    Wang,<br>
     TRNBuild calculates the coefficients of a transfer function that
    describes the way in which energy is transferred through a given
    wall. The transfer function is basically an infinite series and each
    coefficient is a multiplier on a particular term in the transfer
    function (an example of one of the terms is the temperature
    difference across the wall). Time is discretized into steps
    backwards through the wall's history; the step size is called the
    time base. For example, if the time base is 1 hour then coefficient
    multipliers for each term in the transfer function will be computed
    for now, 1 hour ago, 2 hours ago, 3 hours ago etc.<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    On 11/3/2010 09:46, 王洋 wrote:
    <blockquote
      cite="mid:AANLkTimXY6nEkOk8GgSACzdM7E-sRFO_xYM_L9t=fxaA@mail.gmail.com"
      type="cite">
      <div><br>
        Dear all,</div>
      <div> </div>
      <div>  What's the difference between the time base of transfer
        function ( in Outputs of TRNBuild ) and Zone thermal time
        constant?</div>
      <div> </div>
      <div>Are they the same? If different, how to calculate the zone
        thermal time constant? based on which parameters?</div>
      <div> </div>
      <div>Many thanks!</div>
      <div> </div>
      <div>br.</div>
      <div> </div>
      <div>wang</div>
      <div> </div>
      <div> </div>
      <div> </div>
      <div><br>
         </div>
      <div class="gmail_quote">2010/11/3 <span dir="ltr"><<a
            moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
        <blockquote style="border-left: 1px solid rgb(204, 204, 204);
          margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
          class="gmail_quote">Send TRNSYS-users mailing list submissions
          to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          <br>
          To subscribe or unsubscribe via the World Wide Web, visit<br>
                 <a moz-do-not-send="true"
            href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
            target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
          or, via email, send a message with subject or body 'help' to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
          <br>
          You can reach the person managing the list at<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
          <br>
          When replying, please edit your Subject line so it is more
          specific<br>
          than "Re: Contents of TRNSYS-users digest..."<br>
          <br>
          Today's Topics:<br>
          <br>
            1. How to calculate the zone thermal time constant & air
          volume<br>
               flow of opening (=?GB2312?B?zfXR8w==?=)<br>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: 王洋 <<a moz-do-not-send="true"
            href="mailto:wanghongyang1767@gmail.com">wanghongyang1767@gmail.com</a>><br>
          To: <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          Date: Wed, 3 Nov 2010 15:29:36 +0100<br>
          Subject: [TRNSYS-users] How to calculate the zone thermal time
          constant & air volume flow of opening<br>
          <div>Dear all,</div>
          <div> </div>
          <div>1. How to calculate or find the thermal time constant of
            zone in TRNSYS software?  </div>
          <p>---------- WALL TYPE BST_FL_HEAT_W1      ----------</p>
          <p>       THERMAL CONDUCTANCE, U=    67.80000 kJ/h m2K;
            U-Wert=     4.48235 W/m2K<br>
                          (incl. alpha_i=7.7 W/m^2 K and alpha_o=25
            W/m^2 K)</p>
          <p>                        TRANSFERFUNCTION COEFFICIENTS<br>
               K            A              B              C             
            D</p>
          <p>   0       1.7050117E+02    2.1087019E+01   
            1.7050117E+02    1.0000000E+00<br>
               1      -1.1800059E+02    3.5808933E+01   -1.1800059E+02  
            -1.3683139E-01<br>
               2       6.0267372E+00    1.6298573E+00   
            6.0267372E+00    4.7362566E-05<br>
               3      -1.2736107E-03    2.3363784E-04   -1.2736107E-03<br>
              SUM      5.8526043E+01    5.8526043E+01   
            5.8526043E+01    8.6321597E-01</p>
          <div>What's meaning of A B C D? Are they Wall's
            TRANSFERFUNCTION COEFFICIENTS? And what is the thermal time
            constant of the whole zone? How to calculate or find the
            thermal time constant of the whole zone in TRNSYS software?
