class=003562607-14092010>Hi,</SPAN></FONT>
</DIV>
<DIV dir=ltr align=left><FONT size=2 face=Arial><SPAN 
class=003562607-14092010></SPAN></FONT> 
</DIV>
<DIV dir=ltr align=left><FONT size=2 face=Arial><SPAN 
class=003562607-14092010>1) please have a look to the Trnsys3d Tutorial at page 
20. There is a picture at the bottom that shows in what case you'll use the 
virtual surface. Normally this wall type is used if you want to simulate 
stratification effects like in wintergardens,... By this you could for 
example have a radiative zone (means all walls are in radiation exchange) with 
several AIRNODES inside. The virtual surface is just a seperator of these 
Airnodes that will be deleted after importing into 
TRNBUILD.  </SPAN></FONT>
</DIV>
<DIV dir=ltr align=left><FONT size=2 face=Arial><SPAN 
class=003562607-14092010>2) If you use Trnsys3d you'll at first define all 
walls in the 3D geometry. These definitions for walls and windows will remain in 
TRNBUILD. If you have AIRNODES defined for a radiative zone then the REGIME 
DATA is splitted up into two parts, the REGIME DATA for the 
specifique AIRNODES (like heating, cooling,...) and the REGIME DATA for the 
radiative zone (like GEOMETRY MODE,...).</SPAN></FONT>
</DIV>
<DIV dir=ltr align=left><FONT size=2 face=Arial><SPAN 
class=003562607-14092010>3) Normally if you have two zones that are linked by an 
ADJACENT WALL you can define a COUPLING in TRNBUILD if you select these walls 
(like defining a GEOSURF or WALLGAIN). But you have to consider that couplings 
can only be in a positive direction. This means that for example if you are in 
the definition of zone A you can define a COUPLING from zone B with xxx kg/h air 
flow. If you want an air flow the other way then you have to be in the 
definition of zone B and to define a COUPLING from zone A... A special case is 
if you have a virtual surface between AIRNODES because this will be thrown 
out and so you have no wall to define a coupling. For this reason there is a new 
button called COUPLING in the REGIME DATA of the AIRNODES. There you can make 
the same definitions as for walls.</SPAN></FONT>
</DIV>
<DIV><FONT size=2 face=Arial></FONT> 
</DIV>
<DIV align=left>
<DIV align=left><FONT size=2 face=Arial><SPAN 
class=003562607-14092010>Regards</SPAN></FONT>
</DIV>
<DIV align=left><FONT size=2 face=Arial>Christian</FONT>
</DIV>
<DIV align=left><FONT size=2 face=Arial></FONT><FONT size=2 
face=Arial></FONT> 
</DIV>
<DIV align=left><FONT size=2 face=Arial>TRANSSOLAR Software Team</FONT>
</DIV>
<DIV align=left><A 
title="blocked::mailto:hotline@transsolar.com
mailto:hotline@transsolar.com" 
href="mailto:hotline@transsolar.com"><I 
title="blocked::mailto:hotline@transsolar.com
mailto:hotline@transsolar.com"><FONT 
title="blocked::mailto:hotline@transsolar.com
mailto:hotline@transsolar.com" 
face=Arial><FONT 
title="blocked::mailto:hotline@transsolar.com
mailto:hotline@transsolar.com" 
color=#0000ff size=2>hotline@transsolar.com</FONT></I></FONT></A><FONT 
face=Arial><FONT 
size=2>                                 </FONT>
</DIV></FONT>
<DIV align=left><FONT size=2 face=Arial><SPAN 
style="FONT-FAMILY: 'Times New Roman'; FONT-SIZE: 12pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: DE; mso-fareast-language: DE; mso-bidi-language: AR-SA"><?xml:namespace 
prefix = v ns = "urn:schemas-microsoft-com:vml" /><v:shapetype id=_x0000_t75 
coordsize="21600,21600" o:spt="75" o:preferrelative="t" 
path="m@4@5l@4@11@9@11@9@5xe" filled="f" 
stroked="f"> </v:shapetype></SPAN></FONT>
</DIV>
<DIV align=left><A title="blocked::http://trnsys.de/
http://trnsys.de/" 
href="http://www.trnsys.de/"><I 
title="blocked::http://trnsys.de/
http://trnsys.de/"><FONT 
title="blocked::http://trnsys.de/
http://trnsys.de/" color=#0000ff size=2 
face=Arial>www.trnsys.de</FONT></I></A><FONT color=#0000ff size=2 
face=Arial>         </FONT>
</DIV><FONT 
size=1 face=Arial>
<DIV align=left><FONT size=2>Transsolar KlimaEngineering - Technologien für 
energieeffizientes Bauen und Nutzerkomfort in 
Gebäuden</FONT>                                    
</DIV>
<DIV align=left><FONT size=2>Transsolar Energietechnik GmbH, Curiestrasse 2, 
70563 Stuttgart / Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.: 
99073/00911</FONT>        
</DIV>
<DIV align=left><FONT size=2>Geschäftsführer: Dipl.Ing. Matthias Schuler, 
Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst, Prof. Volkmar 
Bleicher</FONT></FONT>
</DIV></DIV>
<DIV> 
</DIV><BR>
<DIV dir=ltr lang=de class=OutlookMessageHeader align=left>
<HR tabIndex=-1>  
<FONT size=2 face=Tahoma><B>Von:</B> aongya.sumaila@lte.ireq.ca 
[mailto:aongya.sumaila@lte.ireq.ca] <BR>
<B>Gesendet:</B> Montag, 13. September 
2010 15:49<BR>
<B>An:</B> trnsys-users@cae.wisc.edu<BR>
<B>Betreff:</B> 
[TRNSYS-users] TRNSYS 17-TRNBuild - multiple airnodes...<BR>
</FONT><BR>
</DIV>
<DIV></DIV>
<P>
<DIV><FONT size=2 face=Arial><SPAN 
class=671522313-13092010>Hello,</SPAN></FONT>
</DIV>
<DIV><FONT size=2 face=Arial><SPAN 
class=671522313-13092010></SPAN></FONT> 
</DIV>
<DIV><FONT size=2 face=Arial><SPAN class=671522313-13092010>I recently started 
to explore TRNSYSv17 and I got a few unanswered questions about TRNBuild. 
