Dear all,<br><br>I have some questons to ask:<br><br>To B4_QBAL: 1. the sum of B4_QBAL is closed to 0 in one day or at any time?<br><br> 2.
But my B4_QBAL isn't closed to 0 at any time and all one day. Please
see the first ATTACHED. Do you mean if not closed to 0, I can set
Control Cards-> Tolerance Convergence as lower? But I set it as
0.001, B4_QBAL still like the ATTACHED not closed to 0. Please tell me
how to make it?<br>
<br>To CO2%: Why there are different CO2% in one same zone only using
Ideal Heating or only using Floor Heating when all the other parameters
are the same such as the same windows sizes and opening factor and so
on? Please see the two results of CO2% ( the second and third ATTACHED)<br>
<br>To Ideal Heating in TRNBuild: 1. Which type it is? Radiator or Air-conditioning or both of them or others?<br><br>2. Wheather the ideal heating's total heat demand is larger than the Floor heating under the same conditons or not?<br>
<br>3. When only using Heating in TRNBuild, can I only compute the sum
of QHEAT as the total heating energy demand in one zone? Or other way to
compute?<br><br>To QALFL(NTYPE 59): I used winter data and heated up
the floor heating, but the sum of QALFL is minus, is it right? Please
explain in detail.<br>
<br>To the internal Gains: The indoor set-point temperature is 21°C in
one zone, but the actual temperature controlled by PID controller is
higher than 21°C when plus internal Gains in TRNBuild such as Person and
Computers. How to deal with this problem? And why the PID controller
doesn't work at this time?<br>
<br>Many thanks!<br><br>Br.<br><br>wang<br><br><div class="gmail_quote">2010/12/8 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
Send TRNSYS-users mailing list submissions to<br>
<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br>
<br>
1. gbXML (Kersken, Matthias)<br>
2. Re: gbXML (keilholz, werner)<br>
<br><br>---------- 已转发邮件 ----------<br>From: "Kersken, Matthias" <<a href="mailto:Matthias.Kersken@ibp.fraunhofer.de">Matthias.Kersken@ibp.fraunhofer.de</a>><br>To: <<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Wed, 8 Dec 2010 13:36:17 +0100<br>Subject: [TRNSYS-users] gbXML<br>
<div>
<div><span><font face="Arial" size="2">Dear <span>TRNSYS </span>users!</font></span></div>
<div><span><font face="Arial" size="2"></font></span> </div>
<div><span><font face="Arial" size="2">Does anyone
of You know any possibility to get a gbXML-file into <span>TRNSYS</span>?</font></span></div>
<div><span><font face="Arial" size="2">(Non commercial
solution would be preferred).</font></span></div>
<div><span><font face="Arial" size="2"></font></span> </div>
<div><span><font face="Arial" size="2">Thank You for
Your help!</font></span></div>
<div><span><font face="Arial" size="2"></font></span> </div>
<div><span><font face="Arial" size="2">With kind
regards,</font></span></div>
<div><span> <font face="Arial" size="2">Matthias Kersken</font></span></div>
<div><font face="Arial" size="2"></font> </div>
<div> </div>
<div>
<p class="MsoNormal"><span style="font-family: Arial; font-size: 10pt;">---</span></p>
<p class="MsoNormal"> </p>
<table align="left" border="0" cellpadding="0">
<tbody>
<tr style="min-height: 150.5pt;">
<td style="padding: 0.75pt; width: 87.75pt; min-height: 150.5pt;" valign="top" width="117">
<div>
<table style="border: medium none; width: 262.5pt; border-collapse: collapse; background: none repeat scroll 0% 0% silver; margin-left: 4.8pt; margin-right: 4.8pt;" width="350" align="left" border="1" cellpadding="0" cellspacing="0">
<tbody>
<tr>
<td style="border: 1pt solid windowtext; padding: 3pt; background: none repeat scroll 0% 0% white;">
<p style="margin: 0cm 0cm 4.5pt;"><b><span style="font-family: Arial; font-size: 10pt;">Dipl.-Ing. Matthias
Kersken<br></span></b><span style="font-family: Arial; font-size: 10pt;">Wissenschaftlicher
Mitarbeiter / Abteilung Energiesysteme</span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;">Fraunhofer-Institut für
Bauphysik <br>Institutsteil Holzkirchen</span></p>
<p style="margin: 0cm 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;">Fraunhoferstraße
10<br>83626 Valley</span></p>
<p style="margin: 4.5pt 0cm;"><span style="font-family: Arial; font-size: 10pt;">eMail: <a href="mailto:Matthias.Kersken@ibp.fraunhofer.de" target="_blank">Matthias.Kersken@ibp.fraunhofer.de</a><br>Telefon
08024 / 643-204<br>Telefax 08024 / 643-366<br><a href="http://www.ibp.fraunhofer.de/" target="_blank">www.ibp.fraunhofer.de</a></span></p></td></tr></tbody></table>
<p class="MsoNormal"></p></div></td>
<td style="padding: 0.75pt; width: 5cm; min-height: 150.5pt;" valign="top" width="189">
<table style="width: 231pt; border-collapse: collapse; background: none repeat scroll 0% 0% silver; margin-left: 4.8pt; margin-right: 4.8pt;" width="308" align="left" border="1" cellpadding="0" cellspacing="0">
<tbody>
<tr>
<td style="padding: 3pt; background: none repeat scroll 0% 0% white;" valign="top">
<p style="margin: 0cm 0cm 4.5pt;"><b><span style="font-family: Arial; font-size: 10pt;" lang="EN-GB">Dipl.-Ing. Matthias Kersken<br></span></b><span style="font-family: Arial; font-size: 10pt;" lang="EN-GB">Research Associate / Department Energy Systems