            <br>
            Need I   calculate by myself the whole zone's
            TRANSFERFUNCTION based on all the walls of the zone or
            others?</div>
          <div> </div>
          <div>2.  How to calculate or find air volume flow of
            the window opening in TRNFlow software?  <br>
          </div>
          <div>The window opening area (m2)is known. Whether it needs
            the wind speed(m/s) or not?</div>
          <div> </div>
          <div>Many thanks!</div>
          <div> </div>
          <div>Br.</div>
          <div> </div>
          <div>wang<br>
          </div>
          <div class="gmail_quote">2010/11/3 <span dir="ltr"><<a
                moz-do-not-send="true"
                href="mailto:trnsys-users-request@cae.wisc.edu"
                target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
            <blockquote style="border-left: 1px solid rgb(204, 204,
              204); margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
              class="gmail_quote">Send TRNSYS-users mailing list
              submissions to<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
              <br>
              To subscribe or unsubscribe via the World Wide Web, visit<br>
                     <a moz-do-not-send="true"
                href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
                target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
              or, via email, send a message with subject or body 'help'
              to<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users-request@cae.wisc.edu"
                target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
              <br>
              You can reach the person managing the list at<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users-owner@cae.wisc.edu"
                target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
              <br>
              When replying, please edit your Subject line so it is more
              specific<br>
              than "Re: Contents of TRNSYS-users digest..."<br>
              <br>
              Today's Topics:<br>
              <br>
                1. Re: GenOpt optimization: problem for the second
              generation<br>
                   after 5 simulations (Thibaut VITTE)<br>
                2. Re: google sketchup+trnsys3d (hotline)<br>
                3. input file (Emiliano Casati - 3ME)<br>
                4. Re: GenOpt optimization: problem for the
              secondgeneration<br>
                   after 5 simulations (Timothy McDowell)<br>
              <br>
              <br>
              ---------- 已转发邮件 ----------<br>
              From: Thibaut VITTE <<a moz-do-not-send="true"
                href="mailto:thibaut.vitte@h3c-energies.fr"
                target="_blank">thibaut.vitte@h3c-energies.fr</a>><br>
              To: <a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
              Date: Wed, 03 Nov 2010 11:27:53 +0100<br>
              Subject: Re: [TRNSYS-users] GenOpt optimization: problem
              for the second generation after 5 simulations<br>
              <div bgcolor="#ffffff" text="#000000">Dear Alexis,<br>
                <br>
                I've had a similar error when I used Genopt. I've had
                several components tracked by a "trace" command that
                made my list file enormous (more than 100Mb) and genopt
                could'nt handle that amount of data.<br>
                <br>
                Just my 2cents.<br>
                <br>
                Thibaut<br>
                <div>-- <br>
                  <table>
                    <tbody>
                      <tr>
                        <td>
                          <div>
                            <div style="min-height: 0.854in; width:
                              2in;">
                              <p><img moz-do-not-send="true"
                                  src="cid:part1.06030601.07070104@h3c-energies.fr"></p>
                              <p>Le futur maîtrisé</p>
                            </div>
                          </div>
                        </td>
                        <td><br>
                        </td>
                        <td>
                          <p>Thibaut VITTE</p>
                          <p>Docteur - Ingénieur Energies</p>
                          <p><span>Mail : </span><span><a
                                moz-do-not-send="true"
                                href="mailto:thibaut.vitte@h3c-energies.fr"
                                target="_blank">thibaut.vitte@h3c-energies.fr</a>
                            </span></p>
                          <p>-----------------------------</p>
                          <p>H3C-énergies</p>
                          <p>35, chemin du vieux Chêne - 38240 MEYLAN</p>
                          <p><span>Tél : </span><span>04 76 41 88 66</span><span>
                              – </span><span>Fax : </span><span>04 76
                              41 28 94</span></p>
                          <p><a moz-do-not-send="true"
                              href="http://www.h3c-energies.fr/"
                              target="_blank">www.h3c-energies.fr</a></p>
                        </td>
                        <td><br>
                        </td>
                      </tr>
                    </tbody>
                  </table>
                  <p>-----------------------------------------------------------------------------------</p>
                  <p>Afin de contribuer au respect de l'environnement,
                    merci de n'imprimer ce message qu'en cas de
                    nécessité.</p>
                  <p>In order to respect the environment, please don't
                    print this e-mail unless you really need to.</p>
                </div>
              </div>
              <br>
              <br>
              ---------- 已转发邮件 ----------<br>
              From: "hotline" <<a moz-do-not-send="true"
                href="mailto:hotline@transsolar.com" target="_blank">hotline@transsolar.com</a>><br>
              To: "julia.feste" <<a moz-do-not-send="true"
                href="mailto:julia.feste@whitepavilion.com.cn"
                target="_blank">julia.feste@whitepavilion.com.cn</a>><br>
              Date: Wed, 3 Nov 2010 11:37:08 +0100<br>
              Subject: Re: [TRNSYS-users] google sketchup+trnsys3d<br>
              Hi,<br>
              <br>
              that's a well known problem that will be fixed in the next
              version.<br>
              Hopefully upcoming within the next weeks.<br>
              <br>
              Regards<br>
              Christian<br>
              <br>
              TRANSSOLAR Software Team<br>
              <a moz-do-not-send="true"
                href="mailto:hotline@transsolar.com" target="_blank">hotline@transsolar.com</a><br>
              <br>
              <a moz-do-not-send="true" href="http://www.trnsys.de/"
                target="_blank">www.trnsys.de</a><br>
              Transsolar KlimaEngineering - Technologien für
              energieeffizientes Bauen<br>
              und Nutzerkomfort in Gebäuden<br>
              Transsolar Energietechnik GmbH, Curiestrasse 2, 70563
              Stuttgart /<br>
              Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.: 99073/00911<br>
              Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing.
