<div>Dear Mr. doell,</div>
<div> </div>
<div> Many thanks for your reply!</div>
<div> </div>
<div> 1. To case 2 and 3: I tried a larger time period 10 days. But the result is still that case 3 is about 4 times than case 2. Do you mean I should simulate one month or one year?</div>
<div> </div>
<div> 2. You're right, I didn't simulate any heat generation. Do you mean I should add the boiler into Active Layer(floor heating). If so, how to add the boiler into the Active Layer? Which type need i use?</div>
<div> </div>
<div>3. you mean Qheat is the case 1's real heat demand. Is the QALFL_Inlet of case 2 not the real heat demand? Is it samller than the real total heat demand? If so, how to get the real total heat demand of case 2 and 3?</div>
<div> </div>
<div>Many thanks!</div>
<div> </div>
<div>Br.</div>
<div> </div>
<div>wang</div>
<div> </div>
<div><br><br> </div>
<div class="gmail_quote">2011/1/7 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br> <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br> <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>or, via email, send a message with subject or body 'help' to<br>
<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br> <a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br><br>Today's Topics:<br><br> 1. Re: Total heating demand (??) (Jochen Doell)<br> 2. Type 927 (Water to Water Heat Pump) (Andrey Vyshnepolsky)<br>
<br><br>---------- 已转发邮件 ----------<br>From: Jochen Doell <<a href="mailto:jochen.doell@ise.fraunhofer.de">jochen.doell@ise.fraunhofer.de</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Fri, 07 Jan 2011 11:07:42 +0100<br>Subject: Re: [TRNSYS-users] Total heating demand (??)<br>Dear Wang,<br><br>Regarding your first question: I suspect the thermal capacity of the floor to cause the difference between case 2 and 3. Simulate a larger time period and this effect should get smaller.<br>
<br>About your second question, floor or wall heating systems are more efficient than radiator based heating systems because they demand lower inlet (or forward) temperatures. By this boiler (and potential storage) efficiency increases. Since you do not simulate any heat generation, these effects do not occur in your simulation.<br>
I expect the Qheat of case 1 to be the real heat demand and QALFL_Inlet of case 2 to be the heat delivered to the room by the active layer.<br><br>Hope this helps.<br><br>Best regards,<br>Jochen<br><br><br><a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a> schrieb:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br> <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>or, via email, send a message with subject or body 'help' to<br>
<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br> <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br> ------------------------------------------------------------------------<br><br>Today's Topics:<br>
<br> 1. Total heating demand (??)<br> 2. Re: question about wall gain (Knut Erik Enerstvedt)<br> 3. Re: question about wall gain (salim mokraoui)<br> <br>------------------------------------------------------------------------<br>
<br>Betreff:<br>[TRNSYS-users] Total heating demand<br>Von:<br>王洋 <<a href="mailto:wanghongyang1767@gmail.com" target="_blank">wanghongyang1767@gmail.com</a>><br>Datum:<br>Thu, 6 Jan 2011 21:16:10 +0100<br>An:<br><a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>An:<br><a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br><br><br>Dear all,<br><br> Happy new year!<br><br> I have a question about calculating total heating demand:<br><br>There is one same room to keep indoor temperature as 20°C one day 24 hours,<br>
the initial indoor temperature is 20°C, there is no infiltration no other<br>internal gains in the room. I used 3 different methods to calculate total<br>heating demand of one day, separately.<br><br>1.First is heating in TRNBuild: after using the INTEGRATOR TYPE 46, the<br>
QHEAT is about 34314 kJ.<br><br>2.Second is floor heating(active layer): after using the INTEGRATOR TYPE 46,<br>the QALFL_Inlet is about 33680.7kJ.<br><br>3.Third is still floor heating(active layer): after using the INTEGRATOR<br>
TYPE 46, but I used Q=CwaterMwater(Tinlet-Toutlet), the result of Q is<br>144639kJ.<br><br>My question is: 1) To 2 and 3: Why is the difference is so large? 3 is<br>almost 4 times than 3? I will get the total heating demand, which one is<br>