</span><span lang="EN-GB"></span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;" lang="EN-GB">Fraunhofer Institute for Building Physics <br>Branch
Holzkirchen</span><span lang="EN-GB"></span></p>
<p style="margin: 0cm 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;" lang="EN-GB">Fraunhoferstraße 10<br>D-83626 Valley</span><span lang="EN-GB"></span></p>
<p style="margin: 4.5pt 0cm;"><span style="font-family: Arial; font-size: 10pt;" lang="EN-GB">eMail: </span><span style="font-family: Arial; font-size: 10pt;"><a href="mailto:Matthias.Kersken@ibp.fraunhofer.de" target="_blank"><span lang="EN-GB">Matthias.Kersken@ibp.fraunhofer.de</span></a></span><span style="font-family: Arial; font-size: 10pt;" lang="EN-GB"><br>
Phone +49 8024 / 643-204<br>Fax +49 8024 /
643-366<br></span><span style="font-family: Arial; font-size: 10pt;"><a href="http://www.ibp.fraunhofer.de/" target="_blank"><span lang="EN-GB">www.ibp.fraunhofer.de</span></a></span><span lang="EN-GB"></span></p>
</td></tr></tbody></table>
<p class="MsoNormal"><span lang="EN-GB"></span></p></td></tr></tbody></table>
<p style="margin: 9pt 0cm 0pt;"><span lang="EN-GB"> </span><span style="font-family: Arial; font-size: 10pt;"></span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;"> </span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;"> </span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;"> </span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;"> </span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;"> </span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;"> </span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;" lang="EN-GB"> </span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;"><img src="cid:921343512@08122010-2154" width="162" border="0" height="44"></span></p>
<p style="margin: 9pt 0cm 0pt;"><span style="font-family: Arial; font-size: 10pt;">---</span></p></div>
<div> </div></div>
<br><br>---------- 已转发邮件 ----------<br>From: "keilholz, werner" <<a href="mailto:werner.keilholz@cstb.fr">werner.keilholz@cstb.fr</a>><br>To: "Kersken, Matthias" <<a href="mailto:Matthias.Kersken@ibp.fraunhofer.de">Matthias.Kersken@ibp.fraunhofer.de</a>>, <<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Wed, 8 Dec 2010 15:01:02 +0100<br>Subject: Re: [TRNSYS-users] gbXML<br>
<div link="blue" vlink="purple" lang="FR">
<div>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Hi Kerksen, </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);" lang="EN-US">I only know about a commercial solution (and it may not be useful
outside France): the tool ClimaWin can import gbXML and export projects to
Trnsys (via <a href="http://nbdm.org" target="_blank">http://nbdm.org</a>). People use this in
France to simplify the transfer of projects between design tools (TRNSYS) and
building code software (ClimaWin). </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);" lang="EN-US"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);" lang="EN-US">I’m afraid it only exists in French. More info: </span><a href="http://www.bbs-slama.com/" target="_blank"><span lang="EN-US">http://www.bbs-slama.com/</span></a><span lang="EN-US"></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);" lang="EN-US"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);" lang="EN-US">Werner</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);" lang="EN-US"> </span></p>
<div>
<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0cm 0cm;">
<p class="MsoNormal"><b><span style="font-size: 10pt;">De :</span></b><span style="font-size: 10pt;"> Kersken, Matthias
[mailto:<a href="mailto:Matthias.Kersken@ibp.fraunhofer.de" target="_blank">Matthias.Kersken@ibp.fraunhofer.de</a>] <br>
<b>Envoyé :</b> mercredi 8 décembre 2010 13:36<br>
<b>À :</b> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<b>Objet :</b> [TRNSYS-users] gbXML</span></p>
</div>
</div>
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal"><span style="font-size: 10pt;">Dear TRNSYS
users!</span></p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 10pt;">Does
anyone of You know any possibility to get a gbXML-file into TRNSYS?</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 10pt;">(Non
commercial solution would be preferred).</span></p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 10pt;">Thank
You for Your help!</span></p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 10pt;">With
kind regards,</span></p>
</div>
<div>
<p class="MsoNormal"> <span style="font-size: 10pt;">Matthias Kersken</span></p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 10pt;">---</span></p>
<p class="MsoNormal"> </p>
<table align="left" border="0" cellpadding="0">
<tbody><tr style="min-height: 150.5pt;">
<td style="width: 87.75pt; padding: 0.75pt; min-height: 150.5pt;" valign="top" width="117">
<div>
<table style="width: 262.5pt; background: none repeat scroll 0% 0% silver; border-collapse: collapse; border: medium none; margin-left: 4.8pt; margin-right: 4.8pt;" width="350" align="left" border="1" cellpadding="0" cellspacing="0">
<tbody><tr>
<td style="border: 1pt solid windowtext; background: none repeat scroll 0% 0% white; padding: 3pt;">
<p style="margin-right: 0cm; margin-bottom: 4.5pt; margin-left: 0cm;"><b><span style="font-size: 10pt;">Dipl.-Ing.
