Wang,<br>
The thermal time constant for a zone in your building is not a
simple thing to compute. It has to do with the materials in the
wall, the placement of the mass within the wall, the capacitance of
the zone, ventilation, infiltration, gains, solar radiation, etc. I
would think that the easiest way to get an estimate of the zone's
thermal time constant is to impose a step change in one input on it
- step change the ambient temperature while holding all other inputs
constant for example. <br>
<br>
The numbers that you see in the *.inf file are transfer function
coefficients. You can read in the ASHRAE Handbook of Fundamentals
about the Conduction Transfer Function methodology. <br>
Regards,<br>
David<br>
<br>
<br>
On 11/3/2010 09:29, 王洋 wrote:
<blockquote
cite="mid:AANLkTimRSHiVy+X9-hf6QBUA0nPCY+iE6zuv2QacSEvg@mail.gmail.com"
type="cite">
<div>Dear all,</div>
<div> </div>
<div>1. How to calculate or find the thermal time constant of zone
in TRNSYS software? </div>
<p>---------- WALL TYPE BST_FL_HEAT_W1 ----------</p>
<p> THERMAL CONDUCTANCE, U= 67.80000 kJ/h m2K;
U-Wert= 4.48235 W/m2K<br>
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)</p>
<p> TRANSFERFUNCTION COEFFICIENTS<br>
K A B C D</p>
<p> 0 1.7050117E+02 2.1087019E+01 1.7050117E+02
1.0000000E+00<br>
1 -1.1800059E+02 3.5808933E+01 -1.1800059E+02
-1.3683139E-01<br>
2 6.0267372E+00 1.6298573E+00 6.0267372E+00
4.7362566E-05<br>
3 -1.2736107E-03 2.3363784E-04 -1.2736107E-03<br>
SUM 5.8526043E+01 5.8526043E+01 5.8526043E+01
8.6321597E-01</p>
<div>What's meaning of A B C D? Are they Wall's TRANSFERFUNCTION
COEFFICIENTS? And what is the thermal time constant of the whole
zone? How to calculate or find the thermal time constant of the
whole zone in TRNSYS software? <br>
Need I calculate by myself the whole zone's TRANSFERFUNCTION
based on all the walls of the zone or others?</div>
<div> </div>
<div>2. How to calculate or find air volume flow of the window
opening in TRNFlow software? <br>
</div>
<div>The window opening area (m2)is known. Whether it needs the
wind speed(m/s) or not?</div>
<div> </div>
<div>Many thanks!</div>
<div> </div>
<div>Br.</div>
<div> </div>
<div>wang<br>
</div>
<div class="gmail_quote">2010/11/3 <span dir="ltr"><<a
moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="border-left: 1px solid rgb(204, 204, 204);
margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
class="gmail_quote">Send TRNSYS-users mailing list submissions
to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
<a moz-do-not-send="true"
href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more
specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>
Today's Topics:<br>
<br>
1. Re: GenOpt optimization: problem for the second
generation<br>
after 5 simulations (Thibaut VITTE)<br>
2. Re: google sketchup+trnsys3d (hotline)<br>
3. input file (Emiliano Casati - 3ME)<br>
4. Re: GenOpt optimization: problem for the secondgeneration<br>
after 5 simulations (Timothy McDowell)<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: Thibaut VITTE <<a moz-do-not-send="true"
href="mailto:thibaut.vitte@h3c-energies.fr">thibaut.vitte@h3c-energies.fr</a>><br>
To: <a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Wed, 03 Nov 2010 11:27:53 +0100<br>
Subject: Re: [TRNSYS-users] GenOpt optimization: problem for
the second generation after 5 simulations<br>
<div bgcolor="#ffffff" text="#000000">Dear Alexis,<br>
<br>
I've had a similar error when I used Genopt. I've had
several components tracked by a "trace" command that made my
list file enormous (more than 100Mb) and genopt could'nt
handle that amount of data.<br>
<br>
Just my 2cents.<br>
<br>
Thibaut<br>
<div>-- <br>
<table>
<tbody>
<tr>
<td>
<div>
<div style="min-height: 0.854in; width: 2in;">
<p><img moz-do-not-send="true"
src="cid:part1.06030601.07070104@h3c-energies.fr"></p>
<p>Le futur maîtrisé</p>
</div>
</div>
</td>
<td><br>
</td>
<td>
<p>Thibaut VITTE</p>
<p>Docteur - Ingénieur Energies</p>
<p><span>Mail : </span><span><a
moz-do-not-send="true"
href="mailto:thibaut.vitte@h3c-energies.fr"
target="_blank">thibaut.vitte@h3c-energies.fr</a>
</span></p>
<p>-----------------------------</p>