right? Why? What's different of both of them?<br><br>2) If 3 is right. Generally, the floor heating should be more energy-saving<br>than common heating. But here result is absolutely opposite. The common<br>heating is more energy-heating. Why? Here what difference of common heating<br>
and floor heating?<br><br>Many thanks!<br><br>Br.<br><br>wang<br>在 2011年1月5日 下午7:55,王洋 <<a href="mailto:wanghongyang1767@gmail.com" target="_blank">wanghongyang1767@gmail.com</a>>写道:<br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Dear all,<br><br> Happy new year!<br><br> I have a question about calculating total heating demand:<br><br>
There is one same room to keep indoor temperature as 20°C one day 24 hours,<br>the initial indoor temperature is 20°C, there is no infiltration no other<br>internal gains in the room. I used 3 different methods to calculate total<br>
heating demand of one day, separately.<br><br>1.First is heating in TRNBuild: after using the INTEGRATOR TYPE 46, the<br>QHEAT is about 34314 kJ.<br><br>2.Second is floor heating(active layer): after using the INTEGRATOR TYPE<br>
46, the QALFL_Inlet is about 33680.7kJ.<br><br>3.Third is still floor heating(active layer): after using the INTEGRATOR<br>TYPE 46, but I used Q=CwaterMwater(Tinlet-Toutlet), the result of Q is<br>144639kJ.<br><br>My question is: 1) To 2 and 3: Why is the difference is so large? 3 is<br>
almost 4 times than 3? I will get the total heating demand, which one is<br>right? Why? What's different of both of them?<br><br>2) If 3 is right. Generally, the floor heating should be more energy-saving<br>than common heating. But here result is absolutely opposite. The common<br>
heating is more energy-heating. Why? Here what difference of common heating<br>and floor heating?<br><br>Many thanks!<br><br>Br.<br><br>wang<br><br><br>在 2011年1月5日 下午2:38,王洋 <<a href="mailto:wanghongyang1767@gmail.com" target="_blank">wanghongyang1767@gmail.com</a>>写道:<br>
<br>Dear all,<br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote"> Happy new year!<br><br> I have a question about calculating total heating demand:<br><br>There is one same room to keep indoor temperature as 20°C one day 24<br>
hours, the initial indoor temperature is 20°C, there is no infiltration no<br>other internal gains in the room. I used 3 different methods to calculate<br>total heating demand of one day, separately.<br><br>1.First is heating in TRNBuild: after using the INTEGRATOR TYPE 46, the<br>
QHEAT is about 34314 kJ.<br><br>2.Second is floor heating(active layer): after using the INTEGRATOR TYPE<br>46, the QALFL_Inlet is about 33680.7kJ.<br><br>3.Third is still floor heating(active layer): after using the INTEGRATOR<br>
TYPE 46, but I used Q=CwaterMwater(Tinlet-Toutlet), the result of Q is<br>144639kJ.<br><br>My question is: 1) To 2 and 3: Why is the difference is so large? 3 is<br>almost 4 times than 3? I will get the total heating demand, which one is<br>
right? Why? What's different of both of them?<br><br>2) If 3 is right. Generally, the floor heating should be more<br>energy-saving than common heating. But here result is absolutely opposite.<br>The common heating is more energy-heating. Why? Here what difference of<br>
common heating and floor heating?<br><br>Many thanks!<br><br>Br.<br><br>wang<br><br><br><br>2011/1/4 <<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>><br><br>
<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br> <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>or, via email, send a message with subject or body 'help' to<br>
<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br> <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br><br>Today's Topics:<br><br> 1. optimization problems using trnopt in Windows 7 OS (Dapeng Li)<br>
<br><br>---------- 已转发邮件 ----------<br>From: Dapeng Li <<a href="mailto:jiap1120@gmail.com" target="_blank">jiap1120@gmail.com</a>><br>To: <a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
Date: Tue, 4 Jan 2011 18:00:38 +0100<br>Subject: [TRNSYS-users] optimization problems using trnopt in Windows 7<br>OS<br>Dear all,<br><br>I want to do optimization using trnsys, trnopt and genopt in* Windows 7<br>OS. *But when I run the example in the directory of "C:\Program<br>
Files\Trnsys16_1\Optimization", I got a error message in Genopt interface<br>that is enclosed in the attachment.<br><br>The version I use is listed below: TRNSYS version 16.01.0003, trnopt<br>version 2.1.0.52, genopt version 2.1.0 June 18, 2008.<br>
