Dr Rami,<br>
I am not aware of any examples of coupling Type36 and Type56.
However, looking at the mathematical reference manual entry for
Type36, I think the best approximation that you are going to be able
to do is as follows:<br>
<br>
Type36 makes the simplifying assumption that the inside surface
temperature of the wall is the same as the innermost node
temperature. It allows you to calculate the convection between that
node and the room temperature by asking you to specify the inside
heat transfer coefficient as an input. In TRNBuild, add a low
resistance "massless" BOUNDARY wall on the south side of your
building and select "userdefined: input" as the back side surface
temperature. Set the outside convection coefficient of that wall to
be 0.0001 (indicating direct contact). Also output the "inside
surface temperature" for that wall from Type56. In Type36, enter the
resistance of the wall for the "inside convection coefficient"
Type56's inside wall surface temperature becomes the room
temperature that you pass to Type36 and Type36 innermost node
temperature becomes the "outside surface temperature" that you pass
back to Type56.<br>
<br>
I am not promising that this will work but I think it is worth a
try.<br>
Best,<br>
David<br>
<br>
<br>
<br>
<br>
On 11/13/2010 03:38, Dr.Rami wrote:
<blockquote cite="mid:000401cb8316$7b0622f0$711268d0$@org"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 12 (filtered
medium)">
<style>
<!--
/* Font Definitions */
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Consolas;
panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
text-align:right;
direction:rtl;
unicode-bidi:embed;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p.MsoPlainText, li.MsoPlainText, div.MsoPlainText
{mso-style-priority:99;
mso-style-link:"\0646\0635 \0639\0627\062F\064A Char";
margin:0cm;
margin-bottom:.0001pt;
text-align:right;
direction:rtl;
unicode-bidi:embed;
font-size:10.5pt;
font-family:Consolas;}
span.Char
{mso-style-name:"\0646\0635 \0639\0627\062F\064A Char";
mso-style-priority:99;
mso-style-link:"\0646\0635 \0639\0627\062F\064A";
font-family:Consolas;}
span.19
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:windowtext;}
span.20
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page Section1
{size:612.0pt 792.0pt;
margin:72.0pt 90.0pt 72.0pt 90.0pt;}
div.Section1
{page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="Section1">
<p class="MsoNormal" style="text-align: left; direction: ltr;
unicode-bidi: embed;"><span style="color: rgb(31, 73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal" style="text-align: left; direction: ltr;
unicode-bidi: embed;"><span style="color: rgb(31, 73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal" style="text-align: left; direction: ltr;
unicode-bidi: embed;"><span style="font-size: 14pt;
font-family: "Times New Roman","serif";
color: black;">Dear
sir<o:p></o:p></span></p>
<p class="MsoNormal" style="text-align: left; direction: ltr;
unicode-bidi: embed;"><span style="color: rgb(31, 73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal" style="text-align: left; direction: ltr;
unicode-bidi: embed;"><span style="font-size: 14pt;
font-family: "Times New Roman","serif";">I
work with
TRNSYS 16 and try to connect Trombe wall (type 36) to
building (type 56). so, I
connect</span><span style="font-size: 14pt; font-family:
"Times New Roman","serif";" lang="EN-GB">ed
the
first output of Trombe wall to defined gain in building and
the room air
temperature to Trombe wall input, but how the program
understand that Trombe wall
is connected to south wall for example. I make the south
wall massless and not
external but boundary, I am not sure if that is true so
could you please help
me to get the correct connection. </span><span
style="font-size: 14pt; font-family: "Times New
Roman","serif";">Please send an example (deck
file).<o:p></o:p></span></p>
<p class="MsoNormal" style="text-align: left; direction: ltr;
unicode-bidi: embed;"><span style="font-size: 14pt;
font-family: "Times New Roman","serif";"
lang="EN-GB"><o:p> </o:p></span></p>
<p class="MsoPlainText" style="text-align: left; direction: ltr;
unicode-bidi: embed;"><span style="font-size: 14pt;
font-family: "Times New Roman","serif";"
lang="EN-GB">With
my best regards</span><o:p></o:p></p>
<p class="MsoNormal" dir="RTL"><span dir="LTR"><o:p> </o:p></span></p>
</div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>