<p>H3C-énergies</p>
<p>35, chemin du vieux Chêne - 38240 MEYLAN</p>
<p><span>Tél : </span><span>04 76 41 88 66</span><span>
</span><span>Fax : </span><span>04 76 41
28 94</span></p>
<p><a moz-do-not-send="true"
href="http://www.h3c-energies.fr/"
target="_blank">www.h3c-energies.fr</a></p>
</td>
<td><br>
</td>
</tr>
</tbody>
</table>
<p>-----------------------------------------------------------------------------------</p>
<p>Afin de contribuer au respect de l'environnement, merci
de n'imprimer ce message qu'en cas de nécessité.</p>
<p>In order to respect the environment, please don't print
this e-mail unless you really need to.</p>
</div>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "hotline" <<a moz-do-not-send="true"
href="mailto:hotline@transsolar.com">hotline@transsolar.com</a>><br>
To: "julia.feste" <<a moz-do-not-send="true"
href="mailto:julia.feste@whitepavilion.com.cn">julia.feste@whitepavilion.com.cn</a>><br>
Date: Wed, 3 Nov 2010 11:37:08 +0100<br>
Subject: Re: [TRNSYS-users] google sketchup+trnsys3d<br>
Hi,<br>
<br>
that's a well known problem that will be fixed in the next
version.<br>
Hopefully upcoming within the next weeks.<br>
<br>
Regards<br>
Christian<br>
<br>
TRANSSOLAR Software Team<br>
<a moz-do-not-send="true" href="mailto:hotline@transsolar.com">hotline@transsolar.com</a><br>
<br>
<a moz-do-not-send="true" href="http://www.trnsys.de/"
target="_blank">www.trnsys.de</a><br>
Transsolar KlimaEngineering - Technologien für
energieeffizientes Bauen<br>
und Nutzerkomfort in Gebäuden<br>
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563
Stuttgart /<br>
Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.: 99073/00911<br>
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas
Auer,<br>
Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher<br>
<br>
-----Ursprüngliche Nachricht-----<br>
Von: julia.feste [mailto:<a moz-do-not-send="true"
href="mailto:julia.feste@whitepavilion.com.cn">julia.feste@whitepavilion.com.cn</a>]<br>
Gesendet: Mittwoch, 3. November 2010 06:46<br>
An: <a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Betreff: [TRNSYS-users] google sketchup+trnsys3d<br>
<br>
<br>
Hello everybody,<br>
Thanks for your posts that's always really interesting!<br>
I come up with a problem using Google Sketchup and TRNSYS3D:
inside a<br>
TRNSYS zone, I draft a square, then I want to pull it up at a
certain<br>
height, so I write the number then Enter, and this error
appears:<br>
<br>
<-----Beginning of the error-----><br>
ERROR:<br>
NoMethodError<br>
undefined method `position' for<br>
#<Sketchup::AttributeDictionary:0xfcb4eb8><br>
<br>
BACKTRACE:<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `polygon_loop'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `each'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `polygon_loop'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/sketchup/Sketchup.rb:321:in `outer_polygon'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/sketchup/Sketchup.rb:326:in `polygon'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:27:in<br>
`detect_base_face'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in `each'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in<br>
`detect_base_face'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:254:in
`face_polygon'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in `each'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in
`face_polygon'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/Surface.rb:107:in<br>
`update_input_object'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:94:in<br>
`update_input_object'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/interfaces/DrawingInterface.rb:353:in<br>
`on_change_entity'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/observers/FaceObserver.rb:32:in
`onChangeEntity'<br>
C:/Program Files/Google/Google SketchUp<br>
8/Plugins/Trnsys3d/lib/AsynchProc.rb:17:in `initialize'<br>
<br>
<-----End of the error-----><br>
<br>
When I pull it up manual, I don't have any problem, just when
I write<br>
the number.<br>
<br>
Thanks in advance for your help,<br>
Julia.<br>
