size="2">IBNORTH, IBSOUTH, IBEAST, IBWEST</font>
<br>
<br>
<font face="sans-serif" size="2">AINORTH, AISOUTH, AIEAST,AIWEST
(I think
these inputs aren´t relevant)</font>
<br>
<br>
<font face="sans-serif" size="2">or could I resolve it by other
way??</font>
<br>
<br>
<font face="sans-serif" size="2">Thank you so much,</font>
<br>
<font face="sans-serif" size="2">Best Regards.</font>
<br>
<br>
<font face="sans-serif" size="2">David Irusta.</font>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>