<br>PS: I ever did optimization in XP OS, and it work well.<br><br>Thanks in advance.<br><br>With kind regards,<br><br>Dapeng Li<br><br><br><br>_______________________________________________<br>TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br><br> <br></blockquote></blockquote></blockquote><br> <br>------------------------------------------------------------------------<br><br>Betreff:<br>Re: [TRNSYS-users] question about wall gain<br>Von:<br>Knut Erik Enerstvedt <<a href="mailto:knut.erik.enerstvedt@gmail.com" target="_blank">knut.erik.enerstvedt@gmail.com</a>><br>
Datum:<br>Fri, 7 Jan 2011 09:18:20 +0100<br>An:<br><a href="mailto:duffy@tess-inc.com" target="_blank">duffy@tess-inc.com</a>, <a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a>, <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>An:<br><a href="mailto:duffy@tess-inc.com" target="_blank">duffy@tess-inc.com</a>, <a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a>, <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br><br>Dear Matt and Salim,<br><br><br>One example of usage for "wall gain" is when you have defined a boundary<br>wall with known boundary temperature, but also want to take into account<br>solar gain from windows on that wall. You can not (at least in TRNSYS 16)<br>
define windows in the normal manner on boundary walls. For example, if you<br>are modelling a zone adjacent to a highly glazed building with known<br>temperature, and a glass wall separates the two. Then you can use "wall<br>
gain" to impose the solar heat flux from the adjacent building on the<br>boundary wall.<br><br><br>Best regards,<br><br>Knut Erik Enerstvedt<br><br><br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Dear Salim,<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">To the best of my knowledge, and according to the documentation, it is<br> <br></blockquote>indeed an energy flux to the inside wall surface. When does one >use this, I<br>
am not exactly sure. Perhaps when there is chimney in a wall with hot<br>exhaust gases that is causing a gain to the zone?<br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Best regards,<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Matt<br> <br></blockquote><br><br><br>*>----- Original Message -----*<br>*>From:* "salim mokraoui" <<a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a>><br>
*>Sent:* Wed, January 5, 2011 9:23<br>*>Subject:* [TRNSYS-users] question about wall gain<br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Dear trnsys users,<br> <br></blockquote><br><br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">In zone window of trnbuild, what does wall gain means actually, is it a<br> <br></blockquote>density flux that we impose at the inside surface of the wall ?<br>
<br><br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Many thanks<br> <br></blockquote><br><br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Salim MOKRAOUI<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Faculté des sciences de Nancy - LERMAB<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">BP 239<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">54506 Vandoeuvre.<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Tél 03 83 68 48 44 - mél <a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a><br>
<br></blockquote><br> <br>------------------------------------------------------------------------<br><br>Betreff:<br>Re: [TRNSYS-users] question about wall gain<br>Von:<br>"salim mokraoui" <<a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a>><br>
Datum:<br>Fri, 7 Jan 2011 10:06:01 +0100<br>An:<br>"'Knut Erik Enerstvedt'" <<a href="mailto:knut.erik.enerstvedt@gmail.com" target="_blank">knut.erik.enerstvedt@gmail.com</a>>, <<a href="mailto:duffy@tess-inc.com" target="_blank">duffy@tess-inc.com</a>>, <<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>
<br>An:<br>"'Knut Erik Enerstvedt'" <<a href="mailto:knut.erik.enerstvedt@gmail.com" target="_blank">knut.erik.enerstvedt@gmail.com</a>>, <<a href="mailto:duffy@tess-inc.com" target="_blank">duffy@tess-inc.com</a>>, <<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>
<br><br>Dear Erik and Matt,<br><br> <br>Thank you very much for your answers. <br>I can understand that this wall gain concerns only a radiative gains, is it<br>right ?<br><br> <br>Best regards<br><br> <br>De : Knut Erik Enerstvedt [mailto:<a href="mailto:knut.erik.enerstvedt@gmail.com" target="_blank">knut.erik.enerstvedt@gmail.com</a>] Envoyé : vendredi 7 janvier 2011 09:18<br>