________________________________________<br>
From: <a moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
[<a moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>]<br>
Sent: Wednesday, November 03, 2010 1:04 AM<br>
To: <a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Subject: TRNSYS-users Digest, Vol 71, Issue 4<br>
<br>
Send TRNSYS-users mailing list submissions to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
<a moz-do-not-send="true"
href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more
specific than<br>
"Re: Contents of TRNSYS-users digest..."<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "Emiliano Casati - 3ME" <<a moz-do-not-send="true"
href="mailto:E.I.M.Casati@tudelft.nl">E.I.M.Casati@tudelft.nl</a>><br>
To: <<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Wed, 3 Nov 2010 13:19:58 +0100<br>
Subject: [TRNSYS-users] input file<br>
<div vlink="purple" link="blue" lang="NL">
<div>
<p class="MsoNormal"><span lang="EN-US">Hi to everybody!</span></p>
<p class="MsoNormal"><span lang="EN-US">I don’t understand
why, for certain projects, I can’t open the input
file, the message is “the system cannot find the path
specified”.</span></p>
<p class="MsoNormal"><span lang="EN-US">Where should I
find the input file?</span></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span lang="EN-US">Thanks a lot</span></p>
<p class="MsoNormal"><span lang="EN-US"> </span></p>
<p class="MsoNormal"><span lang="EN-US">ec</span></p>
</div>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "Timothy McDowell" <<a moz-do-not-send="true"
href="mailto:mcdowell@tess-inc.com">mcdowell@tess-inc.com</a>><br>
To: "Thibaut VITTE" <<a moz-do-not-send="true"
href="mailto:thibaut.vitte@h3c-energies.fr">thibaut.vitte@h3c-energies.fr</a>>,
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Wed, 3 Nov 2010 07:23:05 -0500 (CDT)<br>
Subject: Re: [TRNSYS-users] GenOpt optimization: problem for
the secondgeneration after 5 simulations<br>
This type of error in GenOpt is usually caused by an error in
the TRNSYS<br>
simulation. You need to check the *.lst file for the TRNSYS
run to see<br>
what the TRNSYS error is.<br>
<br>
Regards,<br>
<br>
Tim<br>
<br>
<br>
<br>
<br>
<br>
----------------------------------<br>
Timothy McDowell<br>
Executive Vice President<br>
Thermal Energy System Specialists, LLC<br>
22 N. Carroll St, Suite 370<br>
Madison, WI 53703<br>
Phone: 608-274-2577<br>
Fax: 608-278-1475<br>
<br>
----- Original Message -----<br>
From: "Thibaut VITTE" <<a moz-do-not-send="true"
href="mailto:thibaut.vitte@h3c-energies.fr">thibaut.vitte@h3c-energies.fr</a>><br>
Sent: Wed, November 3, 2010 5:27<br>
Subject:Re: [TRNSYS-users] GenOpt optimization: problem for
the<br>
secondgeneration after 5 simulations<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
Dear Alexis,<br>
<br>
I've had a similar error when I used Genopt. I've had
several<br>
components tracked by a "trace" command that made my list
file<br>
enormous (more than 100Mb) and genopt could'nt handle that
amount of<br>
data.<br>
<br>
Just my 2cents.<br>
<br>
Thibaut<br>
--<br>
<br>
<br>
.bodyclass @page { size: 8.5in 11in; margin-top:
0.7874in; margin-bottom:<br>
0.7874in; margin-left: 0.7874in; margin-right: 0.7874in }<br>
.bodyclass table { border-collapse:collapse;
border-spacing:0;<br>
empty-cells:show }<br>
.bodyclass td, th { vertical-align:top; font-size:12pt;}<br>
.bodyclass h1, h2, h3, h4, h5, h6 { clear:both }<br>
.bodyclass ol, ul { margin:0; padding:0;}<br>
.bodyclass li { list-style: none; margin:0; padding:0;}<br>
.bodyclass li span.odfLiEnd { clear: both; line-height:0;
width:0;<br>
height:0; margin:0; padding:0; }<br>
.bodyclass span.footnodeNumber { padding-right:1em; }<br>
.bodyclass * { margin:0; }<br>
.bodyclass .fr1 { font-size:12pt; text-align:center;
vertical-align:top;<br>
margin-left:0in; margin-right:0in; margin-top:0in;
margin-bottom:0in;<br>
padding:0in; border-style:none; }<br>
.bodyclass .P1 { font-size:12pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Times New Roman; text-align:center ! important; }<br>
.bodyclass .P10 { font-size:7.5pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:justify !
