Wang,<br>
Information of this kind can be found in the TRNBuild / Type56
documentation (volume 05 in the Trnsys17 documentation set).<br>
Kind Regards,<br>
David<br>
<br>
On 12/17/2010 07:22, 王洋 wrote:
<blockquote
cite="mid:AANLkTikGZ57H4weJic6qJmohz1yvfLOb0dT6qGrMwSDM@mail.gmail.com"
type="cite">
<div><br>
Dear all,</div>
<div> </div>
<div> I have a question about room air temperature: NTYPE 1:
TAIR. As we know, there are different room air temperature in
different height of one room. Besides that, the wall, the floor
and roof temperature of the room are also not the same. Please
tell me what's meaning of NTYPE 1: TAIR? Where is This AIRNODE?
How to define This AIRNODE?</div>
<div> </div>
<div> PLUS: to Operative(operation) temperature of room: How to
define it? What' meaning is Operative(operation)temperature of
room? What's difference of Operative(operation) temperature of
room and NTYPE 1: TAIR?</div>
<div> </div>
<div> </div>
<div>Many thanks!</div>
<div> </div>
<div>Br.</div>
<div> </div>
<div>wang</div>
<div> </div>
<div> </div>
<div> </div>
<div class="gmail_quote">2010/12/17 <span dir="ltr"><<a
moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="border-left: 1px solid rgb(204, 204, 204);
margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
class="gmail_quote">Send TRNSYS-users mailing list submissions
to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
<a moz-do-not-send="true"
href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more
specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>
Today's Topics:<br>
<br>
1. Re: Type 56 (David BRADLEY)<br>
2. Re: Psychrometrics (David BRADLEY)<br>
3. Re : Re: Psychrometrics (Jérôme Deroche)<br>
4. error when opening sketchup (Annie Marston)<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: David BRADLEY <<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
To: Abduljalil Ali Al-Abidi <<a moz-do-not-send="true"
href="mailto:abo_anas4@yahoo.com">abo_anas4@yahoo.com</a>><br>
Date: Thu, 16 Dec 2010 12:47:43 -0600<br>
Subject: Re: [TRNSYS-users] Type 56<br>
<div bgcolor="#ffffff" text="#000000">Abduljalil,<br>
In order to change the wall layers, open TRNBuild and open
your building description file (*.bui or *.b17). Select
Typemanager: Walls from the menus at the top of the screen.
Select the appropriate wall from the drop-down list. Double
click on a layer in order to change its thickness.<br>
Best,<br>
David<br>
<br>
<br>
On 12/16/2010 03:26, Abduljalil Ali Al-Abidi wrote:
<blockquote type="cite">
<div style="font-family: arial,helvetica,sans-serif;
font-size: 14pt;">
<div>Dear Trnsys user <br>
I am a new trnsys user and I want to change the
thickness of the wall insulation in the tape 56 (
multi-zone building ). Is it possible to change this
thickness in this type ex. for insulation = 5 cm to 20
cm step 5cm.<br>
I would like to study the effect of insulation thick
to the performance of the system<br>
best regards<br>
</div>
</div>
<br>
<pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: David BRADLEY <<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
To: "Jérôme Deroche" <<a moz-do-not-send="true"
href="mailto:deroche.jerome@cedre-sophia.com">deroche.jerome@cedre-sophia.com</a>><br>
Date: Thu, 16 Dec 2010 12:50:55 -0600<br>
Subject: Re: [TRNSYS-users] Psychrometrics<br>
<div bgcolor="#ffffff" text="#000000">Jérôme,<br>
What is most likely happening is that at a pressure of
1atm, your combination of the dry bulb temperature and the
absolute humidity ratio are on the wrong side of the
saturation line. Since that is physically impossible, the
psychometric routine keeps your dry bulb temperature and
resets the absolute humidity ratio to the value it would be
if the relative humidity were 100%.<br>
Best,<br>
David<br>
<br>
<br>
On 12/16/2010 04:21, wrote:
<blockquote type="cite"><font size="2"><font size="3"><span
style="color: rgb(0, 0, 0);"><span
style="font-family: Arial;">Hello,<br>
i'm using a psychrometrics type with dry bulb
temperature and absolute humidity ratio in inputs.
