Mesude,<br>
I think you want to use one Type567-2 instead. This mode of
Type567 takes the efficiency as an input and not from a data file.
Save the efficiency values from your Excel file as a tab-delimited
or comma delimited text file. Then use a Type9 (data reader) to read
the file during your TRNSYS simulation. The output of Type9 will be
the efficiency input to Type567.<br>
Best,<br>
David<br>
<br>
<br>
On 10/26/2010 21:44, mesude bayrakci wrote:
<blockquote
cite="mid:AANLkTinzR9M8mQQ+gvpXQ75r9sBRZMYKXbSquXha+=5U@mail.gmail.com"
type="cite">Hello,
<div><br>
</div>
<div>I used Type 567-4 (BIPV) so I need a external efficiency
file. There is only two solar values and some cell temperature
values in The Sample_efficienc.dat file.</div>
<div><br>
</div>
<div>I want to calculated cell temperature and efficiency for
every time step during the year. I am attaching my excel file
which shows my values. </div>
<div><br>
</div>
<div>How can I use these values or excel file?</div>
<div><br>
</div>
<div>Thank you.</div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>