important;<br>
color:#f79646; }<br>
.bodyclass .P2 { font-size:9pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:center ! important;<br>
color:#e36c0a; font-style:italic; font-weight:bold; }<br>
.bodyclass .P3 { font-size:9pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:justify !
important;<br>
color:#e36c0a; font-weight:bold; }<br>
.bodyclass .P4 { font-size:9pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:justify !
important;<br>
color:#e36c0a; font-weight:bold; }<br>
.bodyclass .P5 { font-size:7.5pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; color:#e36c0a;
font-weight:bold; }<br>
.bodyclass .P6 { font-size:7.5pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:justify !
important;<br>
color:#3329b1; }<br>
.bodyclass .P61 { font-size:8.5pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:justify !
important;<br>
color:#3329b1; }<br>
.bodyclass .P7 { font-size:7.5pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:justify !
important;<br>
color:#3329b1; font-style:italic; }<br>
.bodyclass .P8 { font-size:7.5pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Tahoma, sans-serif; text-align:justify !
important;<br>
color:#3329b1; font-style:italic; }<br>
.bodyclass .P9 { font-size:12pt; margin-bottom:0in;
margin-top:0in;<br>
font-family:Times New Roman; text-align:justify ! important; }<br>
.bodyclass .P91 { font-size:12pt; margin-bottom:0in;
margin-top:0.05in;<br>
font-family:Times New Roman; text-align:justify ! important; }<br>
.bodyclass .Standard { font-size:12pt; font-family:Times
New Roman; }<br>
.bodyclass .T1 { color:#f79646; }<br>
.bodyclass .T2 { color:#f79646; font-family:Tahoma,
sans-serif;<br>
font-size:7.5pt; }<br>
.bodyclass .T3 { color:#3329b1; font-family:Tahoma,
sans-serif;<br>
font-size:7.5pt; }<br>
.bodyclass { }<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
Le futur maîtrisé<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
Thibaut VITTE<br>
Docteur - Ingénieur Energies<br>
Mail : <a moz-do-not-send="true"
href="mailto:thibaut.vitte@h3c-energies.fr">thibaut.vitte@h3c-energies.fr</a><br>
<br>
-----------------------------<br>
H3C-énergies<br>
35, chemin du vieux Chêne - 38240 MEYLAN<br>
Tél : 04 76 41 88 66 – Fax : 04 76 41 28<br>
94<br>
<a moz-do-not-send="true"
href="http://www.h3c-energies.fr/" target="_blank">www.h3c-energies.fr</a><br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
-----------------------------------------------------------------------------------<br>
Afin de contribuer au respect de l'environnement,<br>
merci de n'imprimer ce message qu'en cas de nécessité.<br>
In order to respect the environment, please don't<br>
print this e-mail unless you really need to.<br>
<br>
<br>
<br>
<br>
<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
<br>
<br>
----- End of original message -----<br>
<br>
<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
<br>
</blockquote>
</div>
<br>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>