Pressure input is set to 1 atm.<br>
<br>
I have noticed that sometimes there is a
difference between the input humidity ratio and
the output humidity ratio. The difference ratio is
about 1 to 12%.<br>
<br>
Could someone explain to me why this difference
happens?<br>
<br>
Thank you <br>
</span></span></font></font>
<div style="background-color: white;"><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"></span><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="2"><br>
Jérôme DEROCHE<br>
Ingénieur d'études<br>
<br>
</font></span></span></font></span><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="5">CEDRE</font></span></span></font></span><br>
<br>
<span style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="2">Tel: 04 92
96 03 77<br>
Port: 06 25 11 21 93<br>
Ophira 1, 1 place Bermond<br>
06560 SOPHIA-ANTIPOLIS<br>
</font></span></span></font></span><br>
</div>
<pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "Jérôme Deroche" <<a moz-do-not-send="true"
href="mailto:deroche.jerome@cedre-sophia.com">deroche.jerome@cedre-sophia.com</a>><br>
To: David BRADLEY <<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
Date: Fri, 17 Dec 2010 05:08:17 -0500 (EST)<br>
Subject: [TRNSYS-users] Re : Re: Psychrometrics<br>
<div bgcolor="#ffffff"><font size="2"><font color="#000000"
face="Arial" size="3">Your answers are right.<br>
Thank you very much<br>
<br>
<br>
</font></font>
<div>
<div style="background-color: white;"><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"></span><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="2"><br>
Jérôme DEROCHE<br>
Ingénieur d'études<br>
<br>
</font></span></span></font></span><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="5">CEDRE</font></span></span></font></span><br>
<br>
<span style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="2">Tel: 04 92
96 03 77<br>
Port: 06 25 11 21 93<br>
Ophira 1, 1 place Bermond<br>
06560 SOPHIA-ANTIPOLIS<br>
</font></span></span></font></span><br>
</div>
<br>
<h1 style="padding-bottom: 3px; background-color: rgb(238,
238, 238); font-family: arial,helvetica; margin-bottom:
1px; color: black; font-size: 10pt; font-weight: bold;
padding-top: 3px;">Message original Re : Re:
[TRNSYS-users] Psychrometrics</h1>
<font style="background-color: white; font-family:
arial,helvetica; color: black; font-size: 10pt;"><b>De : </b>David
BRADLEY <<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>><br>
<b>A : </b>Jérôme Deroche <<a moz-do-not-send="true"
href="mailto:deroche.jerome@cedre-sophia.com"
target="_blank">deroche.jerome@cedre-sophia.com</a>><br>
<b>Date</b> : 2010-12-16 19:51:05</font><br>
<br>
</div>
Jérôme,<br>
What is most likely happening is that at a pressure of
1atm, your combination of the dry bulb temperature and the
absolute humidity ratio are on the wrong side of the
saturation line. Since that is physically impossible, the
psychometric routine keeps your dry bulb temperature and
resets the absolute humidity ratio to the value it would be
if the relative humidity were 100%.<br>
Best,<br>
David<br>
<br>
<br>
On 12/16/2010 04:21, wrote:
<blockquote type="cite"><font size="2"><font size="3"><span
style="color: rgb(0, 0, 0);"><span
style="font-family: Arial;">Hello,<br>
i'm using a psychrometrics type with dry bulb
temperature and absolute humidity ratio in inputs.