Hopefully, someone of you will be able to help me on this.</SPAN></FONT>
</DIV>
<DIV><FONT size=2 face=Arial><SPAN class=671522313-13092010>I'm using TRNSYS3D 
plug-in for Google SketchUp to create 3D Multizone buildings and I import them 
in TRNBuild to add the regime data, equipments...I also worked a bit with the 
Multizone Building tutorial example called 'Restaurant'.</SPAN></FONT>
</DIV>
<DIV><FONT size=2 face=Arial><SPAN 
class=671522313-13092010></SPAN></FONT> 
</DIV>
<DIV><FONT size=+0><SPAN class=671522313-13092010><FONT size=2><FONT 
face=Arial>1- In a practical sense, what means 'Virtual Surface'? <SPAN 
id=result_box><SPAN style="BACKGROUND-COLOR: #fff" title="" 
closure_uid_1n655h="130" ye="Quelles sont les propriétés de mur de ce type?" 
ze="What are the properties of this type of wall? ">What are the properties of 
this type of wall? </SPAN><SPAN style="BACKGROUND-COLOR: #fff" title="" 
closure_uid_1n655h="157" ye="Quel sont les cas dans lesquels on l'utilise?" 
ze="What are the cases in which it is used?">What are the cases in which it is 
used?</SPAN></SPAN></FONT></FONT></SPAN></FONT>
</DIV>
<DIV><FONT size=+0><SPAN class=671522313-13092010><FONT size=2><FONT 
face=Arial><SPAN><SPAN style="BACKGROUND-COLOR: #fff" title="" 
closure_uid_1n655h="157" ye="Quel sont les cas dans lesquels on l'utilise?" 
ze="What are the cases in which it is used?">2- If we create a new airnode in a 
zone, do we have to redefine all the building surfaces or they are 
assigned by default? Same thing but with the regime data, is it assigned to 
all the new airnodes in a zone or just to one by 
default? </SPAN></SPAN></FONT></FONT></SPAN></FONT>
</DIV>
<DIV><FONT size=+0><SPAN class=671522313-13092010><FONT size=2><FONT 
face=Arial><SPAN><SPAN style="BACKGROUND-COLOR: #fff" title="" 
closure_uid_1n655h="157" ye="Quel sont les cas dans lesquels on l'utilise?" 
ze="What are the cases in which it is used?">3- In the restaurant example that I 
tried to recreate, there is a convective coupling between airnodes in two 
differents zones. How is it possible to do 
that?</SPAN></SPAN></FONT></FONT></SPAN></FONT>
</DIV>
<DIV><FONT size=+0><SPAN class=671522313-13092010><FONT size=2><FONT 
face=Arial><SPAN><SPAN style="BACKGROUND-COLOR: #fff" title="" 
closure_uid_1n655h="157" ye="Quel sont les cas dans lesquels on l'utilise?" 
ze="What are the cases in which it is used?"></SPAN></SPAN></FONT></FONT></SPAN></FONT> 
</DIV>
<DIV><FONT size=+0><SPAN class=671522313-13092010><FONT size=2><FONT 
face=Arial><SPAN><SPAN style="BACKGROUND-COLOR: #fff" title="" 
closure_uid_1n655h="157" ye="Quel sont les cas dans lesquels on l'utilise?" 
ze="What are the cases in which it is used?">Thanks in advance for any help you 
can provide!</SPAN></SPAN></FONT></FONT></SPAN></FONT>
</DIV>
<DIV><FONT size=2 face=Arial><SPAN 
class=671522313-13092010></SPAN></FONT> 
</DIV>
<DIV><FONT size=2 face=Arial></FONT> 
</DIV>
<DIV align=left><FONT face=Calibri><EM>Sumaila</EM></FONT>
</DIV>
<DIV align=left><FONT face=Calibri>Laboratoire des technologies de l'énergie 
(LTE)</FONT>
</DIV>
<DIV align=left><FONT face=Calibri>600, avenue de la Montagne</FONT>
</DIV>
<DIV align=left><FONT face=Calibri>Shawinigan, QC, G9N 7N5</FONT>
</DIV>
<DIV align=left><FONT face=Calibri>Tel: 819-539-1400 poste 1340</FONT>
</DIV>
<DIV align=left><FONT face=Calibri>Courriel: </FONT><A 
href="mailto:aongya.sumaila@lte.ireq.ca"><FONT 
face=Calibri>aongya.sumaila@lte.ireq.ca</FONT></A>
</DIV>
<DIV> 
</DIV>
<P>
</P></BODY></HTML>