<div> Dear all,<br><br>     I have a question about room air temperature: NTYPE 1: TAIR. 
As we know, there are different room air temperature in different height
 of one room. Besides that,  the wall, the floor and roof temperature of
 the room are also not the same. Please tell me  what's meaning of NTYPE
 1: TAIR? Where is This AIRNODE? How to define This AIRNODE?</div>


<div> </div>

<div> PLUS: to Operative(operation) temperature of room:  How to define it?  What' meaning is  Operative(operation)temperature of room? What's difference of Operative(operation) temperature of room and  NTYPE 1: TAIR?</div>

  <br> <br><br> I saw the TRNBuild / Type56 documentation . But it only shows NTYPE 1: 
TAIR: air temperature of zone. But I want to know   Where is This 
AIRNODE which measures aie temperature of zone? How to define This 
AIRNODE? Because as we know, there are different room air temperature in
 different height of one room.<br>
 <br>       <br> to Top it shows the operative(operation) 
temperature of room: BUT how to define it?  What' meaning is  
Operative(operation)<div class="im">temperature of room? What's difference of Operative(operation) temperature of room and  NTYPE 1: TAIR?<br>
 <br>  Many thanks!<br> <br>    Br.<br> <br>wang</div><br><br><div class="gmail_quote">2010/12/17  <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">Send TRNSYS-users mailing list submissions to<br>
        <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br>
<br>
   1. Re: Create a final report with TrnEdit (David BRADLEY)<br>
   2. Re: zone air temperature (NTYPE 1: TAIR) (David BRADLEY)<br>
<br><br>---------- 已转发邮件 ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>To: Manu <<a href="mailto:manuel.tilly@gmail.com">manuel.tilly@gmail.com</a>><br>
Date: Fri, 17 Dec 2010 10:21:46 -0600<br>Subject: Re: [TRNSYS-users] Create a final report with TrnEdit<br>

  
    
  
  <div text="#000000" bgcolor="#ffffff">
    Manu,<br>
      TRNEdit is a tool that allows you to directly edit the text of the
    TRNSYS input file. Before the Studio existed, people used TRNEdit to
    create their input file. It doesn't really have any reporting
    features. You might try selecting "Report" from the File menu in the
    TRNSYS Studio. This will generate a summary text file of your
    project.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    On 12/14/2010 07:29, Manu wrote:
    <blockquote type="cite">Hi,<br>
      <br>
      I try to use TrnEdit on a project and I want to know if it's
      possible to generate a final report (Word or pdf extension file)
      withe graphic and text comment, juste like SimSol (french
      application based on TRNSys to dimention a solar system).<br>
      <br>
      Thank you<br>
      <br>
      Best regards<br>
      <br clear="all">
      <br>
      <br>
      <pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

<br><br>---------- 已转发邮件 ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>To: 王洋 <<a href="mailto:wanghongyang1767@gmail.com">wanghongyang1767@gmail.com</a>><br>
Date: Fri, 17 Dec 2010 11:21:12 -0600<br>Subject: Re: [TRNSYS-users] zone air temperature (NTYPE 1: TAIR)<br>

  
    