À : <a href="mailto:duffy@tess-inc.com" target="_blank">duffy@tess-inc.com</a>; <a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a>;<br><a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Objet : Re: [TRNSYS-users] question about wall gain<br><br> <br>Dear Matt and Salim,<br><br> <br>One example of usage for "wall gain" is when you have defined a boundary<br>wall with known boundary temperature, but also want to take into account<br>
solar gain from windows on that wall. You can not (at least in TRNSYS 16)<br>define windows in the normal manner on boundary walls. For example, if you<br>are modelling a zone adjacent to a highly glazed building with known<br>
temperature, and a glass wall separates the two. Then you can use "wall<br>gain" to impose the solar heat flux from the adjacent building on the<br>boundary wall.<br><br> <br>Best regards,<br><br>Knut Erik Enerstvedt<br>
<br> <br> <br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Dear Salim,<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">To the best of my knowledge, and according to the documentation, it is<br> <br></blockquote>indeed an energy flux to the inside wall surface. When does one >use this, I<br>
am not exactly sure. Perhaps when there is chimney in a wall with hot<br>exhaust gases that is causing a gain to the zone?<br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Best regards,<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Matt<br> <br></blockquote><br><br><br><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">----- Original Message -----<br>From: "salim mokraoui" <<a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a>> Sent: Wed, January 5, 2011 9:23<br>
Subject: [TRNSYS-users] question about wall gain<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Dear trnsys users,<br> <br></blockquote><br> <br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">In zone window of trnbuild, what does wall gain means actually, is it a<br> <br></blockquote>density flux that we impose at the inside surface of the wall ?<br>
<br> <br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Many thanks<br> <br></blockquote><br> <br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Salim MOKRAOUI<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Faculté des sciences de Nancy - LERMAB<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">BP 239<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">54506 Vandoeuvre.<br> <br></blockquote><br> <br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Tél 03 83 68 48 44 - mél <a href="mailto:salim.mokraoui@lermab.uhp-nancy.fr" target="_blank">salim.mokraoui@lermab.uhp-nancy.fr</a><br>
<br></blockquote><br><br> ------------------------------------------------------------------------<br><br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br> <br></blockquote><br>-- <br>_________________________________________________<br><br>
Dipl.-Ing. (FH) Jochen Döll<br>Dept. Thermal Systems and Buildings<br><br>Fraunhofer-Institut für Solare Energiesysteme ISE<br>Heidenhofstrasse 2, 79110 Freiburg, Germany<br><br>Phone: +49 (761) 4588-5468<br>Fax: +49 (761) 4588-9000<br>
Mail: <a href="mailto:jochen.doell@ise.fraunhofer.de" target="_blank">jochen.doell@ise.fraunhofer.de</a><br>Web: <a href="http://www.ise.fraunhofer.de/" target="_blank">www.ise.fraunhofer.de</a><br>_________________________________________________<br>
<br><br><br><br>---------- 已转发邮件 ----------<br>From: Andrey Vyshnepolsky <<a href="mailto:Andrey.Vyshnepolsky@rwth-aachen.de">Andrey.Vyshnepolsky@rwth-aachen.de</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Thu, 06 Jan 2011 15:17:53 -0200<br>Subject: [TRNSYS-users] Type 927 (Water to Water Heat Pump)<br>Hello,<br><br>I am simulating a DHW-System where the heat is provided by a flat plate solar collector. Between the collector circle and the water tank circle I have put in a water-to-water heat pump (Type 927). The main idea behind this is to replace the auxiliary heater of the water tank. Sadly the heat pump doesn’t work right:<br>
<br>The plotter shows a value of nearly zero for the gain heat of the collector and the heat transfer to the load circle of the heat pump is lower than the supplied power to the pump. But for me the heat pump shall follow this equation: Heat_source (=Heat_coll) + Power_pump = Heat_load.<br>
<br>A further question is: is it allowed to change the temprature and mass flow values in the performance data files of the heat pump?<br><br>For a better understanding I have attached the working file.<br><br>Thank you very much for any kind of help in advance.<br>
<br>With best regards,<br><br>Andrey<br><br><br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>