Sunliang,<br>
Unfortunately, these files are becoming harder to find. It used to
be that manufacturer's would provide printed or online documents
containing tables of performance at different entering conditions.
In my experience, a lot of manufacturer's have now developed
in-house software tools that their sales representatives use to
generate performance at a few design inlet conditions. I have had
some luck in making the performance maps required by Type680 by
asking a representative to run the software tool a lot of times.<br>
Regards,<br>
David<br>
<br>
<br>
On 10/21/2010 04:34, SUNLIANG CAO wrote:
<blockquote cite="mid:SNT114-W61C6AAE924014DA4038BDCAD5D0@phx.gbl"
type="cite">
<style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Tahoma
}
--></style>
Dear all,<br>
<br>
I have one question concerning TYPE 680 SINGLE-EFFECT HOT
WATER-FIRED ABSORPTION CHILLER.<br>
<br>
This type 680 requires the user to provide the external catalogue
file (the performance file of absorption chiller).<br>
<br>
I checked several commercial products' website, but unfortunately
the engineering files provided on their websites are not
sufficient for me to write the catalogue file.<br>
<br>
Is there anybody knwos any website which can provide a relatively
detailed performance files for TYPE 680 SINGLE-EFFECT HOT
WATER-FIRED ABSORPTION CHILLER?<br>
<br>
Thank you very much.<br>
<br>
Kind Regards,<br>
Sunliang Cao<br>
<br>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>