Pressure input is set to 1 atm.<br>
<br>
I have noticed that sometimes there is a
difference between the input humidity ratio and
the output humidity ratio. The difference ratio is
about 1 to 12%.<br>
<br>
Could someone explain to me why this difference
happens?<br>
<br>
Thank you <br>
</span></span></font></font>
<div style="background-color: white;"><span
style="line-height: 150%; font-size: 11pt;"></span><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="2"><br>
Jérôme DEROCHE<br>
Ingénieur d'études<br>
<br>
</font></span></span></font></span><span
style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="5">CEDRE</font></span></span></font></span><br>
<br>
<span style="line-height: 150%; font-family: 'Times New
Roman'; font-size: 11pt;"><font style="color: rgb(65,
105, 225);" size="4"><span style="font-family:
Arial; font-weight: bold;"><span style="color:
rgb(100, 149, 237);"><font size="2">Tel: 04 92
96 03 77<br>
Port: 06 25 11 21 93<br>
Ophira 1, 1 place Bermond<br>
06560 SOPHIA-ANTIPOLIS<br>
</font></span></span></font></span><br>
</div>
<pre><fieldset></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: Annie Marston <<a moz-do-not-send="true"
href="mailto:A.Marston@eb-engineers.com">A.Marston@eb-engineers.com</a>><br>
To: "<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>"
<<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Thu, 16 Dec 2010 14:30:35 +0000<br>
Subject: [TRNSYS-users] error when opening sketchup<br>
<div vlink="purple" link="blue" lang="EN-US">
<div>
<p class="MsoNormal">Hi,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I am using the TRNSYS 3d plugin for
SketchUp V7. I have v8 but the plugin doesn’t seem to
attach to v8 (is this correct? Is there a plugin for
v8). Whenever I open sketch up I get the following
error:</p>
<p class="MsoNormal">Sorry… the plugin has encountered an
error. This error may cause unpredictable behavior in
the plugin continue this session with caution! It would
probably be a good idea to exit SketchUp and start
again. (unfortunately this happens everytime I open
sketchup)</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">For help please contact…</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Error:</p>
<p class="MsoNormal">NameError</p>
<p class="MsoNormal">Wrong constant name jectinfoInterface</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Backtrace:</p>
<p class="MsoNormal">C:/Program Files (x86)/Google/Google
SketchUp 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in
`const_get'</p>
<p class="MsoNormal">C:/Program Files (x86)/Google/Google
SketchUp 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in
`restore_state'</p>
<p class="MsoNormal">C:/Program Files (x86)/Google/Google
SketchUp 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in
`initialize'</p>
<p class="MsoNormal">C:/Program Files (x86)/Google/Google
SketchUp 7/Plugins/Trnsys3d/lib/AsynchProc.rb:13:in
`call'</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">My version of the plugin is 1.0.5.362</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Can you help</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Thanks</p>
<p class="MsoNormal">Annie</p>
<p class="MsoNormal"> </p>
<p style="margin-bottom: 5pt; margin-left: 0in;
margin-right: 0in;" class="MsoNormal"><b><span
style="color: navy;">Dr. A. Marston, Ph.D. LEED® AP</span></b></p>
<p style="margin-bottom: 5pt; margin-left: 0in;
margin-right: 0in;" class="MsoNormal"><b><span
style="color: navy; font-size: 10pt;">Building
Performance Analyst</span></b></p>
<p style="margin-bottom: 5pt; margin-left: 0in;
margin-right: 0in;" class="MsoNormal"><span
style="color: navy; font-size: 10pt;"> </span></p>
<p class="MsoNormal"><b><span style="color: navy;
font-size: 10pt;">Ebert & Baumann Consulting
Engineers, Inc.</span></b><span style="color: navy;
font-size: 12pt;"></span></p>
<p class="MsoNormal"><b><span style="letter-spacing:
2.6pt; color: rgb(153, 153, 153); font-size: 10pt;">An
Enterprise of the Ebert-Consulting Group</span></b><b><span
style="letter-spacing: 2.6pt; color: rgb(153, 153,
153); font-size: 10pt;"></span></b></p>
<p class="MsoNormal"><span style="color: navy; font-size:
5pt;"> </span></p>
<p class="MsoNormal"><span style="font-size: 10pt;">734 15<sup>th</sup>
Street, NW </span></p>
<p class="MsoNormal"><span style="font-size: 10pt;">Suite
1000</span></p>
<p style="margin-bottom: 6pt;" class="MsoNormal"><span
style="font-size: 10pt;">Washington, D.C. 20005, USA</span></p>
<p class="MsoNormal"><b><span style="color: navy;
font-size: 10pt;">Tel +1.202.608.1334</span></b><b><span
style="color: navy;"></span></b></p>
<p class="MsoNormal"><b><span style="color: navy;
font-size: 10pt;">Fax +1.202.544.1434</span></b></p>
<p class="MsoNormal"><b><span style="color: navy;
font-size: 10pt;"> </span></b></p>
<p class="MsoNormal"><b><span style="color: navy;
font-size: 10pt;"><a moz-do-not-send="true"
title="blocked::mailto:o.baumann@eb-engineers.com"
href="mailto:a.marston@eb-engineers.com"
target="_blank"><span style="color: navy;
text-decoration: none;">a.marston@eb-engineers.com</span></a></span></b></p>
<p class="MsoNormal"> </p>
</div>
</div>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
<br>
</blockquote>
</div>
<br>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>