<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#ffffff">
    Marek,<br>
      The connection from your weather component (Type15) to your
    psychrometrics component (Type33) includes the humidity ratio but no
    atmospheric pressure or temperature. Consequently, Type33 is trying
    to calculate thermodynamic moist air properties for a varying
    humidity ratio at a constant 20C and 1atm. Very often the result
    that it comes up with is above the saturation line. I think if you
    connect the ambient temperature and pressure to Type33 your errors
    will go away.<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    On 10/25/2010 00:41, Kremen Marek wrote:
    <blockquote
cite="mid:B6198CBF2D449E47BDFBBACD63AEAB600A491FC0EE@EXCHANGE32.staff.main.ntu.edu.sg"
      type="cite">
      <pre wrap="">Hi, I have a question using energy plus weather file with type 56. I am currently dealing with simulation of simple "black box" building located in humid, hot climate (Singapore). I downloaed the data from Energy + site and result of simulation should be condensation in the building....I have problem with running the simulation, it causes errors all the time. Can you help? 

Thanks, Marek 

PS: all files are attached within this email</pre>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>