  
  <div text="#000000" bgcolor="#ffffff">
    Wang,<br>
      Information of this kind can be found in the TRNBuild / Type56
    documentation (volume 05 in the Trnsys17 documentation set).<br>
    Kind Regards,<br>
     David<br>
    <br>
    On 12/17/2010 07:22, 王洋 wrote:
    <blockquote type="cite">
      <div><br>
        Dear all,</div>
      <div> </div>
      <div>     I have a question about room air temperature: NTYPE 1:
        TAIR. As we know, there are different room air temperature in
        different height of one room. Besides that,  the wall, the floor
        and roof temperature of the room are also not the same. Please
        tell me  what's meaning of NTYPE 1: TAIR? Where is This AIRNODE?
        How to define This AIRNODE?</div>
      <div> </div>
      <div> PLUS: to Operative(operation) temperature of room:  How to
        define it?  What' meaning is  Operative(operation)temperature of
        room? What's difference of Operative(operation) temperature of
        room and  NTYPE 1: TAIR?</div>
      <div> </div>
      <div> </div>
      <div>Many thanks!</div>
      <div> </div>
      <div>Br.</div>
      <div> </div>
      <div>wang</div>
      <div> </div>
      <div> </div>
      <div> </div>
      <div class="gmail_quote">2010/12/17 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
        <blockquote style="border-left: 1px solid rgb(204, 204, 204); margin: 0px 0px 0px 0.8ex; padding-left: 1ex;" class="gmail_quote">Send TRNSYS-users mailing list submissions
          to<br>
                 <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
          <br>
          To subscribe or unsubscribe via the World Wide Web, visit<br>
                 <a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
          or, via email, send a message with subject or body 'help' to<br>
                 <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
          <br>
          You can reach the person managing the list at<br>
                 <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
          <br>
          When replying, please edit your Subject line so it is more
          specific<br>
          than "Re: Contents of TRNSYS-users digest..."<br>
          <br>
          Today's Topics:<br>
          <br>
            1. Re: Type 56 (David BRADLEY)<br>
            2. Re: Psychrometrics (David BRADLEY)<br>
            3. Re : Re:  Psychrometrics (Jérôme Deroche)<br>
            4. error when opening sketchup (Annie Marston)<br>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>><br>
          To: Abduljalil Ali Al-Abidi <<a href="mailto:abo_anas4@yahoo.com" target="_blank">abo_anas4@yahoo.com</a>><br>
          Date: Thu, 16 Dec 2010 12:47:43 -0600<br>
          Subject: Re: [TRNSYS-users] Type 56<br>
          <div bgcolor="#ffffff" text="#000000">Abduljalil,<br>
              In order to change the wall layers, open TRNBuild and open
            your building description file (*.bui or *.b17). Select
            Typemanager: Walls from the menus at the top of the screen.
            Select the appropriate wall from the drop-down list. Double
            click on a layer in order to change its thickness.<br>
            Best,<br>
             David<br>
            <br>
            <br>
            On 12/16/2010 03:26, Abduljalil Ali Al-Abidi wrote:
            <blockquote type="cite">
              <div style="font-family: arial,helvetica,sans-serif; font-size: 14pt;">
                <div>Dear Trnsys user <br>
                  I am a new trnsys user and I want to change the
                  thickness of the wall insulation in the tape 56 (
                  multi-zone building ). Is it possible to change this
                  thickness in this type ex. for insulation = 5 cm to 20
                  cm step 5cm.<br>
                  I would like to study the effect of insulation thick
                  to the performance of the system<br>
                  best regards<br>
                </div>
              </div>
              <br>
              <pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
            </blockquote>
            <br>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>><br>
          To: "Jérôme Deroche" <<a href="mailto:deroche.jerome@cedre-sophia.com" target="_blank">deroche.jerome@cedre-sophia.com</a>><br>
          Date: Thu, 16 Dec 2010 12:50:55 -0600<br>
          Subject: Re: [TRNSYS-users] Psychrometrics<br>
          <div bgcolor="#ffffff" text="#000000">Jérôme,<br>
              What is most likely happening is that at a pressure of
            1atm, your combination of the dry bulb temperature and the
            absolute humidity ratio are on the wrong side of the
            saturation line. Since that is physically impossible, the
            psychometric routine  keeps your dry bulb temperature and
            resets the absolute humidity ratio to the value it would be
            if the relative humidity were 100%.<br>
            Best,<br>
             David<br>
            <br>
            <br>
            On 12/16/2010 04:21,  wrote:
            <blockquote type="cite"><font size="2"><font size="3"><span style="color: rgb(0, 0, 0);"><span style="font-family: Arial;">Hello,<br>
                      i'm using a psychrometrics type with dry bulb
                      temperature and absolute humidity ratio in inputs.
                      Pressure input is set to 1 atm.<br>
                      <br>
                      I have noticed that sometimes there is a
                      difference between the input humidity ratio and
                      the output humidity ratio. The difference ratio is
                      about 1 to 12%.<br>
                      <br>
                      Could someone explain to me why this difference
                      happens?<br>
                      <br>
                      Thank you <br>
                    </span></span></font></font>
              <div style="background-color: white;"><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"></span><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="2"><br>

                          Jérôme DEROCHE<br>
                          Ingénieur d'études<br>
                          <br>
                        </font></span></span></font></span><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="5">CEDRE</font></span></span></font></span><br>