              Thomas Auer,<br>
              Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher<br>
              <br>
              -----Ursprüngliche Nachricht-----<br>
              Von: julia.feste [mailto:<a moz-do-not-send="true"
                href="mailto:julia.feste@whitepavilion.com.cn"
                target="_blank">julia.feste@whitepavilion.com.cn</a>]<br>
              Gesendet: Mittwoch, 3. November 2010 06:46<br>
              An: <a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
              Betreff: [TRNSYS-users] google sketchup+trnsys3d<br>
              <br>
              <br>
              Hello everybody,<br>
              Thanks for your posts that's always really interesting!<br>
              I come up with a problem using Google Sketchup and
              TRNSYS3D: inside a<br>
              TRNSYS zone, I draft a square, then I want to pull it up
              at a certain<br>
              height, so I write the number then Enter, and this error
              appears:<br>
              <br>
              <-----Beginning of the error-----><br>
              ERROR:<br>
              NoMethodError<br>
              undefined method `position' for<br>
              #<Sketchup::AttributeDictionary:0xfcb4eb8><br>
              <br>
              BACKTRACE:<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in
              `polygon_loop'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `each'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in
              `polygon_loop'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/sketchup/Sketchup.rb:321:in
              `outer_polygon'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/sketchup/Sketchup.rb:326:in `polygon'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:27:in<br>
              `detect_base_face'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in
              `each'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in<br>
              `detect_base_face'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:254:in
              `face_polygon'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in
              `each'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in
              `face_polygon'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/Surface.rb:107:in<br>
              `update_input_object'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:94:in<br>
              `update_input_object'<br>
              C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/DrawingInterface.rb:353:in<br>
              `on_change_entity'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/observers/FaceObserver.rb:32:in
              `onChangeEntity'<br>
              C:/Program Files/Google/Google SketchUp<br>
              8/Plugins/Trnsys3d/lib/AsynchProc.rb:17:in `initialize'<br>
              <br>
              <-----End of the error-----><br>
              <br>
              When I pull it up manual, I don't have any problem, just
              when I write<br>
              the number.<br>
              <br>
              Thanks in advance for your help,<br>
              Julia.<br>
              ________________________________________<br>
              From: <a moz-do-not-send="true"
                href="mailto:trnsys-users-request@cae.wisc.edu"
                target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
              [<a moz-do-not-send="true"
                href="mailto:trnsys-users-request@cae.wisc.edu"
                target="_blank">trnsys-users-request@cae.wisc.edu</a>]<br>
              Sent: Wednesday, November 03, 2010 1:04 AM<br>
              To: <a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
              Subject: TRNSYS-users Digest, Vol 71, Issue 4<br>
              <br>
              Send TRNSYS-users mailing list submissions to<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
              <br>
              To subscribe or unsubscribe via the World Wide Web, visit<br>
                     <a moz-do-not-send="true"
                href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
                target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
              or, via email, send a message with subject or body 'help'
              to<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users-request@cae.wisc.edu"
                target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
              <br>
              You can reach the person managing the list at<br>
                     <a moz-do-not-send="true"
                href="mailto:trnsys-users-owner@cae.wisc.edu"
                target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
              <br>
              When replying, please edit your Subject line so it is more
              specific than<br>
              "Re: Contents of TRNSYS-users digest..."<br>
              <br>
              _______________________________________________<br>
              TRNSYS-users mailing list<br>
              <a moz-do-not-send="true"
                href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
              <a moz-do-not-send="true"
                href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
