<div>Dear all,</div>
<div> </div>
<div>  I designed a floor heating ( heating is only floor heating ) temperature PID control system. The set-point value is 19 C when  unoccupied, 21C when occupied. But there is a problem: it needs about 2 hours from 19C to 21C, BUT it needs about 7 hours from 21C to 19C. Attached is the figure.</div>

<div> </div>
<div> Please tell me why it can result in this situation? and how to deal with it?</div>
<div> </div>
<div>Many thanks!</div>
<div> </div>
<div>br.</div>
<div> </div>
<div>wang</div>
<div> </div>
<div><br><br> </div>
<div class="gmail_quote">2010/12/3 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br>       <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br>       <a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>       <a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br>
       <a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br><br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br><br>  1. not linked into trndll.dll (Bashar Termanini)<br>  2. Re: not linked into trndll.dll (Matt Duffy)<br>  3. Re: not linked into trndll.dll (David BRADLEY)<br>  4. Re: HELP TRNSYS 16 (David BRADLEY)<br>
<br><br>---------- 已转发邮件 ----------<br>From: "Bashar Termanini" <<a href="mailto:bashartermanini@gmail.com">bashartermanini@gmail.com</a>><br>To: <<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Fri, 3 Dec 2010 16:19:27 +0200<br>Subject: [TRNSYS-users] not linked into trndll.dll<br>Hi,<br><br>When I try to use my new component I get this error<br>"A TYPE was called in the TRNSYS input file but was either not linked into<br>
trndll.dll or was not found in an external dll. A dummy subroutine was<br>called in its place. Please link the TYPE or remove it from the input file"<br>Any help?<br><br>Thanks<br><br><br><br><br>---------- 已转发邮件 ----------<br>
From: "Matt Duffy" <<a href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>><br>To: "Bashar Termanini" <<a href="mailto:bashartermanini@gmail.com">bashartermanini@gmail.com</a>>, <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Fri, 3 Dec 2010 08:30:41 -0600 (CST)<br>Subject: Re: [TRNSYS-users] not linked into trndll.dll<br>Please make sure that the DLL that you compiled for your new component is<br>placed in the appropriate directory (.\Userlib\ReleaseDLLs).<br>
<br>Best regards,<br><br>Matt Duffy<br><br><br><br>----- Original Message -----<br>From: "Bashar Termanini" <<a href="mailto:bashartermanini@gmail.com">bashartermanini@gmail.com</a>><br>Sent: Fri, December 3, 2010 8:19<br>
Subject:[TRNSYS-users] not linked into trndll.dll<br><br>Hi,<br><br>When I try to use my new component I get this error<br>"A TYPE was called in the TRNSYS input file but was either not linked into<br>trndll.dll or was not found in an external dll. A dummy subroutine was<br>
called in its place. Please link the TYPE or remove it from the input file"<br>Any help?<br><br>Thanks<br><br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br><br>----- End of original message -----<br><br><br><br><br>---------- 已转发邮件 ----------<br>
From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>To: Bashar Termanini <<a href="mailto:bashartermanini@gmail.com">bashartermanini@gmail.com</a>><br>Date: Fri, 03 Dec 2010 09:47:17 -0600<br>
Subject: Re: [TRNSYS-users] not linked into trndll.dll<br>Bashar,<br>Also please make sure that you have the following line in your source code:<br><br>!DEC$ATTRIBUTES DLLEXPORT :: TYPExxx<br><br>where "xxx" is replaced by your Type number. If you are writing Type201, the line would be<br>
<br>!DEC$ATTRIBUTES DLLEXPORT :: TYPE201<br><br>Best,<br>David<br><br><br><br>On 12/3/2010 08:19, Bashar Termanini wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Hi,<br><br>When I try to use my new component I get this error<br>"A TYPE was called in the TRNSYS input file but was either not linked into<br>
trndll.dll or was not found in an external dll. A dummy subroutine was<br>called in its place. Please link the TYPE or remove it from the input file"<br>Any help?<br><br>Thanks<br><br>_______________________________________________<br>
TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br><a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
<br></blockquote><br>-- <br>***************************<br>David BRADLEY<br>Principal<br>Thermal Energy Systems Specialists, LLC<br>22 North Carroll Street - suite 370<br>Madison, WI  53703 USA<br><br>P:+1.608.274.2577<br>
F:+1.608.278.1475<br><a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a><br><br><a href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a><br><a href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a><br>
<br><br><br><br>---------- 已转发邮件 ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>To: <a href="mailto:david.irusta@idom.com">david.irusta@idom.com</a><br>Date: Fri, 03 Dec 2010 10:36:58 -0600<br>
Subject: Re: [TRNSYS-users] HELP TRNSYS 16<br>
<div bgcolor="#ffffff" text="#000000">David<br><br>
<blockquote type="cite"><font size="2" face="sans-serif"></font><font size="2" face="sans-serif">-How do you Know if the horizontal wall is floor o ceiling?</font> <br></blockquote>The TRNSYS 16 building model was non-geometric; when you define a horizontal surface, the only thing that indicates whether it is a floor or a ceiling is the condition that you impose on the opposite side of the surface.<br>

<blockquote type="cite"><font size="2" face="sans-serif">-Creating a Multizone Building, </font><br><font size="2" face="sans-serif">        when you have to decide the outputs,how can you select a surface(to choose for example TOFL) instead of a Thermal zone?</font> <br>
</blockquote>there are a number of radio buttons across the middle of the window. You still select a zone but then you switch to "surface outputs" and you will see the available NTYPEs for the surfaces in that zone.<br>

<blockquote type="cite"><font size="2" face="sans-serif">        how can you do a multistorey building??</font> <br></blockquote>The ceiling of one zone is set as wall type "ADJACENT" and you indicate the name of the zone above whose floor is the same as that ceiling.<br>

<blockquote type="cite"><font size="2" face="sans-serif">I´m interested in create a model about TABS (thermal active building system) which includes active layers</font> <br><font size="2" face="sans-serif">-where can I find examples or tutorials with TRNSYS 16? </font><br>
</blockquote>I believe that some of the feedback controller examples (..trnsys16\Examples\...) show how to use the active layers.<br><br>Best,<br> David<br><br><pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com</a></pre></div><br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br><br></blockquote></div><br>