                <br>
                <span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="2">Tel: 04 92
                          96 03 77<br>
                          Port: 06 25 11 21 93<br>
                          Ophira 1, 1 place Bermond<br>
                          06560 SOPHIA-ANTIPOLIS<br>
                        </font></span></span></font></span><br>
              </div>
              <pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
            </blockquote>
            <br>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: "Jérôme Deroche" <<a href="mailto:deroche.jerome@cedre-sophia.com" target="_blank">deroche.jerome@cedre-sophia.com</a>><br>
          To: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>><br>
          Date: Fri, 17 Dec 2010 05:08:17 -0500 (EST)<br>
          Subject: [TRNSYS-users] Re : Re: Psychrometrics<br>
          <div bgcolor="#ffffff"><font size="2"><font color="#000000" face="Arial" size="3">Your answers are right.<br>
                Thank you very much<br>
                <br>
                <br>
              </font></font>
            <div>
              <div style="background-color: white;"><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"></span><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="2"><br>

                          Jérôme DEROCHE<br>
                          Ingénieur d'études<br>
                          <br>
                        </font></span></span></font></span><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="5">CEDRE</font></span></span></font></span><br>

                <br>
                <span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="2">Tel: 04 92
                          96 03 77<br>
                          Port: 06 25 11 21 93<br>
                          Ophira 1, 1 place Bermond<br>
                          06560 SOPHIA-ANTIPOLIS<br>
                        </font></span></span></font></span><br>
              </div>
              <br>
              <h1 style="padding-bottom: 3px; background-color: rgb(238, 238, 238); font-family: arial,helvetica; margin-bottom: 1px; color: black; font-size: 10pt; font-weight: bold; padding-top: 3px;">Message original Re : Re:
                [TRNSYS-users] Psychrometrics</h1>
              <font style="background-color: white; font-family: arial,helvetica; color: black; font-size: 10pt;"><b>De : </b>David
                BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>><br>
                <b>A : </b>Jérôme Deroche <<a href="mailto:deroche.jerome@cedre-sophia.com" target="_blank">deroche.jerome@cedre-sophia.com</a>><br>
                <b>Date</b> : 2010-12-16 19:51:05</font><br>
              <br>
            </div>
            Jérôme,<br>
              What is most likely happening is that at a pressure of
            1atm, your combination of the dry bulb temperature and the
            absolute humidity ratio are on the wrong side of the
            saturation line. Since that is physically impossible, the
            psychometric routine  keeps your dry bulb temperature and
            resets the absolute humidity ratio to the value it would be
            if the relative humidity were 100%.<br>
            Best,<br>
             David<br>
            <br>
            <br>
            On 12/16/2010 04:21,  wrote:
            <blockquote type="cite"><font size="2"><font size="3"><span style="color: rgb(0, 0, 0);"><span style="font-family: Arial;">Hello,<br>
                      i'm using a psychrometrics type with dry bulb
                      temperature and absolute humidity ratio in inputs.
                      Pressure input is set to 1 atm.<br>
                      <br>
                      I have noticed that sometimes there is a
                      difference between the input humidity ratio and
                      the output humidity ratio. The difference ratio is
                      about 1 to 12%.<br>
                      <br>
                      Could someone explain to me why this difference
                      happens?<br>
                      <br>
                      Thank you <br>
                    </span></span></font></font>
              <div style="background-color: white;"><span style="line-height: 150%; font-size: 11pt;"></span><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="2"><br>

                          Jérôme DEROCHE<br>
                          Ingénieur d'études<br>
                          <br>
                        </font></span></span></font></span><span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="5">CEDRE</font></span></span></font></span><br>