                target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              ---------- 已转发邮件 ----------<br>
              From: "Emiliano Casati - 3ME" <<a
                moz-do-not-send="true"
                href="mailto:E.I.M.Casati@tudelft.nl" target="_blank">E.I.M.Casati@tudelft.nl</a>><br>
              To: <<a moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>
              Date: Wed, 3 Nov 2010 13:19:58 +0100<br>
              Subject: [TRNSYS-users] input file<br>
              <div vlink="purple" link="blue" lang="NL">
                <div>
                  <p class="MsoNormal"><span lang="EN-US">Hi to
                      everybody!</span></p>
                  <p class="MsoNormal"><span lang="EN-US">I don’t
                      understand why, for certain projects, I can’t open
                      the input file, the message is “the system cannot
                      find the path specified”.</span></p>
                  <p class="MsoNormal"><span lang="EN-US">Where should I
                      find the input file?</span></p>
                  <p class="MsoNormal"><span lang="EN-US"> </span></p>
                  <p class="MsoNormal"><span lang="EN-US">Thanks a lot</span></p>
                  <p class="MsoNormal"><span lang="EN-US"> </span></p>
                  <p class="MsoNormal"><span lang="EN-US">ec</span></p>
                </div>
              </div>
              <br>
              <br>
              ---------- 已转发邮件 ----------<br>
              From: "Timothy McDowell" <<a moz-do-not-send="true"
                href="mailto:mcdowell@tess-inc.com" target="_blank">mcdowell@tess-inc.com</a>><br>
              To: "Thibaut VITTE" <<a moz-do-not-send="true"
                href="mailto:thibaut.vitte@h3c-energies.fr"
                target="_blank">thibaut.vitte@h3c-energies.fr</a>>, <a
                moz-do-not-send="true"
                href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
              Date: Wed, 3 Nov 2010 07:23:05 -0500 (CDT)<br>
              Subject: Re: [TRNSYS-users] GenOpt optimization: problem
              for the secondgeneration after 5 simulations<br>
              This type of error in GenOpt is usually caused by an error
              in the TRNSYS<br>
              simulation.  You need to check the *.lst file for the
              TRNSYS run to see<br>
              what the TRNSYS error is.<br>
              <br>
              Regards,<br>
              <br>
              Tim<br>
              <br>
              <br>
              <br>
              <br>
              <br>
              ----------------------------------<br>
              Timothy McDowell<br>
              Executive Vice President<br>
              Thermal Energy System Specialists, LLC<br>
              22 N. Carroll St, Suite 370<br>
              Madison, WI 53703<br>
              Phone: 608-274-2577<br>
              Fax: 608-278-1475<br>
              <br>
              ----- Original Message -----<br>
              From: "Thibaut VITTE" <<a moz-do-not-send="true"
                href="mailto:thibaut.vitte@h3c-energies.fr"
                target="_blank">thibaut.vitte@h3c-energies.fr</a>><br>
              Sent: Wed, November 3, 2010 5:27<br>
              Subject:Re: [TRNSYS-users] GenOpt optimization: problem
              for the<br>
              secondgeneration after 5 simulations<br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
                 Dear Alexis,<br>
              <br>
                 I've had a similar error when I used Genopt. I've had
              several<br>
                 components tracked by a "trace" command that made my
              list file<br>
                 enormous (more than 100Mb) and genopt could'nt handle
              that amount of<br>
                 data.<br>
              <br>
                 Just my 2cents.<br>
              <br>
                 Thibaut<br>
                 --<br>
              <br>
              <br>
              .bodyclass      @page { size: 8.5in 11in; margin-top:
              0.7874in; margin-bottom:<br>
              0.7874in; margin-left: 0.7874in; margin-right: 0.7874in }<br>
              .bodyclass      table { border-collapse:collapse;
              border-spacing:0;<br>
              empty-cells:show }<br>
              .bodyclass      td, th { vertical-align:top;
              font-size:12pt;}<br>
              .bodyclass      h1, h2, h3, h4, h5, h6 { clear:both }<br>
              .bodyclass      ol, ul { margin:0; padding:0;}<br>
              .bodyclass      li { list-style: none; margin:0;
              padding:0;}<br>
              .bodyclass      li span.odfLiEnd { clear: both;
              line-height:0; width:0;<br>
              height:0; margin:0; padding:0; }<br>
              .bodyclass      span.footnodeNumber { padding-right:1em; }<br>
              .bodyclass      * { margin:0; }<br>
              .bodyclass      .fr1 { font-size:12pt; text-align:center;
              vertical-align:top;<br>
              margin-left:0in; margin-right:0in; margin-top:0in;
              margin-bottom:0in;<br>
              padding:0in; border-style:none; }<br>
              .bodyclass      .P1 { font-size:12pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Times New Roman; text-align:center !