Matthias Kersken<br>
</span></b><span style="font-size: 10pt;">Wissenschaftlicher
Mitarbeiter / Abteilung Energiesysteme</span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;">Fraunhofer-Institut
für Bauphysik <br>
Institutsteil Holzkirchen</span></p>
<p style="margin: 0cm 0cm 0.0001pt;"><span style="font-size: 10pt;">Fraunhoferstraße
10<br>
83626 Valley</span></p>
<p style="margin-right: 0cm; margin-bottom: 4.5pt; margin-left: 0cm;"><span style="font-size: 10pt;">eMail: <a href="mailto:Matthias.Kersken@ibp.fraunhofer.de" target="_blank">Matthias.Kersken@ibp.fraunhofer.de</a><br>
Telefon 08024 / 643-204<br>
Telefax 08024 / 643-366<br>
<a href="http://www.ibp.fraunhofer.de/" target="_blank">www.ibp.fraunhofer.de</a></span></p>
</td>
</tr>
</tbody></table>
</div>
</td>
<td style="width: 5cm; padding: 0.75pt; min-height: 150.5pt;" valign="top" width="189">
<table style="width: 231pt; background: none repeat scroll 0% 0% silver; border-collapse: collapse; margin-left: 4.8pt; margin-right: 4.8pt;" width="308" align="left" border="1" cellpadding="0" cellspacing="0">
<tbody><tr>
<td style="background: none repeat scroll 0% 0% white; padding: 3pt;" valign="top">
<p style="margin-right: 0cm; margin-bottom: 4.5pt; margin-left: 0cm;"><b><span style="font-size: 10pt;" lang="EN-GB">Dipl.-Ing.
Matthias Kersken<br>
</span></b><span style="font-size: 10pt;" lang="EN-GB">Research
Associate / Department Energy Systems </span><span lang="EN-GB"></span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;" lang="EN-GB">Fraunhofer
Institute for Building Physics <br>
Branch Holzkirchen</span><span lang="EN-GB"></span></p>
<p style="margin: 0cm 0cm 0.0001pt;"><span style="font-size: 10pt;" lang="EN-GB">Fraunhoferstraße
10<br>
D-83626 Valley</span><span lang="EN-GB"></span></p>
<p style="margin-right: 0cm; margin-bottom: 4.5pt; margin-left: 0cm;"><span style="font-size: 10pt;" lang="EN-GB">eMail: </span><span style="font-size: 10pt;"><a href="mailto:Matthias.Kersken@ibp.fraunhofer.de" target="_blank"><span lang="EN-GB">Matthias.Kersken@ibp.fraunhofer.de</span></a></span><span style="font-size: 10pt;" lang="EN-GB"><br>
Phone +49 8024 / 643-204<br>
Fax +49 8024 / 643-366<br>
</span><span style="font-size: 10pt;"><a href="http://www.ibp.fraunhofer.de/" target="_blank"><span lang="EN-GB">www.ibp.fraunhofer.de</span></a></span><span lang="EN-GB"></span></p>
</td>
</tr>
</tbody></table>
</td>
</tr>
</tbody></table>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span lang="EN-GB"> </span><span style="font-size: 10pt;"></span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;"> </span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;"> </span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;"> </span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;"> </span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;"> </span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;"> </span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;" lang="EN-GB"> </span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;"><img src="cid:image001.jpg@01CB96E8.BAE4B180" width="162" border="0" height="44"></span></p>
<p style="margin-right: 0cm; margin-left: 0cm; margin-bottom: 0.0001pt;"><span style="font-size: 10pt;">---</span></p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
</div>
</div>
<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
<br></blockquote></div><br>