                <br>
                <span style="line-height: 150%; font-family: 'Times New Roman'; font-size: 11pt;"><font style="color: rgb(65, 105, 225);" size="4"><span style="font-family: Arial; font-weight: bold;"><span style="color: rgb(100, 149, 237);"><font size="2">Tel: 04 92
                          96 03 77<br>
                          Port: 06 25 11 21 93<br>
                          Ophira 1, 1 place Bermond<br>
                          06560 SOPHIA-ANTIPOLIS<br>
                        </font></span></span></font></span><br>
              </div>
              <pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
            </blockquote>
            <br>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: Annie Marston <<a href="mailto:A.Marston@eb-engineers.com" target="_blank">A.Marston@eb-engineers.com</a>><br>
          To: "<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>"
          <<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>
          Date: Thu, 16 Dec 2010 14:30:35 +0000<br>
          Subject: [TRNSYS-users] error when opening sketchup<br>
          <div vlink="purple" link="blue" lang="EN-US">
            <div>
              <p class="MsoNormal">Hi,</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">I am using the TRNSYS 3d plugin for
                SketchUp V7. I have v8 but the plugin doesn’t seem to
                attach to v8 (is this correct? Is there a plugin for
                v8). Whenever I open sketch up I get the following
                error:</p>
              <p class="MsoNormal">Sorry… the plugin has encountered an
                error. This error may cause unpredictable behavior in
                the plugin continue this session with caution! It would
                probably be a good idea to exit SketchUp  and start
                again. (unfortunately this happens everytime I open
                sketchup)</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">For help please contact…</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">Error:</p>
              <p class="MsoNormal">NameError</p>
              <p class="MsoNormal">Wrong constant name jectinfoInterface</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">Backtrace:</p>
              <p class="MsoNormal">C:/Program Files (x86)/Google/Google
                SketchUp 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in
                `const_get'</p>
              <p class="MsoNormal">C:/Program Files (x86)/Google/Google
                SketchUp 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in
                `restore_state'</p>
              <p class="MsoNormal">C:/Program Files (x86)/Google/Google
                SketchUp 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in
                `initialize'</p>
              <p class="MsoNormal">C:/Program Files (x86)/Google/Google
                SketchUp 7/Plugins/Trnsys3d/lib/AsynchProc.rb:13:in
                `call'</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">My version of the plugin is 1.0.5.362</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">Can you help</p>
              <p class="MsoNormal"> </p>
              <p class="MsoNormal">Thanks</p>
              <p class="MsoNormal">Annie</p>
              <p class="MsoNormal"> </p>
              <p style="margin-bottom: 5pt; margin-left: 0in; margin-right: 0in;" class="MsoNormal"><b><span style="color: navy;">Dr. A. Marston, Ph.D. LEED® AP</span></b></p>
              <p style="margin-bottom: 5pt; margin-left: 0in; margin-right: 0in;" class="MsoNormal"><b><span style="color: navy; font-size: 10pt;">Building
                    Performance Analyst</span></b></p>
              <p style="margin-bottom: 5pt; margin-left: 0in; margin-right: 0in;" class="MsoNormal"><span style="color: navy; font-size: 10pt;"> </span></p>
              <p class="MsoNormal"><b><span style="color: navy; font-size: 10pt;">Ebert & Baumann Consulting
                    Engineers, Inc.</span></b><span style="color: navy; font-size: 12pt;"></span></p>
              <p class="MsoNormal"><b><span style="letter-spacing: 2.6pt; color: rgb(153, 153, 153); font-size: 10pt;">An 
                    Enterprise  of  the  Ebert-Consulting Group</span></b><b><span style="letter-spacing: 2.6pt; color: rgb(153, 153, 153); font-size: 10pt;"></span></b></p>
              <p class="MsoNormal"><span style="color: navy; font-size: 5pt;"> </span></p>
              <p class="MsoNormal"><span style="font-size: 10pt;">734 15<sup>th</sup>
                  Street, NW </span></p>
              <p class="MsoNormal"><span style="font-size: 10pt;">Suite
                  1000</span></p>
              <p style="margin-bottom: 6pt;" class="MsoNormal"><span style="font-size: 10pt;">Washington, D.C. 20005, USA</span></p>
              <p class="MsoNormal"><b><span style="color: navy; font-size: 10pt;">Tel          +1.202.608.1334</span></b><b><span style="color: navy;"></span></b></p>
              <p class="MsoNormal"><b><span style="color: navy; font-size: 10pt;">Fax         +1.202.544.1434</span></b></p>
              <p class="MsoNormal"><b><span style="color: navy; font-size: 10pt;"> </span></b></p>
              <p class="MsoNormal"><b><span style="color: navy; font-size: 10pt;"><a title="blocked::mailto:o.baumann@eb-engineers.com" href="mailto:a.marston@eb-engineers.com" target="_blank"><span style="color: navy; text-decoration: none;">a.marston@eb-engineers.com</span></a></span></b></p>

              <p class="MsoNormal"> </p>
            </div>
          </div>
          <br>
          _______________________________________________<br>
          TRNSYS-users mailing list<br>
          <a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
          <a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
<br></blockquote></div><br>