              important; }<br>
              .bodyclass      .P10 { font-size:7.5pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:justify !
              important;<br>
              color:#f79646; }<br>
              .bodyclass      .P2 { font-size:9pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:center !
              important;<br>
              color:#e36c0a; font-style:italic; font-weight:bold; }<br>
              .bodyclass      .P3 { font-size:9pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:justify !
              important;<br>
              color:#e36c0a; font-weight:bold; }<br>
              .bodyclass      .P4 { font-size:9pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:justify !
              important;<br>
              color:#e36c0a; font-weight:bold; }<br>
              .bodyclass      .P5 { font-size:7.5pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; color:#e36c0a;
              font-weight:bold; }<br>
              .bodyclass      .P6 { font-size:7.5pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:justify !
              important;<br>
              color:#3329b1; }<br>
              .bodyclass      .P61 { font-size:8.5pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:justify !
              important;<br>
              color:#3329b1; }<br>
              .bodyclass      .P7 { font-size:7.5pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:justify !
              important;<br>
              color:#3329b1; font-style:italic; }<br>
              .bodyclass      .P8 { font-size:7.5pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Tahoma, sans-serif; text-align:justify !
              important;<br>
              color:#3329b1; font-style:italic; }<br>
              .bodyclass      .P9 { font-size:12pt; margin-bottom:0in;
              margin-top:0in;<br>
              font-family:Times New Roman; text-align:justify !
              important; }<br>
              .bodyclass      .P91 { font-size:12pt; margin-bottom:0in;
              margin-top:0.05in;<br>
              font-family:Times New Roman; text-align:justify !
              important; }<br>
              .bodyclass      .Standard { font-size:12pt;
              font-family:Times New Roman; }<br>
              .bodyclass      .T1 { color:#f79646; }<br>
              .bodyclass      .T2 { color:#f79646; font-family:Tahoma,
              sans-serif;<br>
              font-size:7.5pt; }<br>
              .bodyclass      .T3 { color:#3329b1; font-family:Tahoma,
              sans-serif;<br>
              font-size:7.5pt; }<br>
              .bodyclass      { }<br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
                               Le futur maîtrisé<br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
                           Thibaut VITTE<br>
                           Docteur - Ingénieur Energies<br>
                           Mail : <a moz-do-not-send="true"
                href="mailto:thibaut.vitte@h3c-energies.fr"
                target="_blank">thibaut.vitte@h3c-energies.fr</a><br>
              <br>
                           -----------------------------<br>
                           H3C-énergies<br>
                           35, chemin du vieux Chêne - 38240 MEYLAN<br>
                           Tél : 04 76 41 88 66 – Fax : 04 76 41 28<br>
                               94<br>
                           <a moz-do-not-send="true"
                href="http://www.h3c-energies.fr/" target="_blank">www.h3c-energies.fr</a><br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
                 
 -----------------------------------------------------------------------------------<br>
                   Afin de contribuer au respect de l'environnement,<br>
                     merci de n'imprimer ce message qu'en cas de
              nécessité.<br>
                   In order to respect the environment, please don't<br>
                     print this e-mail unless you really need to.<br>
              <br>
              <br>
              <br>
              <br>
              <br>
              <br>
              _______________________________________________<br>
              TRNSYS-users mailing list<br>
              <a moz-do-not-send="true"
                href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
              <a moz-do-not-send="true"
                href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
                target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
              <br>
              <br>
              ----- End of original message -----<br>
              <br>
              <br>
              <br>
              _______________________________________________<br>
              TRNSYS-users mailing list<br>
              <a moz-do-not-send="true"
                href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
              <a moz-do-not-send="true"
                href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
                target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
              <br>
            </blockquote>
          </div>
          <br>
          <br>
          _______________________________________________<br>
          TRNSYS-users mailing list<br>
          <a moz-do-not-send="true"
            href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
          <a moz-do-not-send="true"
            href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
            target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>